I have an old, 1930s garage. I'm going to be tearing off the roof, rafters, etc. It's about 18' wide x 15' 6" deep. That means I can run 16' boards for the ceiling joists. It's in CA, no snow and I don't need storage in the attic, so I'm not too concerned with load. It's going to be about a 6/12 pitch. Recommendations on ceiling joist and rafter sizes and spacing?
 
To avoid these ads, REGISTER NOW!

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,680
Location
Richmond, VA
There are lots of span and sizing tables online. Is this being inspected?

Without looking it up, I would be inclined to think a 2x8 rafter and 2x6 rafter tie would work, both at 24OC. Are you installing a ceiling or leaving it open?
 
OP
D

Don_Juan

Member
Joined
Aug 25, 2015
Messages
12
It looks like I need to go 2x6 16 oc for rafter ties. Yes, drywall ceiling. I'm going to look into trusses too. Part of that depends on how long it takes to get them made.
 

billconner

Well-known member
Joined
Jul 20, 2021
Messages
6,970
Location
Thousand Islands NYS
Gable roof with ridge parallel to 18' sides, so 7'-9" rafter spans and 15'-6" ceiling joists, IRC says in for 20 psf live load - least allowed - and 10 psf dead load, SPF no. 2, 24" o. c., a 2x4 spans 8' so fine for your 7'-9" rafters. (And span is based on clear inside dimension - dimension from inside of top plate to top plate.)

Same spacing and species - a 2x6 ceiling joist for drywall - 1:240 - NO Storage at all - is good for only 14'-9". Need to go to 2x8 - 18'-9" - or a different species or spacing. You're good at 19.2" o.c. or #1 Doug fir larch.
Tables at California Residential Code on Up.Codes, down in section R802. I used tables R802.4.1(1) for rafters and R802.5.1(1) for ceiling joists.
 
OP
D

Don_Juan

Member
Joined
Aug 25, 2015
Messages
12
Yes, I saw those. So it looks like 2x8 rafter ties and 2x10x10 rafters 24oc. And to think they built this back in the day all with 2x4 rafters and rafter ties!
 

billconner

Well-known member
Joined
Jul 20, 2021
Messages
6,970
Location
Thousand Islands NYS
I would go with 2x6 if just rafter ties, and probably every other or third rafter, but hanging sheet rock on them makes them ceiling joists and deflection and cracking the drywall rules.
 
To avoid these ads, REGISTER NOW!

billconner

Well-known member
Joined
Jul 20, 2021
Messages
6,970
Location
Thousand Islands NYS
I usually try to answer inquiry's but fwiw I think I'd use 2x6 rafters and apply sheet rock to them. And use maybe 3 - 4x6s for collar ties. I just like the look of the lifted ceiling and spaced out beefy collar ties. Built an addition for my mil in 80s like this and just saw it was on the market.
 

Attachments

  • Screenshot_20240428-112529.png
    Screenshot_20240428-112529.png
    872.6 KB · Views: 9
OP
D

Don_Juan

Member
Joined
Aug 25, 2015
Messages
12
I usually try to answer inquiry's but fwiw I think I'd use 2x6 rafters and apply sheet rock to them. And use maybe 3 - 4x6s for collar ties. I just like the look of the lifted ceiling and spaced out beefy collar ties. Built an addition for my mil in 80s like this and just saw it was on the market.
Very nice! But, I'm going to keep it simple and boring with a flat ceiling.
 
OP
D

Don_Juan

Member
Joined
Aug 25, 2015
Messages
12
Existing roof and stucco gables. I don't want to cut/modify the gables for a lower pitch roof.
 

billconner

Well-known member
Joined
Jul 20, 2021
Messages
6,970
Location
Thousand Islands NYS
Which code? IBC says 4'. IRC does say 24" but also notes "other approved rafter tie methods shall be permitted." So, if this one is to be permitted and inspected, ask the building department or just submit plans showing other spacing. Or ask. If no permit and no inspection, I'd be very comfortable with the spacing I suggested. The addition in photo was permitted and inspected (albeit drive by) and is also still very plumb and level - 40 years later.

And have seen lots of buildings, especially detached garages, with sparse rafter ties. Many fine, some not so much.

Not a purely black and white issue IMHO.
 

TRWham

Well-known member
Joined
Aug 11, 2017
Messages
1,961
Location
East Cobb County, Georgia
Which code? IBC says 4'. IRC does say 24" but also notes "other approved rafter tie methods shall be permitted." So, if this one is to be permitted and inspected, ask the building department or just submit plans showing other spacing. Or ask. If no permit and no inspection, I'd be very comfortable with the spacing I suggested. The addition in photo was permitted and inspected (albeit drive by) and is also still very plumb and level - 40 years later.

And have seen lots of buildings, especially detached garages, with sparse rafter ties. Many fine, some not so much.

Not a purely black and white issue IMHO.
2018 R802.5.2 says "Each rafter shall be tied across the structure with a rafter tie..." 2021 is similar. I have not applied 2024 so not sure if it has changed, but not relevant to us just yet.
 

billconner

Well-known member
Joined
Jul 20, 2021
Messages
6,970
Location
Thousand Islands NYS
This is what I referred to. Pretty significant when code say other approved rafter tie methods shall be permitted.

2021 IRC

R802.5.2.2 Rafter ties.

Wood rafter ties shall be not less than 2 inches by 4 inches (51 mm × 102 mm) installed in accordance with Table R802.5.2(1) at a maximum of 24 inches (610 mm) on center. Other approved rafter tie methods shall be permitted.

You pulled from this section referring to ceiling joists and rafter ties perpendicular to and above ceiling joists, which may be 2x4s in all cases.

2018 IRC

R802.5.2 Ceiling joist and rafter connections.

Where ceiling joists run parallel to rafters, they shall be connected to rafters at the top wall plate in accordance with Table R802.5.2. Where ceiling joists are not connected to the rafters at the top wall plate, they shall be installed in the bottom third of the rafter height in accordance with Figure R802.4.5 and Table R802.5.2. Where the ceiling joists are installed above the bottom third of the rafter height, the ridge shall be designed as a beam.Where ceiling joists do not run parallel to rafters, the ceiling joists shall be connected to top plates in accordance with Table R602.3(1). Each rafter shall be tied across the structure with a rafter tie or a 2-inch by 4-inch (51 mm × 102 mm) kicker connected to the ceiling diaphragm with nails equivalent in capacity to Table R802.5.2.

I just believe a pretty good case can be made for more widely spaced rafter ties, as the IBC permits.
 