OK but usually we now use GFCI recepts for economy rather than breakers...
So am I correct what I am saying that sure he can run a 12/3 to the first 1900 w two GFCI recepts... but the he CANNOT continue down the wall w a 12/3?
Correct?
Marc
Depends on the GFCI breaker style used.
If a 120/240v rated gfci cb is used - basically a 3 wire version, it will monitor both hot legs and the neutral together. It also has the downside of both ckts tripping together regardless of which ckt had the fault.
I would skip the MWBC, run conduit and 4 wires - 2 independant ckts.
Here's a link you can reference:
https://download.schneider-electric..._Name=48840-058-03.pdf&p_Doc_Ref=48840-058-03
Refer to figure #2