My DIY off grid 16kw Solar Project is working out great a month into operation. When the sun is shiningi have more capacity than im using and mcguyvering ways to top off the Tesla and a plug in Prius..

But i really wish to think about adding a gen transfer switch to take the "inside 200 amp panel" with lighter loads and switch in onto solar most of the time. I have a 3p transfer switch in hand that can do that. The house is very energy efficient and has led lights and mini splits all over. By coincidence the panel outside the house feeds the water heater, oven and spa and accessory building panel...

So my question is on the Neutral Bond. I think it is supposed to be bonded once and i think that happened in the outside panel. If i splice in between the house outside panel and the house inside panel the 3 pole transfer switch... I think this is what is needed. My solar is 16 kw 2 phase (110 + 110) with two MPP lv6048 in parallel for inverters).

So if i do a visual inspection and sketch out where the bond(s) are .. is there a DVOM meter test to also do to see if im not creating a disaster? What would be a danger or concern? THANKS!


beutralbond01-13.png
 
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,220
Location
Modesto, CA
Your main service pane is the only place neutral is to be bonded unless your transfer switch switches the neutral....

You dont want neutral bonded in multiple places
 
To avoid these ads, REGISTER NOW!
OP
I

inphx

Well-known member
Joined
Feb 23, 2012
Messages
1,303
Location
Phoenix/Scottsdale AZ
Thanks - i am planning to transfer neutral (3 pole gen switch) because the solar is an independent source. of the l1, l2, neutral

The ground in the accessory building.. is earth ground and i do not know for certain if the Inverters themselves internally are bonded to the earth ground, they may be. I don't know if or how that may matters in my scheme. Back at the house it would inherit the earth ground but the neutral is isolated to serve the in house panel at that point coming from the gen switch.
 