Need to wire my shop

Sychotix57

Well-known member
Joined
Mar 21, 2015
Messages
81
Location
Rocky Mount, NC
I have a 24x30 metal building I'm having built. I have a 100amp panel to install that was free. I want to feed it off my house, which is roughly 75 feet away. I will be running light fixtures, fridge, a fan, power tools, and a 110 air compressor. I'd like have 220 if I can so I can use a welder or upgrade my air compressor. Due to finances, 220 is not a necessity. What size wire should I run? I've read other threads but I just don't understand of them.

Sent from my Pixel XL using Tapatalk
 
To avoid these ads, REGISTER NOW!

matt_i

Well-known member
Joined
Mar 14, 2008
Messages
10,728
Location
SE Michigan
Alarm bells start going off at the mention of "free panel". Depending on what brand, how old, etc, it might be better to get a new one at your local big box.

You will have 240vac available in the panel whether you like it or not.

The time to study your panel location and correctly locate the feed conduit is *now*.

You have more time to finalize your layout and put specific circuits here and there but I'd also recommend a "shotgun" approach of putting outlets every "X" inches based on the availability of attaching to your interior "framework".
 
OP
S

Sychotix57

Well-known member
Joined
Mar 21, 2015
Messages
81
Location
Rocky Mount, NC
Alarm bells start going off at the mention of "free panel". Depending on what brand, how old, etc, it might be better to get a new one at your local big box.

You will have 240vac available in the panel whether you like it or not.

The time to study your panel location and correctly locate the feed conduit is *now*.

You have more time to finalize your layout and put specific circuits here and there but I'd also recommend a "shotgun" approach of putting outlets every "X" inches based on the availability of attaching to your interior "framework".

Well it's a Square D panel (not sure of age) I just figured that would save me $100. I'd like outlets every 4ft to match the framework and one or two 220 outlets. I had a electrician tell me to use direct burial wire to the house. And I already have about 200ft of Romex (free) that I'd like to use as well.

Sent from my Pixel XL using Tapatalk
 

rburke65

Well-known member
Joined
Nov 10, 2007
Messages
12,349
Location
Canfield, Ohio
Its worth it in the long run to update your location in your profile. Run 2" PVC conduit and pull in your feed. What size service do you have in your house?
 
OP
S

Sychotix57

Well-known member
Joined
Mar 21, 2015
Messages
81
Location
Rocky Mount, NC
Its worth it in the long run to update your location in your profile. Run 2" PVC conduit and pull in your feed. What size service do you have in your house?
Alright. I have 200amp on the house and have 3 spots left on my house panel.

Sent from my Pixel XL using Tapatalk
 

malibu101

Well-known member
Joined
Jul 1, 2005
Messages
3,908
Location
Walnutport PA
I understand being on a budget....
While a trench is dug for whatever electric you take to the shop, put in a conduit for communication wires even if you're not going to use it now.
Conduit is not too expensive and it's easier than digging again.

Otherwise, if you don't, in a few years, you'll remember my bit of advise.
 
OP
S

Sychotix57

Well-known member
Joined
Mar 21, 2015
Messages
81
Location
Rocky Mount, NC
I understand being on a budget....
While a trench is dug for whatever electric you take to the shop, put in a conduit for communication wires even if you're not going to use it now.
Conduit is not too expensive and it's easier than digging again.

Otherwise, if you don't, in a few years, you'll remember my bit of advise.
Noted.

Sent from my Pixel XL using Tapatalk
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,750
Location
NW Iowa
75' of aluminum would be pretty cheap. Some #2 would get you 90 amps.
That setup would be fine, probably even overkill as long as you don't plan some massive welder or air compressor. You can compare prices of wire if you want to go smaller but you won't save much.

Otherwise, if you don't, in a few years, you'll remember my bit of advise.

Or 40+ years. I've seen lots of URD from the 70's that's never had issues.:dunno:
 
Last edited:
OP
S

Sychotix57

Well-known member
Joined
Mar 21, 2015
Messages
81
Location
Rocky Mount, NC
75' of aluminum would be pretty cheap. Some #2 would get you 90 amps.
That setup would be fine, probably even overkill as long as you don't plan some massive welder or air compressor. You can compare prices of wire if you want to go smaller but you won't save much.



Or 40+ years. I've seen lots of URD from the 70's that's never had issues.:dunno:
So do I use 2/2/4/6 or 2/2/2/4?

Sent from my Pixel XL using Tapatalk
 
To avoid these ads, REGISTER NOW!

malibu101

Well-known member
Joined
Jul 1, 2005
Messages
3,908
Location
Walnutport PA
75' of aluminum would be pretty cheap. Some #2 would get you 90 amps.
That setup would be fine, probably even overkill as long as you don't plan some massive welder or air compressor. You can compare prices of wire if you want to go smaller but you won't save much.



Or 40+ years. I've seen lots of URD from the 70's that's never had issues.:dunno:
I don't disagree with what you say about URD.

Read my whole post not just the last line of it that was quoted above.
I wasn't talking about about electric wires.
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
2 2 2 4 , this is as cheap and good as it gets. You can do it either way, direct or pipe. If you know you need another cable, tv or such the time to include it is now but with wireless there isn't much need for additional raceway.
 
Last edited:

Notgrownup

Well-known member
Joined
May 5, 2014
Messages
5,927
Location
Snow Hill NC
I used 2/2/2/4 I think, it was direct burial but I still ran it in conduit for extra protection. I think the local guy called it Mobile Home Feed...I have a 100 amp sub, I am wiring for A/C, compressor, both 220vac and 12/3 romex throughout with 20 amp breakers. I think an outlet every 4 ft us a bit overkill but that is me...I have mine every 8'. I did do a breaker for each wall for 3 wall but split over 2 breakers on my workbench wall.
1 breaker for 8 each 4' T8 double fixtures and miscellaneous other lines...ceiling fans, attic lights and garage door opener, outside lighting etc....and a 30 amp reverse feed fir generator.
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
I did do a breaker for each wall for 3 wall but split over 2 breakers on my workbench wall
. This is good, a couple general tool circuits with nothing but recepts on them, I like a circuit for all the parasitic stuff and a way to get at the panel for any additional specialized equipment that comes along, nothing better than being able to tailor it as it happens.
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,750
Location
NW Iowa
Either 2-2-2-4 or 2-2-4-6, I have heard some area's don't like the reduced neutral. In many other area's the reduced neutral is common.

I don't disagree with what you say about URD.
Read my whole post not just the last line of it that was quoted above.
I wasn't talking about about electric wires.

Looks like I have to eat my words this time. I'm getting so used to the usual "URD is going to fail is a few years" line that I didn't read what you wrote very thoughtfully. Sorry for jumping to conclusions.

I do agree that it would be good to consider making provisions if you every want data/cable in the building. Seems like many people battle a wireless setup that doesn't work well.
 
Last edited:
OP
S

Sychotix57

Well-known member
Joined
Mar 21, 2015
Messages
81
Location
Rocky Mount, NC
I used 2/2/2/4 I think, it was direct burial but I still ran it in conduit for extra protection. I think the local guy called it Mobile Home Feed...I have a 100 amp sub, I am wiring for A/C, compressor, both 220vac and 12/3 romex throughout with 20 amp breakers. I think an outlet every 4 ft us a bit overkill but that is me...I have mine every 8'. I did do a breaker for each wall for 3 wall but split over 2 breakers on my workbench wall.
1 breaker for 8 each 4' T8 double fixtures and miscellaneous other lines...ceiling fans, attic lights and garage door opener, outside lighting etc....and a 30 amp reverse feed fir generator.
Okay. I had the same general idea. Thanks

Sent from my Pixel XL using Tapatalk
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,030
Location
Modesto, CA
conduit is cheap insurance.

Use #2 for the 90a MHF and a couple 1" for comm cable in the future if u dont need it now.

U will also need 2 ground rods spaced min 6' and an isolated neutral bar. U may also need to buy a ground bar kit that is listed for your panel.
 

HotwheelsYJ

Well-known member
Joined
Oct 28, 2009
Messages
81
Location
Cleveland TN
I have basically the same shop dimensions 32x20 with a 100 amp panel fed with 2/2/2/4 direct burial mobile home wire. (90A breaker @ main)
Plus a run of 3/4 PEX for internet.

I put 110v outlets every 32"(2 studs) @ 49" to bottom of box.
My breaker layout is:
1. 50a welder, door wall
2. 50a welder, back wall
3. 30a compressor outside
4. 110 back wall
5. 110 left side
6. 110 right side
7. 110 overhead & door wall
8. Lights
9. Water heater

I have a few more slots open if I ever decide to add dedicated HVAC. For now, I made a pigtail to plug in the welder outlet for the window AC or elec heater.

Sent from my Pixel using Tapatalk
 