neutral wire for 3 phase

wantacoe

Well-known member
Joined
Apr 28, 2015
Messages
653
Location
Sycamore, il
I bought a Kaeser model AB 1000 air compressor. 7.5 hp, 3 phase. I was told that you can run a neutral wire to make it single phase. If true is that a permanent fix? If not is it ok just to test the compressor. I bought it at an auction "as is". I would like to know if it is any good before spending more money on it. Thanks for any info.
 

Attachments

  • IMG_4346.JPG
    IMG_4346.JPG
    230.3 KB · Views: 48
  • IMG_4347.JPG
    IMG_4347.JPG
    321.7 KB · Views: 52
To avoid these ads, REGISTER NOW!

LXCam

ALLIANCE MEMBER
Joined
Apr 23, 2013
Messages
19,147
Location
AZ
Does it have a built in vfd? Post a pic of the schematic.
 
OP
W

wantacoe

Well-known member
Joined
Apr 28, 2015
Messages
653
Location
Sycamore, il
Pics. I don't think it has a vfd.
 

Attachments

  • IMG_4380.JPG
    IMG_4380.JPG
    319.7 KB · Views: 52
  • IMG_4384.JPG
    IMG_4384.JPG
    309.8 KB · Views: 56

LXCam

ALLIANCE MEMBER
Joined
Apr 23, 2013
Messages
19,147
Location
AZ
Nope, no vfd and no it won’t work directly off single phase. You’ll need either need a vfd which is the way I’d go or a rotary phase converter. And being 7.5HP utilizing a soft start feature with a controlled unloader valve would be a good thing.

There’s a good vfd thread floating around, I’ll see if I can find it.
 

LXCam

ALLIANCE MEMBER
Joined
Apr 23, 2013
Messages
19,147
Location
AZ
Here’s where I’m sure you’ll find some good suggestions. Id dial it in better but doing it off my phone ain’t gonna happen.

 

LXCam

ALLIANCE MEMBER
Joined
Apr 23, 2013
Messages
19,147
Location
AZ
Btw, if you want to know if it works before you do more with it. Go rent a smallish generator and test it out. Most rental yards have towable 50kw units.
 
To avoid these ads, REGISTER NOW!

PoorUB

Well-known member
Joined
Mar 29, 2021
Messages
11,652
Location
Fargo, ND
Keep in mind if you go with a VFD you need to put the VFD in place of the contactor in the schematic. Most all VFD's do not like power being cut off on the output side. I would also disable the overloads as the VFD will handle that duty.
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,758
VFD’s are not well suited for phase conversion on a air compressor, a RPC, rotary phase converter would be better.
 

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
7,973
Location
Central Iowa
Yep, as stated a neutral won't fix anything. On another note, I have a customer with 2500 semi trucks on the road. About six or seven years ago, they got on a Kaeser compressor kick. I wired three 10 and two 15 horsepower units in about a six month span. Within three years, they replaced all of them except one of the 10 horse units, and the remaining unit would get replaced, but it's too big of a pita to get it out of the room that was built around it and it's only used a couple of hours a day for the paint booth. The maintenance supervisor told me they were the biggest pos ever made. I have to admit to not knowing what the problem(s) were, but that's a lot of money to spend because of small problems so it had to be a big deal.
 
OP
W

wantacoe

Well-known member
Joined
Apr 28, 2015
Messages
653
Location
Sycamore, il
Yep, as stated a neutral won't fix anything. On another note, I have a customer with 2500 semi trucks on the road. About six or seven years ago, they got on a Kaeser compressor kick. I wired three 10 and two 15 horsepower units in about a six month span. Within three years, they replaced all of them except one of the 10 horse units, and the remaining unit would get replaced, but it's too big of a pita to get it out of the room that was built around it and it's only used a couple of hours a day for the paint booth. The maintenance supervisor told me they were the biggest pos ever made. I have to admit to not knowing what the problem(s) were, but that's a lot of money to spend because of small problems so it had to be a big deal.
Ouch, Chances are mine is scrap too. Thats why I want to check it before I get in any deeper. It is either a 1996 or 99 model with 3500 hours on it, that is if the hour meter was still working.
 
OP
W

wantacoe

Well-known member
Joined
Apr 28, 2015
Messages
653
Location
Sycamore, il
On a side note, Does anyone know why these divorced tanks are made to look like a rocket instead of having legs extending from the side like most tanks?
 

Attachments

  • IMG_4388.JPG
    IMG_4388.JPG
    227.5 KB · Views: 39

pancho400cid

Well-known member
Joined
Sep 26, 2014
Messages
4,516
Location
Austin, TX
Does anyone know why these divorced tanks are made to look like a rocket instead of having legs extending from the side like most tanks?
Because for the particular manufacturer of those tanks, rolling/welding sheet steel was cheaper than stamping legs or buying legs from an outside supplier.

Looks like they made it a little extra-far off the floor for valve access or something.

..
 

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
7,973
Location
Central Iowa
Ouch, Chances are mine is scrap too. Thats why I want to check it before I get in any deeper. It is either a 1996 or 99 model with 3500 hours on it, that is if the hour meter was still working.
You wouldn't happen to know someone that has a shop with a three phase service would you? I don't know how big of a pita it would be to load it on a trailer or flatbed and take it to the power supply, but that's the most cost effective way I can think to check it out.
 
OP
W

wantacoe

Well-known member
Joined
Apr 28, 2015
Messages
653
Location
Sycamore, il
Out of curiosity, how much are you into it for?
I don't think I am in too bad of shape, about 800. It was an online auction and I missed the preview day. It was advertised as a screw compressor, that is why I bid on it.
 