I have a 48x88 pole barn with a wall separating the front 32'. Adjacent to this room/wall is a 20x24 wood shop (no pex) where the wall in between is not insulated, just osb. Above both these rooms is an attic/loft, where the walls and ceiling are insulated but not the floor between. So I pretty much have 2000 sqft of floor space, with ~1280 of attic to heat. Both the woodshop and the 32x48, we'll call that the autoshop room, have an uninsulated full view 10x8 garage door opening to the interior of the non-heated portion. All the exterior walls have 2" spray foam.
The autoshop (1536sqft) has 5 loops in 1/2 pex. I have a Menard's hydrosmart panel and a 40 gal/4500 watt electric water heater, running it as an open radiant system. I've had it running for about 5 days now and have learned, it can not keep up. I think it's just simple math, too little heat for too much space. Today it got pretty cold, 21F, I set the wall thermostat to 50F and the pumps run constantly, keeping it at about 47F.
I think I need to add insulation to just heat the autoshop, but that water heater may not be able to keep up OR invest in an electric (no gas here) boiler.
What do you guys think?
yeldogt
I have a very well insulated 1600sf space and 4500w can keep it warm. Only around 15k BTU's -- is the slab insulated?
You can measure the slab temp.
I can not fully understand the space from the post ..... but 2000sf w/ marginal insulation and no insulation under the slab -- you don't have enough heat
F
fordman302
IL
Thanks for the quick reply. I should have mentioned I have 2" foam under the PEX. When the pumps are running constantly, the temp into the floor is 70F, out is 60F. I believe I set all the loops to flow .5 GPM. I have inserted a rough floor plan of the barn. The temp gun reads the floor at about 60F.
kj_mustang
Harrisonburg, VA
I have over 1600 sq foot of radiant floor heated in a very well insulated building. But I have 6 loops and incoming water temp of about 115F with a 20 degree delta return. You need more BTUs to raise that water temp.
Firebrick43
West central Indiana
First, 2" of foam is only r8-r10 at most. You need more insulation. R19 is recommended as is r38 in the ceiling. Throw in those huge heat loss doors and you probably need some where north of 100k btus. Did you do a Manual J calculation?
It is completely unreasonable to expect the pex section to heat the adjacent wood shop.
Third, how long are the loops? What size tubing? Are the loops equal length?
With 1/2" pex the rule of thumb is pretty much 1' of pex per square foot of area. Extremely well insulated areas may need less and poorly insulated need more but its not to far off. 5/8 or 3/4 can get away with less.
Also 1/2 pex loops should be under 300 feet, ideally around 250 feet. Again, large tubing can be longer.
finn
The UP, God's country
Your delta T across the floor, at ten degrees is in the ballpark, although a little smaller delta, say seven degrees, would be better.
Your temp into the floor, at 70 degrees though, is too low, which suggests your water heater heat input to the system is insufficient, ie you need a bigger boiler.
There should be a thermal break between the unheated concrete floor and the floor with the pex, to minimize thermally induced stress and subsequent slab failure, and minimize heat loss to the unheated section of the building. You’re also losing a lot of heat through the uninsulated door.
yeldogt
The 2" foam board is about R10 -- 2" of spray foam is about 14 max. Don't think any difference between the red or blue foam board. Under an on-grade slab 2" is typically recommended. Wish there were some real studies done on foam under a slab. It would be interesting to know the running costs of various possible setups.
Firebrick43
I am talking in the walls. R7 per inch is fairy tale stuff, especially applied in the field.
kj_mustang
Harrisonburg, VA
I have only 2" closed cell sprayed on the walls in half my building. No issues heating it with radiant. The ceiling and garage doors are well insulated though and again my setup has probably more pex in the floor than FordMan302's building.
tdkkart
Eastern Iowa
Not enough insulation, not enough heat input.
Rule of thumb I picked up a few years ago is that in "well insulated envelope", your floor temp
should be approx. 5 degrees warmer than your desired room temp. That's the theory, and it has proven
to be correct on my system for many years. You're floor temp is 60* and you're only getting 47* air temp.
You've got about 60,000+lbs of concrete to warm up, and only feeding it with 70* water it'd gonna take a LONG time, that 4500W heater ain't gonna do it, you're only feeding 15,000btus to the floor.
Firebrick43
You can heat any building with enough btus. 15K will do a building that size if superinsulated, my house and garage are bigger and do fine at with 15k
F
fordman302
IL
Well I slowed all the loops down from .5 GPM to about .3 GPM and within 15 minutes the water going in rose from 70F to 80F and still at 60F coming out. We'll see in the morning if that helps.
PoorUB
Fargo, ND
My numbers say you have about 1/3rd the heating capacity you need.
I am assuming about 1500 feet of tube and I would size it for 30 BTU per foot, which depending on the tubing might be a bit high. You are pumping 15,000 BTU into the and need 45,000 BTU.
F
fordman302
IL
I have 5 loops of 300' and had to cut anywhere from 10 to 30 foot off each loop, so I probably have about 1400ft of 1/2" PEX in the slab.
I checked my panel about every other hour last night (have a camera on my panel) and never caught the system on. This morning the autoshop was 50F, a reasonable 48F in the woodshop and upstairs was 47F. I still have about 5% of insulating to do and will go around with my FLIR camera and fix the cool spots, which will help with loss. I agree I don't have enough BTU's and when the weather gets below zero, that sure will show. For now, if I can keep it from freezing, I'm happy. I have a woodstove furnace I use when I'm out there working. Eventually, I'll probably have to upgrade to an electric boiler.
Thanks
jlv03
SE IA
Can you pull another electrical feed to your water heater? If so, split the top element off from feeding the bottom element and run both elements at the same time.
yeldogt
Thanks
It's hard to tell you "what you need" as far as BTU ..... I would "need" more than you because I want my shop warmer. One person can say ... I love my shop heat and another in the same shop be unhappy.
Trying to keep a space at 50 degrees is not going to require the same BTU input as it will at 65. Same if you normally have 20 degree temps and another identical shop is at 40 degrees.
Slowing down the water as it goes through the boiler will up the temp ..... it's not increasing the BTU's coming out. If the unit shuts off and the temp in the building has reached the target you want ... you have enough BTU's at those outside/inside temps.
If the boiler is running 24/7 and not getting where you want -- you don't have enough. One thing to understand is that when you wnat low temps inside -- there is a limit. It's hard to modulate inside temps when the delta of what you want is close to what's outside -- 20 degrees or so. The daytime temps will cause the floor to turn off and then it has to fully heat at night
finn
The other thing to do is look at the slab temp. From memory, mine runs somewhere between 3-7 degrees above the thermostat set point, depending on the outside temperature. Insulation quality will vary this.
It takes something in the area of a week to stabilize my slab temperature after firing up the boiler if the slab is cold soaked to the upper thirties. My boiler is probably oversized compared to yours normalized for square footage, so your system may well take additional time.
Remember, you’re not only heating the slab and air, but all of the objects in the room. The slab alone weighs many tons, and that’s all thermal mass that takes time to bring to a stabil temperature.
yeldogt
This is where a modulating boiler, constant circulation and outdoor reset comes in. You are giving the slab what it needs based on the outside temp and the curve that you have determined works after some trial and error.
Inside temp sensors (thermostats) work well as overrides .... a typically cloudy winter weather area can benefit from a thermostat to lower temps on those odd sunny days. A slab sensor can work to keep a floor "on" in other situations when temps are fluctuating widely in spring and fall.
Most better boilers that one would use in a house have these as options .... simple boilers for a garage will need workarounds. People look at constant circulation the wrong way .... modern pumps only use 20w keeping thins moving
finn
I haven’t found that my outdoor reset helps all that much with my modulating boiler.
Biggest issue with these systems is simply that the high thermal mass of the floor just doesn’t allow respond fast enough for anything but stable outdoor conditions. Think thermal inertia. The outdoor reset simply gives the boiler a head start on changing conditions. It can spool up the boiler as temperatures drop outside, or cut back the propane as it warms up, but, in the end, it’s no match for thermal inertia.
The floor sensors seem to be more like limit sensors to keep from overheating the slab than something to control ambient temperature with large fluctuations in outdoor temperature, although I suppose a lower limit set slightly below the room air target could be useful to keep the slab temperature up to improve response slightly.
Like my hvac guy who’s probably installed hundreds of systems says, they’re ok for tweaking, but don’t expect miracles.
In my case, I have, from memory, a 100 or 110 k btu boiler with an 8:1 or 10:1 turn down ratio, and a slab somewhat larger that the op has. I think part of his problem is simply that the water heater is undersized, and will take a long tome to bring the slab to the target temperature.
Patients, Grasshopper.
yeldogt
Unless your building leaks and is poorly insulated 100k Btu should be enough .. if not too much.
My new house project (if I can ever get it done) is a stone church from 1873 w/ new addition on the back ---- it's spray foamed. Some exposed stone walls for cool factor. Obviously -- tall ceilings. Foamed roof deck under the slate -- about 4". 4000sf + over 5 levels. The boiler is a Viessmann with a net of around 60k. It had no problem in PA at sub 10 degrees (coldest last year) keeping the place above 70.
With radiant you always have to think about response time. In areas where there is greater regular temp swings in 24 hours -- you have to plan for that. Same when doing radiant in more temperate climates because the system will be asked to supply fewer BTU's in the middle of a sunny day. Doing radiant in very cold climates is actually easier -- the BTU loss is constant.
If you think about my above house there are many times in the spring and fall when that space does not need the 12k minimum -- so the boiler will cycle on the primary. If you don't have a primary/ secondary w/ constant circulation the boiler has to stop.
ODR can't work w/o constant circulation and some way to modulate the input. The Germans first came out with Cast Iron that was more forgiving of lower temps. They designed these high mass boilers to fire on and off to keep a set temp in the primary -- it was an easy jump to condensing boilers and then full modulating. The idea stayed the same ,,,, I did a full ODR over 30 years ago.
The next thing people don't fully grasp is the floor. 1/2 Pex 12" apart in a 4" slab is not going to evenly heat the slab -- there will be bands of heat. If you double the Pex and place it 6" apart the slab is going to respond much quicker and with lower water. A 12" spacing in a cold climate will be easier to work with because over time the slab can stabilize and the variations needed are less. If the floor is 6" thick the problem is greater. Also when you try and keep the interior of a garage at 60 -- the input is going to be more stable and the discomfort of over shooting the target temp less of a problem.
This is why I always tell people to think about what they are heating. In a big garage it's often advisable to plan on making some areas warmer then others -- this can easily be done with more tube in one area -- or with flow control. I like to add loops to those areas -- with both Pex and manifold spaces cheap it's easy to double up the areas where you will be. This naturally makes those spaces faster to respond.
The better boilers have additional controls. My Viessmann boiler has an interior wall control -- I can change this temp and the boiler will alter it's internal curve to either make the space warmer or colder. It will also allow a space to better adapt to sun gain.
Using a wall thermostat to turn a system off can be problematic. They work when it's an odd day .... but if common you have to plen better and lower the curve ... constant circulation is often needed to get this close.
I have had to use slab sensors in some situations. I built an addition off the back of my suburban house years ago .... lots of glass with a limestone floor. Trying to control using the temp of the air was not possible throughout the winter -- the sun would heat the space and turn off the floor. The floor could not respond fast enough and it was always cold as the sun went down. The solution was to fix the floor temp with a slab and have some supplemental heat. In that case I had two tower Runtal units made that would flood the space with heat when needed. In the cold of the winter the floor was fine on ODR.
There are just too many variables. Looking at a space before you put the tubes down is very important - especially in larger or odd shaped spaces.
finn
Mine has primary / secondary loops. It has no problems maintaining the set point at -20F.
the point is simply with all that mass, the outdoor reset doesn’t seem to help stabilize temp much with wildly fluctuating outdoor temperatures.
The previous boiler was a standard low efficiency oil fired Buderus, with no outdoor reset. I don’t see much difference other than fuel consumption is lower now on a btu basis.
Same observations on my house system.
Outdoor reset is a nice to have feature, but not critical, in my opinion. I wouldn’t condemn a system without it, but wouldn’t install a new system without it either.
yeldogt
With home temps there is no way to have success over many systems w/o ODR. Wall thermostats taking only air temps are going to over shoot -- there is just too much lag. Now can you make a system work with lots of trial and error dial in setback and recovery times on a thermostat along with boiler water temp adjustments through the year .. sure.
Thick slabs with far spaced tubing just don't respond quickly -- the input temp that you have to dial in is just too great. That heat does not spread out equally .. and they over shoot. Now in a shop keeping lower temps it's actually easier ... the delta is lower and if it overshoots you are not really uncomfortable. In a house going from 72 to 78 is not ideal
Does you ODR have two curves ? I'm surprised you can't get it close.
In a mixed system I typically do install some Honeywell thermostats with both air and slab sensor ... or at least a wire to the location. The slab sensors are only $6 from Supply House. That way I can partially lower some temps .... but the rest of the house is ODR.
Also -- like I mentioned about the German boilers can also have an inside thermostat control that acts as a modifier. Even the Buderus oil boilers could be outfitted with that type of ODR
F
fordman302
IL
Thanks for the replies/help, I appreciate it.
We finished up the little areas that were not yet insulated and closed off the 8'x6' foot opening from the main floor to the attic. I think that has helped. I really won't know until we get consistent cold temps. Between the sunny days and me running the wood furnace while out there working, there is a lot of temperature fluctuation.
Right now, I have the air thermostat about 5 feet up going to a Taco SR501, so no ODR. I'll have to either place it on the floor or look for a slab thermo. Alot of times I'll kick the thermostat up, just cuz I know the HWH is at full temp and can put some heat into the floor to help get it thru a cold night.
I'm seeing the temp returning from the floor ranging from ~57 to 60, while the slab surface ranges from 58-63. I'm just amazed at how cold that water always returns, pretty much always lower than 60 degrees, even when it's first kicked on and the supply temp is 120-110 for the first 15 mins or so. I guess that's the idea, a huge heat sink that keeps a constant temp. I think I need to keep it closer to 60 than 57 to get the benefit and maintain the 50F set point.
u3b3rg33k
My advice is always insulate & air seal before you add more BTUs. you pay for insulation once, you pay for BTUs forever.
this will accomplish nothing with an electric heat source. Delivered BTU will not change with flow rate, unless you go so slow the tank starts cycling, at which point your delivered BTU is going down (even with hotter water), and your problems get worse. you'll just get a larger ∆T across your floor with a lower flow rate.
jlv03
SE IA
What thermostat are you using? I hooked up the fan connection on my Nest thermostat to the same point as the W connection on a Taco SR501. This lets me use the timed fan settings to circulate the water on occasion in the off season (with the boiler turned off, of course). I also have it programmed to run the fan (really the heat) for 15 minutes every morning so I can hear/see the system turn on during a time I know I will be home. Just a thought on how to periodically pump heat into your slab.
F
fordman302
IL
I just have a cheap $17 Honeywell, but that's interesting, so do you have two wires going to W on the Taco? I like this idea, I'll have to consider this if I get a different thermostat. I may be able to get the programming part of it done with a smart plug or switch or something if I can find or convert to low voltage.
HoosierBuddy
Southern Indiana
4.5 KW per hour X 24 hours X .10 cents/KWH X 30 days = $324/month....to hold 50 degrees. If your power is 13 cents, it goes to $421/month. This assumes your water heater can't keep up. If it can hold temperature, the hours on would drop.
I'm not a fan of any form of electric resistance heat. Spins the power meter way too fast.
yeldogt
A tank full of hot water is not holding enough BTU's to heat that slab. You are passing water through a tube surrounded by a cold slab .. It's like the cold water dispenser on your refrigerator. Depending on the GPM trough the PEX ... you may get some heat back in excess of the slab .... the idea is to match. The idea is to fully heat the slab to as low as possible .... this will often not be the case w/o ODR. You get hot bands that will indeed heat the space .. just w/ more uneven heat. Depending on the heat loss and leaking -- the slab can be anywhere between 5-10 degrees higher than target temp.
jlv03
SE IA
Yes, two wires landed on the W terminal in the Taco control board. My Thermoelec boiler has a 40A circuit breaker built into the face, so during the summer I just open the breaker but leave the 120VAC power on for the pump and Taco controller.
Did you see my post earlier about pulling another circuit for your water heater? You can double your heating capacity without switching out the tank/installing a boiler.
F
fordman302
IL
I did see that and look into it a bit, right now I'm not comfortable with rigging that up like that. If I get desperate and really do need more BTU's to keep the shop from freezing this winter, I'll reconsider.