New concrete not as flat as I expected...

Vintage Veloce

Well-known member
Joined
Feb 27, 2015
Messages
1,076
Location
San Diego
So my new 25' x 21' concrete foundation is in. Overall, it is fairly level, as I requested.

However, there are areas that are not very flat. I know this is a manually done floor, so it won't be perfect, but how flat should I expect?

I put a 6' straight edge down and there are some areas that are more than 1/2 inch high or low.

We did use 3500 PSI concrete, so it didn't flow much, maybe there just want much "self leveling" I know the concrete finisher was nervous about getting it all done before it hardened.

Is this just what I should expect? Should I complain? I'd been thinking I might want to put tile in someday, I imagine this much wavy-ness might be a problem. But at this point what could be done? Could we pour another 1" on top to try and level it?

C
 
To avoid these ads, REGISTER NOW!

lakeroadster

Well-known member
Joined
Jan 19, 2015
Messages
5,166
Location
Central Colorado
How thick is the slab?

A 4" floor slab should have a thickness variation of no more than -1/4", +3/8", under ACI tolerances. That's a total allowable variance of 5/8".
 
Last edited:

Strouty

Well-known member
Joined
Mar 21, 2010
Messages
38,215
Location
Southern Maine
I thought the OP was saying that it was from 1/2" low to 1/2" high in 6' span. That would be an inch variation, unless it was all one direction for a specified slope then I would think that was a lot, especially if it is fresh concrete. As it cures it could become even worse.
 

LXCam

ALLIANCE MEMBER
Joined
Apr 23, 2013
Messages
19,109
Location
AZ
That's unacceptable. Did they screed the pour? or just bullfloat it?

Wait, let me take a guess at this. They only bullfloated it in one direction?.

BTW a typical standard is 3/16" between two points 10ft apart. 1/2" within 6 is a skateboard park.
 
Last edited:
OP
V

Vintage Veloce

Well-known member
Joined
Feb 27, 2015
Messages
1,076
Location
San Diego
They had a long aluminum flat thing that they pulled across the floor following the pumper, isn't that the screed? Then they bull floated a couple directions, and then they hand finished it while riding on aluminum skis.

The worst spot seems to be a high spot, maybe a bit more than a 1/2" high. You can put the 6' straight edge across it, and both ends would be about 1/2" above the concrete. Or you could push down one end, and then the other would be an 1" above the concrete. Kind of like a teeter totter.

C
 
Last edited:

LXCam

ALLIANCE MEMBER
Joined
Apr 23, 2013
Messages
19,109
Location
AZ
Flood your slab and take a picture. Since they did screed it and ran the float both directions I wonder if they just mounded up the cream or is the entire slab wavy?.
 
OP
V

Vintage Veloce

Well-known member
Joined
Feb 27, 2015
Messages
1,076
Location
San Diego
It was poured last Monday and we start the walls tomorrow morning. So it's a week old.

This is the worse illustration. I'm holding the straight edge down on one side of the high spot, so the other end is elevated. You can see the 6' straight edge is about 1" up on the far end.
i-zLphw7H-L.jpg


The rest of the 21' x 25' pad is better, this is the worst spot.
C
 

RivennHewn

Well-known member
Joined
Jun 4, 2011
Messages
10,370
Location
PNW
Outline the problem area w/ chalk. Figure out how much area you have a problem with.

Rent a diamond stone terrazzo machine for a day and grind it down.

Will leave a smooth, exposed look but if you're going to epoxy/paint/ or tile it anyway- no problem.

From what I see, I would not accept it.
 

carcajou

Well-known member
Joined
Dec 7, 2012
Messages
879
Location
SW Alberta
High is relatively easy to remedy. Even an angle grinder and concrete grinding disks will repair that. I would expect the contractor to at least take down the high spots.
 

katmat

Well-known member
Joined
Jan 10, 2007
Messages
91
If it is only at one spot, you could core drill a hole the size of a floor drain & put a drain cover on it.
 

LXCam

ALLIANCE MEMBER
Joined
Apr 23, 2013
Messages
19,109
Location
AZ
That's ridiculous, is this guy a licensed contractor or were these the Home Depot weekend warriors. From your description sounds like he let the mud get away from him and didn't work it in time. Were you there? Did they start using a lot of water to help bring the cream up when they started troweling it?
 

Strouty

Well-known member
Joined
Mar 21, 2010
Messages
38,215
Location
Southern Maine
It may be the picture, but it looks like it curls up on the edges too. Anything can be fixed, all it takes is time and money.
 
To avoid these ads, REGISTER NOW!

Roddyo

Well-known member
Joined
Nov 16, 2015
Messages
89
It looks like they screeded one end the then screeded the other wet screeding what they screeded first.

Laymans terms. Is this hump about 10 feet from one end where they over lapped while screeding the floor?
 
OP
V

Vintage Veloce

Well-known member
Joined
Feb 27, 2015
Messages
1,076
Location
San Diego
It was just dark enough that I could use my laser level out there. Much of the garage is within an 1/8". Certainly most is within +/- 1/4" in the height around the garage. There is that one area that goes to - 1/2 that I illustrated with the straight edge above.
While I don't love it, I'm can probably be OK with this.

I have no interest in any coatings. But I could imagine polishing it or maybe tiling it some day.

If I was going to make the floor flatter now, how would I do it? Can you pour another 1" on top to level it and not have that top layer crack off in 10 years? Or can you get guys who can grind and polish the whole thing to +/- 1/8" better?

C
 

pmiranda

Well-known member
Joined
Jul 15, 2008
Messages
1,504
Location
Austin, TX
Like a couple guys already said, if it's just a high spot, that can be ground down and you'll be in good shape.
 

chief ben

Well-known member
Joined
Sep 7, 2010
Messages
618
Location
Hot Springs, Arkansas
We had our welding shop floor put down 22 years ago and 6 inch thick, and fiber glass in it,
26 feet X 50 Feet, I told the guy I want it slick as a baby *** and flat so when I lay out something to weld up I didn't have to shore up anything,
and he did a great job,
And it only cost $ 2000.oo bucks back in 1994 And still No Cracks in it.
I don't know what you payed, But I think you got a bad job done,
 

Cyberbear

Well-known member
Joined
Nov 23, 2013
Messages
1,524
Location
California
1" difference in floor level is a LOT, and will require a lot to fix it. They make a floor leveling compound that is cement based that is often used by the floor covering trade. I had it used in a bathroom that had a rough and un-level floor. They came in and mixed the self leveling compound to a soupy consistency and simply poured what was needed to reach level all over. You may need to have the high spots ground down before the compound can be used.
 

lakeroadster

Well-known member
Joined
Jan 19, 2015
Messages
5,166
Location
Central Colorado
BTW a typical standard is 3/16" between two points 10ft apart. 1/2" within 6 is a skateboard park.

standard quality is 1/8 inch in ten feet

What "standards" are you guys referring to? To be a "standard" it needs to be from a recognized authority (such as ACI) and be adopted and recognized. The other option is simply numbers written into your contract with the contractor... as Bill eludes to.

What are the specifications in the contract?

You do have a contract with specifications....right?

Bill
 

LXCam

ALLIANCE MEMBER
Joined
Apr 23, 2013
Messages
19,109
Location
AZ
That time lapse is cool. They sure had enough guys to not have that happen. All it comes down too is the guy bull floating didn't do his job correctly. Had he gone both directions he would have caught that high spot. Basically they did everything ok, they just aren't very good. Hell the finisher would have felt that hand troweling but by that time there isn't too much he could have done to correct it. I'd suggest if you can live with the look to just grind it flat.
 

cshield09

Member
Joined
Oct 20, 2015
Messages
5
1/8-inch in 10 ft is actually reeeeeally flat. Doesn't help the OP much, but the ACI 117 commentary describes a 1/8" in 10 ft as "superflat", corresponding to a FF50 floor flatness when tested using the F-number system that is much more commonly used in commercial construction, at least in my limited experience/area of practice.

TL;DR - 1/8" in 10 ft shouldn't be specified for general construction because it's a really, really flat slab.


Sent from my iPhone using Tapatalk
 

mfrantz90

Well-known member
Joined
Mar 12, 2015
Messages
95
That is terrible if you ask me... I did concrete for a living for a while. There is no way we would have left a job with it like that. Or let it set like that; I would be raising hell if I were you


Sent from my iPhone using Tapatalk
 

Diesel Dan

Well-known member
Joined
Jul 21, 2013
Messages
2,458
Location
TN
Just for info, cshield, what is a typical standard for residential construction?

Something I'd like to know as well.

I have never had a contractor tell me they will pour a rough, uneven slab and provide a smooth, flat and level floor. However I have seen contractors that state they can do flat/level work and deliver a rough and uneven product.

So far I've been through at least 6 contractors and none will state a figure. They ALL claim it will be flat/level and have had no complaints.

You want to scare them off fast? Ask if they have a 8' bull float.
 

ADSR

Well-known member
Joined
Jan 12, 2013
Messages
10,713
I wouldn't accept that and neither would my customers. That floor would be coming out.
 

R. Deschain

Well-known member
Joined
Jan 7, 2016
Messages
393
Location
Seattle, Wa
I have a 1/4" variance over 30' and I am not 100% happy. I have one 1/8" high spot and a low spot that is about 4' in diameter - about 1/8" below the perimeter walls. I can live with mine as it is a garage and wood shop, but I would be seriously making noise if I were you. At the minimum, I would demand that the high spots be ground flat.
 

nadogail

Well-known member
Joined
Jan 23, 2009
Messages
31,935
Location
Coronado, CA
In the shipyards we used an epoxy compound to fill gaps between the foundations and machinery we were installing.
 

bczygan

Well-known member
Joined
Nov 4, 2009
Messages
22,002
Location
DETROIT! Arsenal of Scrappers
I used to work for a design/build architect who wrote his specifications to benefit himself.

The wood door section said "Wood doors will be installed".

Hollow core luan?

Solid core oak?

It was all up to him when the time came to install.

And every change was an up-charge.

Would you sign a contract that said "I will build you a house", with no other definition?

Bill

EVERYTHING should be specified and performance specifications should detail every variation allowed. Admitted that nothing in the world is perfect, and you pay more when you try to get closer to that goal. But if you don't specify EXACTLY the level of fit and finish you expect, then you are liable to get anything.

And you then have no bargaining chips or legal recourse.

Bill
 

Diesel Dan

Well-known member
Joined
Jul 21, 2013
Messages
2,458
Location
TN
EVERYTHING should be specified and performance specifications should detail every variation allowed. Admitted that nothing in the world is perfect, and you pay more when you try to get closer to that goal. But if you don't specify EXACTLY the level of fit and finish you expect, then you are liable to get anything.

Again, here lies the issue.
How to spec a residential finish.
 

whiteg77

Member
Joined
Apr 28, 2012
Messages
8
I had my new slab grinded (ground??) by the contractor after I was complaining about the ridge marks from each float pass. It took him a day to complete and generated loads of dust but it was really smooth after the fact. Two complaints would be that the look is not uniform and i feel that maybe the surface is now softer than it should be. The texture of the surface is flat but I have loads of traction. I never worry about my family slipping. There are products that can go on post-grinding that re-harden the surface and take care of the dust but I opted for an epoxy. The epoxy lasted 7 months and peeled off. Now I don't care as much what it looks like. Good luck to you.


Sent from my iPhone using Tapatalk
 