Hi All,

I just put up a 24x32 polebarn and now am going to get some power to it. I was hoping some of the electricians in the group can check my plans.

I have a 150A main panel in the basement of my house, i plan on running about 90' of 2-2-2-4 SER cable from a 90A breaker through the basement and then transition to 2-2-2-4 URD in an outside juction box on the house and then direct bury that about 30' into the barn and connect to a 100A main panel. Will add 2 ground rods at the barn 6' apart and connect both with #2 bare ground and into the panel.Will use conduit where the URD comes above ground and into the panel in the barn.

A couple questions-

Whats the best way to splice the two different wires together? and to connect to the ground rod wire mechanical lug or crimp?

Will i need an adapter to connect the neutral and ground wires in the main panel?

Does all this sound about right or is there a better way? Anything else i'll need?

Thanks in advance!
JG
 
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,030
Location
Modesto, CA
URD is NOT allowed inside structures.

#2 is way overkill for the GEC for the rods.

Use solid #6 cu.

Make sure to isolate the neutral bar in the subpanel which may require the purchasing of a separate ground bar kit.
 
OP
J

jg4660

Well-known member
Joined
Jul 30, 2019
Messages
130
Location
Western NY
Yep..The URD will all be outside except for the run in conduit to the panel in the barn.

Thanks
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
5,978
Location
NJ
URD is NOT allowed inside structures.

#2 is way overkill for the GEC for the rods.

Use solid #6 cu.

Make sure to isolate the neutral bar in the subpanel which may require the purchasing of a separate ground bar kit.

Yep..The URD will all be outside except for the run in conduit to the panel in the barn.

Thanks


That's the part that's a nope.

Consider MHF or pipe it point to point and use xhhw Aluminum.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,030
Location
Modesto, CA
Yep..The URD will all be outside except for the run in conduit to the panel in the barn.

Thanks

That will not be code compliant.

Doesnt matter that its in conduit.

Conduit does not change the insulation rating which prohibits its use indoors.
 
OP
J

jg4660

Well-known member
Joined
Jul 30, 2019
Messages
130
Location
Western NY
Ok..Gotcha. So i'll use MHF from the junction box on the outside of the house piped where above ground and to the panel in the barn. Thanks for clarifying that, didn't realize URD couldn't be used inside in conduit.

Thanks
JG
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,639
Location
Richmond, VA
Ok..Gotcha. So i'll use MHF from the junction box on the outside of the house piped where above ground and to the panel in the barn. Thanks for clarifying that, didn't realize URD could be used inside in conduit.

Thanks
JG

If you run conduit inside the house, you could use MHF end to end and avoid the splice.

If you keep the splice, Polaris connectors or split bolts are popular. Box size is set by conduit size, IIRC. So going big on the conduit will mean a very large box
 
OP
J

jg4660

Well-known member
Joined
Jul 30, 2019
Messages
130
Location
Western NY
Yea i thought of piping inside the house but the cable costs me about the same minus the extra labor of piping so i decided against it.

So what is URD used for if it cant be brought inside..pole to pedestal only huh?

JG
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
5,978
Location
NJ
Yea i thought of piping inside the house but the cable costs me about the same minus the extra labor of piping so i decided against it.

So what is URD used for if it cant be brought inside..pole to pedestal only huh?

JG

Correct - pole to ped, pole to meter, pad to ped, pad to meter where peds and meters are outside.

UNDERGROUND Residential Distribution cable.
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
5,978
Location
NJ
Yea i thought of piping inside the house but the cable costs me about the same minus the extra labor of piping so i decided against it.


JG

Jbox and terminations cost money and labor. Splices may one day become problem. For certain if they dont exist they arent a problem.

Could possibly even run conduit through foundation and never see any conduit/fitting.
 
To avoid these ads, REGISTER NOW!
OP
J

jg4660

Well-known member
Joined
Jul 30, 2019
Messages
130
Location
Western NY
One last thing...Where the 2-2-2-4 MHF comes above ground what size conduit should i use 2''? and how about the size of the junction box, i'll have the 2'' (or ?) MHF conduit coming in the bottom and the 2-2-2-4 SER cable coming into the back, how should that enter ser clamp seeing it won't be in conduit. So i need space to splice 3 #2's and 1 #4.

Thanks
JG
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,639
Location
Richmond, VA
For just protection, 2" is way overkill. 1.5" is plenty and I think 1.25 would work..not sure on the fill.

For a full run I would advocate 2" to make the pull easier,but depending on the number of bends, 1.5" would probably work fine too
 

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
7,974
Location
Central Iowa
I would check with your local inspector. Around my area in cases like this, they let us stick the urd into the panel for a sub panel. If not, I know j-boxes have already been mentioned. If it were me, I think I would use a 3R disconnect back to back with the panel then run THHN into the building. In my opinion, it would look better even though it costs more.
 

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
7,974
Location
Central Iowa
Or, how about a Quazite type hand hole close to the barn. You could make your transition from urd to thwn or xhhw there and run a minimal amount of pvc to the barn. No ugly boxes on the wall.
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,639
Location
Richmond, VA
Or, how about a Quazite type hand hole close to the barn. You could make your transition from urd to thwn or xhhw there and run a minimal amount of pvc to the barn. No ugly boxes on the wall.

URD is more expensive than MHF and running MHF requires no transitions at the barn, as long as the wire is in conduit to the panel.

Makes no sense to use URD, IMO
 

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
7,974
Location
Central Iowa
URD is more expensive than MHF and running MHF requires no transitions at the barn, as long as the wire is in conduit to the panel.

Makes no sense to use URD, IMO

I didn't pay attention to the other posts suggesting mhf. I have never heard of it before.
Is it something fairly new or have I just been missing out all these years?a

Edit. Nevermind. I just looked it up. I have seen it but didn't realize it was different than urd. I even used it on a job a coup!e of weeks ago,
but the customer supplied it. I just figured it was a different brand of quad urd than I was used to.
 
Last edited: