Nema 6-50 Receptical

manuelc

New member
Joined
Oct 20, 2010
Messages
2
I just bought a lincoln 185 tig welder. It says it requires a 50 amp circuit.
I have a 220 circuit in my shop that had a 3 prong plug (the one with the L shaped prong) I ran a buzz box off of it for years.
So I replaced my old plug recptical with a new 6-50 to match the plug that came with the welder.
Both the main panel and my sub panel have 40 amp breakers.
Will changing them to 50 amp breakers make this a 50 amp service?
I hope that doesn't sound stupid.
Thanks in advance
 
To avoid these ads, REGISTER NOW!

Motofixxer

Well-known member
Joined
Oct 10, 2009
Messages
693
In simple terms, electrical safety is only as good as the weakest link. Check the size of wire for that circuit. Sometimes it's upsized. If the wire is not rated for the size breaker you want then you can't add a larger breaker. Have to add another circuit sized properly for your needs.
 
To avoid these ads, REGISTER NOW!

jkeyser14

Well-known member
Joined
Dec 19, 2008
Messages
1,823
Location
(rural) Maryland
Welders aren't considered continuous duty and the NEC allows you run them on breakers that are sized larger than their table rating for wire (by some set percentage, I don't remember what it is off the top of my head). However, I would still change out the wire too in case something else ever gets plugged in there.
 

Killer95Stang

Well-known member
Joined
Jan 1, 2008
Messages
341
That welder only pulls 21 - 23 amps.... so the 40A breaker that's already there should be good enough... that is, as long as the wire feeding that 40A breaker is correct.
 
OP
M

manuelc

New member
Joined
Oct 20, 2010
Messages
2
Thanks for all the help guys,
I had an electrician take a look at it and he said it was OK. Wire size was
6ga copper coming off a 100 amp service to my sub panel in my little shop.
I was chasing a prob with my welder and needed to rule out the power source.
Thanks again
Manuel
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
Is there an owners manual for this machine?
That welder only pulls 21 - 23 amps.... so the 40A breaker that's already there should be good enough... that is, as long as the wire feeding that 40A breaker is correct.
Evidently Killer has seen it. If it pulls 23 it could be breakerd to 50A provided the wire is 12 or better. I suspect (if the 23 is correct) they allow for a minimum of 14 wire but the breaker would need to be reduced to 30A, also the minimums are usually single circuit in pipe so if using cable such as Romex it needs to be a size up from that. Welders are most often dedicated circuits and may be sized for specific machines, if this is a general type circuit that may be used with other equipment then requirements may be different. If I derate them I usually write on cover, welder only and the wire size used.
 