Need tricks and tips using a fish tape

lhc_cj7

Well-known member
Joined
Oct 28, 2008
Messages
86
Location
Ohio
This is a redo of my long awaited 100 amp sub panel that turns out to have several NEC code infractions. The lack of a 4th or bonding wire from the main to the sub is the subject of this thread. Its 75’ of 2” PVC buried down 24” with 3 1\0 wires. I pushed a fish tape from the main panel and it stopped at the 3rd bend so tried from the garage side and it stopped about 40’ in on the straight stretch behind the house. Tried about 6 times each way and gave up. I’d much rather do this then in the attic just because of the hole needed in the bedroom wall and disturbing the attic insulation.

So any tricks of the trade on getting the fish tape thru the stopping points?

Thanks
 
To avoid these ads, REGISTER NOW!

Evan(CA)

Banned
Joined
Mar 3, 2013
Messages
996
What kind of fish tape? Make sure it has a flexible end on it and isn't just curled over metal. Once you hit the bend all you can do is pull it back and forth until it finds a way through. You'll get it. Use a bit of soap if you absolutely have to but it shouldn't be necessary.
 

Mustang51js

Well-known member
Joined
Jan 24, 2014
Messages
1,734
Location
Haskell nj
There's a couple things but don't think some will work since there's wires in allready. One is to get another snake and push it in the other end and twist it, it will catch the other snake but don't think it will work with wires. Another thing is have someone bang on the elbow while your pushing but if it's buried in the ground that's not possible. Your last option and probably the best way in your case is to tape the fish tape to one of the existing wires and pull one wire back out, then attach both wires onto the snake and pull it back through,just make sure you wrap part of the wire on the hook of the snake so there's no chance of it coming off midway,get some wire lube and use that to help, put it in both ends just not at same time,one side when u pull snake back and then on the wires when pulling back through.
 

rockwithjason

Well-known member
Joined
Jan 8, 2006
Messages
2,633
Location
Las Vegas
you can loop several turns of twine or string around the end of the tape and then try to hook it from the other side.
 

Heatdr

Member
Joined
Oct 6, 2010
Messages
13
Location
Weymouth,New Jersey
They make a fish string thats very light but strong,youpierce a table tennis ball and tie the string to it and put a shop vac on the other end.It will fly right through,the tie the string to a rope and pull that through then pull the wires with the rope.Use pulling compound on the wires,its messy but makes it go so much easier
 

Milton Shaw

Well-known member
Joined
Feb 11, 2011
Messages
4,837
The tennis ball idea I don't think would work with wires already in the pipe. Greenlee and others make foam string pullers that work with a shop vacuum. You can also force it through with compressed air to assist the vacuum. DO USE THE VACUUM BEFORE USING FORCED AIR IS THERE COULD BE WATER/JUNK IN THE PIPE. I saw a telephone installer use forced air to blow the foam string puller through and it ended up under another desk than he thought it was and the girl there was covered with water/trash.
 

MTW

Well-known member
Joined
Aug 6, 2013
Messages
294
Location
SE Michigan
Need tricks and tips using a fish tape, lhc_cj7

My 2 cents:
You've had enough tricks already, haven't you. An inadequate job that also passed inspection? Bought and paid for....? What you now have is a very difficult job to try and rectify with no support from the supposed expert.

I'm not here to criticize you but to try and inform that "you learn as you burn ", this way of learning is often the most expensive, but never forgotten.

Onto the problem, of trying to get a ground wire installed or just getting a fishtape trough an existing conduit.

I went and looked over your post on the install before commenting, so as to offer the best remedy, not just random thoughts or suggestions. I will offer the best suggestions first, as I would do on the job . But after reviewing your actual install my opinion changed.

1. Use a round (nylon) fishtape. They are expensive, but the round profile guides itself around obstructions and turns much better than a flat coiled steel tape, even if it has a round metal leader section.

2. Pull the wires out, with a pulling rope attached to the end. Attach the additional conductor and re-pull in.

After install thread review.

3. Put away your fish tape, and connect it for a safe 3 wire installation. This was briefly mentioned earlier by wyliesdiesels near the end of the original thread. 3 wire feeders were accepted practice for many years but are no longer accepted, but is a lot safer than what you have now, ungrounded equipment. Install the neutral bonding screws in both panels neutral bar to give your sub-panel enclosure a ground connection. For all intensive purposes your ground rod is useless as a equipment ground.

Reasons for this line of thinking.

4. If you cant get a tape through, wire installation will be almost impossible. Especially after looking at the install photos. After looking at the size of the boxes, the conduit routing, splicing in each box and type of wire, there are too many things working against you.

5, Five 90deg bends in the underground conduit is one more than allowed by code. Too many bends to replace or install the wire without damage or undue force. That's the reason for the rule allowing 360 degree maximum (4, 90's). The underground should have failed inspection if one was even done, before the trench was covered.

6, The neat bending you mentioned with a rosebud is the next issue. PVC conduit is to be heated in an oven or blanket for uniform bending. Airtight plugs are used at the ends of the conduit before heating to prevent the pipe from constricting while being bent. The internal air pressure that builds up pressurizes the pipe to help prevent it from flattening out when being bent and cooled. The 2" field bend shown in your photo definitely looks flattened out to me, and I'm sure the others were similar. 1 1/5" is the smallest I ever try to bend without the air plugs, 2" and larger collapses even with, even heating.

7, The style of wire you used is "tri-plexed" conductors that are twisted together. This makes for a larger overall bundle diameter than individual straight conductors and much stiffer to restrict movement. The spiral shape of the bundle also tends to deflect the fish tape in a spiral pattern around the bundle. This will give you the Chinese finger-grip effect on the bundle when trying to pull the new conductor in.

8, The tiny boxes with no surplus wire or room to maneuver is a problem. Again the reason for the code rule of min 6x the raceway diameter 2" x 6 = 12" min box size.

Code section:314.28
(2) Angle or U Pulls, or Splices. Where splices or where
angle or U pulls are made, the distance between each raceway
entry inside the box or conduit body and the opposite
wall of the box or conduit body shall not be less than six
times the metric designator (trade size) of the largest raceway
in a row. This distance shall be increased for additional
entries by the amount of the sum of the diameters of all other
raceway entries in the same row on the same wall of the box.
Each row shall be calculated individually, and the single row
that provides the maximum distance shall be used.

9, Your steel splice boxes and thinwall conduit sections are not grounded. If a short were to occur anywhere, say in one of your splices, the boxes and conduit would become live. This constitutes a serious electrocution and fire hazard were it to occur. This metal, enclosing the wiring must be properly grounded if you elect to go with the 3 wire feeder as a stop gap solution, for your own safety

10, Service entrance cable (SE) used in the interior wall. As others suggested previously, you would need to replace this too, thus requiring opening up the wall again.

11, Given that all of the above confront the installation, repair to code would necessitate almost the entire installation being redone. Making it safer would require bonding both panels neutral bars for effective, if not code approved equipment grounding connection, and running a properly sized ground wire to the metal conduits and boxes. Even this would require opening the wall again.

Food for thought, depending on where you sit, consider the following.

If this was done for hire from a licensed professional and inspected, I would be complaining to the city or county that they are sending out rubber stamp inspectors, that allow shady contractors to install an unsafe and nonconforming installations. And get them to pressure the contractor to make it right.

If you and your buddy did this with someone else's license, then you should man up and fix it right, even if it got a rubber stamp. When something goes wrong the insurance company is going to be looking to someone to blame. At a bare minimum get the conduit, boxes, and subpanel loadcenter enclosure connected to ground, the real ground in your service panel, not some rod beaten into dry soil.

End of 2 cents, for what it's worth. Ω
 

hh76

Well-known member
Joined
Nov 9, 2010
Messages
3,447
Location
NE Wisconsin
I'm not a huge fan of using a fish tape with wire already in the pipe. To many sharp edges to nick the existing wires. Good chance that the tape will get stuck on the wire and you'll end up pulling them out to get it free.

Best to just pull out one of the wires with Two more attached to take it's place.
 

73surffisher

Well-known member
Joined
Sep 11, 2013
Messages
125
Location
Hampstead, MD
I concur with MTW, , you need to make it right by code before some one gets hurt really bad , , , , no piling on just an observation, , ,

Agree with hh76 as well, , I've never had luck fishing a conduit with existing wires, , , it takes less time to simply pull them out, , then pull them in again, , , , ,

My dad used to ask me "if you don't have time to do it right the first time, how are you going to find the time to do it over again "
 

Falcon67

Well-known member
Joined
Jun 11, 2009
Messages
18,371
Location
Merkel, TX
They make a fish string thats very light but strong,youpierce a table tennis ball and tie the string to it and put a shop vac on the other end.It will fly right through,the tie the string to a rope and pull that through then pull the wires with the rope.Use pulling compound on the wires,its messy but makes it go so much easier

If there are wires, then use a wad of paper towels and a smaller string and pull it through with the shop vac. Follow with larger rope.
 
To avoid these ads, REGISTER NOW!
OP
L

lhc_cj7

Well-known member
Joined
Oct 28, 2008
Messages
86
Location
Ohio
An array of valuable informaton. :bowdown:
1) Gonna try the tape again from each end.
2) will try with looped wire on one tape end and try to hook from the other tape
3) Disconnec the 3 wires from one end and pull in enough to try the vacuum thing.
4) Pull the wires all the way out, attach bond wire and pull back thru.

Not sure when this will happen. I've had a pinched nerve behind the left shoulder blade and the chiro doc is working on it.
 

mobiledynamics

Well-known member
Joined
Mar 14, 2010
Messages
5,037
Location
Gotham City
LHC.

If it was me, I would just not waste any effort or time. pull the wire out. Attach a drag or 2 to the end. Then pull the entire run back through.

IMO. It would be the easiest and fastest way...
 

Huxley

Well-known member
Joined
Mar 4, 2008
Messages
210
Location
Colorado
I have little to no hope for methods 1-3. Use #4 for sure. I would pull all 3 wires out while pulling the fish in at the same time. In the original thread, you stated it took 5 min to pull the wires. You likely already have far more time in than that trying to get that fish in the hole. You are going to get really frustrated with the first 3 methods & resort to #4 anyway. What is it? 2" pipe? Figure it is about 1/2 full of wires, with several 90's. I don't like the chances even if you have a bunch of lubricant in there.

I would also remove the junction box from the wall to make life easier. Makes for a nice straight shot into the conduit & reduces the chance of nicking the insulation. Great excuse / opportunity to replace the existing box with the 6X size noted.

Thank you for posting. It was an interesting read. I will be rewiring my garage soon.
 
OP
L

lhc_cj7

Well-known member
Joined
Oct 28, 2008
Messages
86
Location
Ohio
Need tricks and tips using a fish tape, lhc_cj7

My 2 cents:
You've had enough tricks already, haven't you. An inadequate job that also passed inspection? Bought and paid for....? What you now have is a very difficult job to try and rectify with no support from the supposed expert. Agreed

8, The tiny boxes with no surplus wire or room to maneuver is a problem. Again the reason for the code rule of min 6x the raceway diameter 2" x 6 = 12" min box size. We will change this out to 6x6 minimum


9, Your steel splice boxes and thinwall conduit sections are not grounded. If a short were to occur anywhere, say in one of your splices, the boxes and conduit would become live. This constitutes a serious electrocution and fire hazard were it to occur. This metal, enclosing the wiring must be properly grounded if you elect to go with the 3 wire feeder as a stop gap solution, for your own safety what is the proper way to bond these boxes and emt? Will one bond wire connected to the first box and then to the sub meet code?

10, Service entrance cable (SE) used in the interior wall. As others suggested previously, you would need to replace this too, thus requiring opening up the wall again.
The SE is a 4 wire bundle, the bond wire is available in the jbox outside the garage but in the sub panel was cut back to the sheathing. If you look at the pic in the OE post 2nd page is code met if we were to peel back the remainintng sheathing and splice what's available?

Thanks to all for staying with me on this.
 

MTW

Well-known member
Joined
Aug 6, 2013
Messages
294
Location
SE Michigan
8, The tiny boxes with no surplus wire or room to maneuver is a problem. Again the reason for the code rule of min 6x the raceway diameter 2" x 6 = 12" min box size. We will change this out to 6x6 minimum
This should be 12x12.

9, Your steel splice boxes and thinwall conduit sections are not grounded. If a short were to occur anywhere, say in one of your splices, the boxes and conduit would become live. This constitutes a serious electrocution and fire hazard were it to occur. This metal, enclosing the wiring must be properly grounded if you elect to go with the 3 wire feeder as a stop gap solution, for your own safety what is the proper way to bond these boxes and emt? Will one bond wire connected to the first box and then to the sub meet code?
Bonding one end is sufficient for branch circuits and feeders, as long as the metal is continuous and the fittings are tight. Ideally the ground would come from the source end (Main Panel) but connecting it to the load end would be better than doing nothing. The minimum size for 125A main breaker would be #6 copper or #4 Aluminum. Bolt a aluminum lug to the enclosure for connecting the wire. My preferred method is with a green ground screw into a 10-32 tapped hole in the back of the enclosure.

The SE is a 4 wire bundle, the bond wire is available in the jbox outside the garage but in the sub panel was cut back to the sheathing. If you look at the pic in the OE post 2nd page is code met if we were to peel back the remaining sheathing and splice what's available?

Doesn't look like there is enough conductor left to get a proper splice, under the sheathing. The SE cable ground is made of aluminum, so splice to Aluminum with an alum rated splice connector (split bolt). If you use copper, make sure you have a connector rated for both metals.

Thanks to all for staying with me on this.

Your welcome, that's what the forum is all about, sharing the knowledge.
Get it fixed up so you can, use it safely, and forget about worrying about it.

Can you comment on this part below, I'm sure it would be beneficial for other members and lurkers, as many on the forum undertake this same project.

If this was done for hire from a licensed professional and inspected, I would be complaining to the city or county that they are sending out rubber stamp inspectors, that allow shady contractors to install an unsafe and nonconforming installations. And get them to pressure the contractor to make it right.

If you and your buddy did this with someone else's license, then you should man up and fix it right, even if it got a rubber stamp. When something goes wrong the insurance company is going to be looking to someone to blame.
Ω
 

CNGsaves

Well-known member
Joined
Sep 26, 2012
Messages
13,233
Location
KS and OK
2 more things that didn't appear to be covered:

a) Did the main load center of the entire house have proper TWO ground rods at least 6 ft apart ?? (can pull and re-use the "orphan" ground rod that was not needed for subpanel on attached garage)
b) Was the incoming water service grounded within 6 ft of when it entered the house ??
 

Charles (in GA)

Well-known member
Joined
Jan 11, 2006
Messages
12,489
Location
50 mi south of Atlanta
I'm not a huge fan of using a fish tape with wire already in the pipe. To many sharp edges to nick the existing wires. Good chance that the tape will get stuck on the wire and you'll end up pulling them out to get it free.

Best to just pull out one of the wires with Two more attached to take it's place.

^^^
THIS
Just about impossible to run a fish tape down a pipe with wire in it. Not worth the effort. Pull the existing wire and repull it with the additional wire. Tape will get down between and thru the wires and make a tangled mess.

Charles
 