I have been lurking around and reading all the different discussions on adding a sub panel. I am about to add one to my attached garage, I want to add a 100 amp sub panel roughly about 50 ft from my main panel which is a 200 amp service and has about 10 open spots. After doing all the reading I am wondering if it would just be better off to run the lines I need to the garage and save some money on wire.
I am adding 3 240v outlets so I have dedicated outlets for my 2 welders and plasma cutter.
Miller 211 requires 25 amps at full power
Miller Diversion 180 TIG requires 20 amps
ESAB PCM 875 plasma requires 55 amps at full power which I will never use at home
I am wondering if I could get away with just running romex NM-B 6/3 from the main panel to outlets in the garage?
My other option is using #3 THHN and add a 100 amp sub panel in the garage and then have room to expand in the future?
Thanks