Aluminum will cost a 1/4 of that
What size/type would you suggest? It seems like there are a bevy of options for aluminum (I keep seeing "mobile home feeder" as a suggestion). My goal is:Aluminum will cost a 1/4 of that
Interesting! Thanks for the idea.
In the past I have taken pieces of 2" pipe or conduit and placed them directly on the buried line so you can see the line if you look down into it and there is room to drop a tspe measure down to verify depth. Not sure if it will fly with all inspectors but along with pics it should satisfy most.take pictures of a tape measure showing depth of trench.
May save hassles later from an inspector
What size/type would you suggest? It seems like there are a bevy of options for aluminum (I keep seeing "mobile home feeder" as a suggestion). My goal is:
* provide 60A service to barn, install 100A capable conductor
* run about 120', assume 145' max
I'm fine with aluminum as long as I'm able to install it in a way that I feel safe. I know there's a grease, and that there are special clamps to use in some circumstances.
If conduit end to end, might as well use 1—1—1—3 and get the full 100A you want. For some reason, everyone keeps recommending 90 regardless. Only solid reason I was given was if you are using mhf, as it doesn't come in 100A version, only 2—2—2—4. Nobody could give a good reason why to only run 90 if using individual wires, except "Nobody actually needs 100A, so save money". Which isn't actually a reason...
Sent from my Phone 2 using The Garage Journal mobile app
Because that is what the OP asked about. Why install 20A breakers at all, instead of just 15s? 14ga is cheaper than 12. Sorry, I dont buy the slippery slope argument. All I am saying is because you (generic you) dont think the OP needs the extra 10A, you arent going to tell him how to wire it, and only tell him about 90A options? Again, for MHF, it makes sense, as the next size up made is overkill for 100A. But the point of individual conductors is to size them for what you need. And if the OP says 100A, my answer will include what is need for 100A. I may offer suggestions for other amps as well, but when I originally asked the same kind of question over a year ago, it was pulling teeth to have someone actually answer me, instead of tell me why I only needed 90. I knew what I was wiring, had good reasons why I wanted 100 instead of 90, but everyone was trying to tell me why I was wrong instead of actually answering the question I asked. Trying to save the OP from the same aggravation.
Sent from my Phone 2 using The Garage Journal mobile app
Maximum distance would be 145 feet - best I can tell (wheel over ground, tape measure inside) it will be about 120' from main electrical panel to sub panel.You are looking in the 90 degree column, you have to use the 75 degree column because that is what the temperature rating of your terminals is. The 90 degree column is pretty much for a start in derating calculations. What is the distance of the run. And it also has been already said that there is errors in that calculator
This option would be very expensive for me. I checked with the local power company already (DTE). I would be responsible for running the conduit, paying for the copper wire from barn to pole, and paying them $12/ft (around 200 feet from the pole) to pull the wire. I also got an estimate from an electrician - quote was $8,000 to do this (not including the DTE fees).When I built my garage I had the power company run a 200 amp service line to the garage. My house has a 100 amp service and I felt it made much more sense to run a new electrical service from the street rather than come off my main house electrical service. Yes, now I have to two meter charges, but I really don't care. With a new 200 amp service in the garage, I have all the power I will need for future equipment I might decide to purchase. I seriously doubt I will ever need that much electrical power in my garage, but if I do, it is already there.
Maximum distance would be 145 feet - best I can tell (wheel over ground, tape measure inside) it will be about 120' from main electrical panel to sub panel.
I'd prefer not to go up a size - I just want to be assured that 1-1-1-6 AL XHHW-2 at 145' will be sufficient for 100A.I personally wouldn't be worried about a voltage drop at that distance, you could bump it up one size, but I wouldn't be concerned
I'd prefer not to go up a size - I just want to be assured that 1-1-1-6 AL XHHW-2 at 145' will be sufficient for 100A.
The 75C column in NEC Table 310.15(B)16) lists 100A as the allowable ampacity. I don't understand why a Type XHHW-2 would fall under the 75C ratings, and not the 90C column.
Gotcha!The temperature ratings refer to the ratings on the breakers and the lugs in the panels. 90 degree rated equipment is not common, that why the 75 degree column is used since 75 degree equipment is common. There are some cables, NM-b is one, that are considered a 60 degree cable, so the 60 degree column has to be used no matter what. The 90 degree column is allowed to be used as a starting point when you have to derate the conductors ampacity. They will let you start with the higher ampacity in your calculations
Mike Holt has some good videos on YouTube as well, he has been teaching code classes for many years.I've also been watching YouTube, been looking over the "Electrician U" channel which has been very helpful.
Certainly! In my email I stated which conductor size I wanted to use, based on the NEC tables, and wanted confirmation that I was interpreting the code correctly.Be careful about what the inspector says. They don't get to make rules, only enforce them.
I get that sometimes it is easiest to go along but if they are talking about significant added cost or work, make sure they prove the requirement.
The last guy I spoke to admitted as much (not an electrician). He suggested I reach out to the inspector - he’s had enough people who have asked to return (used) feeder because it didn’t meet the inspector’s approval.One thing to always keep in mind about supply houses, the guys working there are not out in the field for one reason or another. Sometimes you will have a retired master electrician working there, that guy might have been really good and just enjoys seeing all the same guys he saw when working or he might have been an absolute hack.
You can use 2-2-2-6 underground service entrance (USE) comes as a cable for direct burial. If in conduit use THHW individual conductors same size. Copper or aluminum may be used although copper is rated higher and more expensive.
I know that - why did the inspector say #2 AL was fine? Was he being lazy? I'm not doubting the NEC code - I'm just a little confused why he would say to use #2.As stated here already, #2 AL cannot be used for 100a to a subpanel.
If you are OK with 90a, #2 AL is fine. There is nothing to debate on that.
Buy copper if you want less money or maybe a little smaller conduit
I know that - why did the inspector say #2 AL was fine? Was he being lazy? I'm not doubting the NEC code - I'm just a little confused why they would say that.
Is there an outside terminal block one uses to connect the inside wiring to the outside then?
I know that - why did the inspector say #2 AL was fine? Was he being lazy? I'm not doubting the NEC code - I'm just a little confused why he would say to use #2.