As soon as I get a weather break I am going to run the electrical. (metal shop building). I am trying to save as much as I can so here is the plan. A board mount for the utility that will have a 100 amp meter . Triplex 2-2-2 (direct burial) to the shop (125'), then into the shop panel. Does this sound ok? Do I need a disconnect at the shop or just penetrate the wall into the panel. Is 100 amp enough or should I do bigger?
 
To avoid these ads, REGISTER NOW!

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,441
Location
Richmond, VA
You need a 4 wire feeder and URD can't go inside a building at all. #2 is also only good for 90a, which is plenty for nearly all one man shops.

Mobile Home Feeder is a great option for this since it can go inside (in conduit) and is direct burial.

What is your location?
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
If this is a service feed from meter to a main service panel then 3 wire is okay and #2Al is good for 100A. 4 wire is required for subpanel feeder. Now if there is a breaker disconnect at the meter then the feeder to the shop panel becomes a subpanel feed and a 4 wire feeder is needed. Also the #2Al feed becomes 90A rated. Don't ask why.
I just noticed the link to the metermain you are using, that will need a 4 wire feeder to the shop.
 
Last edited:
OP
T

tycham

Member
Joined
Nov 23, 2022
Messages
21
I am in northern California. The meter box does have a circuit breaker or I can use a meter box and a disconnect
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,441
Location
Richmond, VA
If this is a service feed from meter to a main service panel then 3 wire is okay and #2Al is good for 100A. 4 wire is required for subpanel feeder. Now if there is a breaker disconnect at the meter then the feeder to the shop panel becomes a subpanel and a 4 wire feed is needed.
Yes, absolutely, I made the assumption that there would be a disconnect at the meter
 
OP
T

tycham

Member
Joined
Nov 23, 2022
Messages
21
OK. So do the panel with the breaker, 2-2-2-4 AL MHF to the shop and through the wall (conduit) , into the panel? I am familiar with Nassua and will be getting it there. I just wish they didn't immediately call and email when you visit their site
 
To avoid these ads, REGISTER NOW!

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,441
Location
Richmond, VA
OK. So do the panel with the breaker, 2-2-2-4 AL MHF to the shop and through the wall (conduit) , into the panel? I am familiar with Nassua and will be getting it there. I just wish they didn't immediately call and email when you visit their site
Disconnect/panel at the meter with two ground rods, then run to a main breaker panel, another two rods there (or ufer). In the shop panel, the neutral bar has to be isolated from the case and all ground wires

That's what I would do.
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
Are you having this inspected? Technically by the NEC the #2Al is listed as 90A when used as a branch feeder, so the feeding breaker needs to be 90A. The metermain comes with a 100A breaker. Your local inspector may allow 100A breaker on the #2Al.
 
OP
T

tycham

Member
Joined
Nov 23, 2022
Messages
21
I have foundation ground tied to the rebar in the shop, so I am all set there. A main panel in the shop. Remove the neutral bonding screw. So the meter panel with disconnect breaker, 2 ground rods, cable to panel in shop. Thanks for all the.
help. Can't wait to get off the generator and extension cord
 
OP
T

tycham

Member
Joined
Nov 23, 2022
Messages
21
Are you having this inspected? Technically by the NEC the #2Al is listed as 90A when used as a branch feeder, so the feeding breaker needs to be 90A. The metermain comes with a 100A breaker. Your local inspector may allow 100A breaker on the #2Al.
It will be inspected (California). If they want I can always change the breaker
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,994
Location
Modesto, CA
If this is a service feed from meter to a main service panel then 3 wire is okay and #2Al is good for 100A. 4 wire is required for subpanel feeder. Now if there is a breaker disconnect at the meter then the feeder to the shop panel becomes a subpanel feed and a 4 wire feeder is needed. Also the #2Al feed becomes 90A rated. Don't ask why.
I just noticed the link to the metermain you are using, that will need a 4 wire feeder to the shop.
Only when feeding a dwelling...
 