Need wire size

steve308

Well-known member
Joined
Nov 20, 2011
Messages
2,075
I am updating my breaker box later today (work being done by an electrician) to add additional power to my garage. I've run the wires for two 20 amp circuits but I would also like to run the proper gauge for a later install of a mini-split unit. Do I need anything larger than 12-3? Oh - the electrician works in a secure building so I can't call him and I want to have everything laid out to save him time. Thanks in advance.
 
To avoid these ads, REGISTER NOW!
OP
S

steve308

Well-known member
Joined
Nov 20, 2011
Messages
2,075
15000 btu unit heat pump-AC / box to hook up will be 25 - 30ft in length

TYPE: Heat Pump (Inverter)

Performance Ratings:

•Size: 1.25 TON
•SEER: 21.0
•EER: 13.0
•HSPF: 10.0
•Cooling Capacity: 14,000 Btu/h
•Tax Credit Qualify: Yes

Outdoor Unit: MUZGE15NA
•Height: 21 5/8"
•Width: 31 1/2"
•Depth: 11 1/4"
•Min. Amp: 12.0
•Max. Fuse: 15.0
•Liquid Line: 1/4"
•Suction Line: 1/2"
•Max. Refrigerant Pipe Length: 65'
•Max. Refrigerant Pipe Height Difference: 40'

Indoor Unit: MSZGE15NA
•Height: 11 5/8"
•Width: 31 7/16"
•Depth: 9 1/8"
•Min. Amp: 1.0
•Max. Fuse: 15.0
Thanks
 

BillK

Well-known member
Joined
Aug 24, 2006
Messages
9,353
Location
Beautiful Southern Maryland
Outdoor Unit: MUZGE15NA

•Min. Amp: 12.0
•Max. Fuse: 15.0


Indoor Unit: MSZGE15NA

•Min. Amp: 1.0
•Max. Fuse: 15.0

If these specs are correct then #12 wire should be fine. It looks like they want no more than a 15 amp breaker for both units.
Personally I would wait and ask the electrician though, just to be certain.
 

theoldwizard1

Well-known member
Joined
Feb 22, 2011
Messages
43,237
Location
SE MI
I think you have your part number wrong ! I believe the outside unit should be a MSY-D30NA, which, according to the spec sheet requires a 25A breaker.

Of course, this means 10-3 copper wire

FYI : The 36,000 BTU model (MSY-D36NA) will also run on a 25A breaker.
 
To avoid these ads, REGISTER NOW!
OP
S

steve308

Well-known member
Joined
Nov 20, 2011
Messages
2,075
Specs were copied and pasted directly from 'Mitzi" spec sheet. Should I install the 10-3 just to be on the safe side? I am a subscriber that to much is just short of enough. (Room in question is 400 Sq. with vaulted ceiling so I think I should be OK with the 15000 unit)
 

RKA

Well-known member
Joined
Jun 9, 2010
Messages
1,744
Location
NJ
According to mitsu's website, min circuit ampacity is 12A for that unit (220v), add 20% to that an a 15A circuit is fine. 12-2 should be just fine.

Don't forget to look up the requirements for the indoor unit. I think mine required a 16-3 300v wire to connect it to the outdoor unit.
 

theoldwizard1

Well-known member
Joined
Feb 22, 2011
Messages
43,237
Location
SE MI
Specs were copied and pasted directly from 'Mitzi" spec sheet. Should I install the 10-3 just to be on the safe side? I am a subscriber that to much is just short of enough. (Room in question is 400 Sq. with vaulted ceiling so I think I should be OK with the 15000 unit)

Page from the catalog I have is attached.

Oversized wire is much better than undersized !!
 

Attachments

  • Mitsubishi Page 25.jpg
    Mitsubishi Page 25.jpg
    148.9 KB · Views: 20

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,769
According to mitsu's website, min circuit ampacity is 12A for that unit (220v), add 20% to that an a 15A circuit is fine. 12-2 should be just fine.

Don't forget to look up the requirements for the indoor unit. I think mine required a 16-3 300v wire to connect it to the outdoor unit.

You do not need to add anything, the manufacturer has done that already, MCA = Minimum Circuit Ampacity, the MOCP = Maximum Over Current Protection, Per NEC art. 440 you get to wire to the minimum & install the maximum allowed overcurrent protection device allowed by the label.

The rules for A/C equipment are different then "normal" branch circuit wiring, so things that are wrong for a branch circuit can be just fine & code compliant on a A/C.
 

ixlr8

Well-known member
Joined
Sep 15, 2009
Messages
435
Location
Mid-Coast Maine---> Eastern Shore Virginia
I have the same unit, 12-2 is fine, I have similar distances. Inside unit got it's power from the outside unit and that wiring came with the unit. Although, I did have the HVAC company install the unit so maybe they are the one's who supplied the inside to outside wiring, I know I didn't. I just supplied the 12-2 to the outside disconnect I put in.
 