Wiring my new garage and my electrician told me to use 2-2-4 from sub to main panel. I asked him about a ground rod or water pipe ground, he said only if i really want to? also when he wired the house he did'nt ground it, he said it is better to have it go back to the source, the pole? Am I going to die?
 
To avoid these ads, REGISTER NOW!

kngelv

Well-known member
Joined
May 25, 2011
Messages
2,230
Location
Detroit, MI
Probably won't die but he is an idiot. For your main panel you need two ground rods eight feet apart with a single ground cable connected to both plus the panel. A bond on both sides of the water meter connected back to your panel is also needed with the same size cable. Ground wire size is dependent on panel rating.

James
 

kngelv

Well-known member
Joined
May 25, 2011
Messages
2,230
Location
Detroit, MI
Oops forgot about the garage. Put a ground rod out there for the garage panel and make sure all circuits are GFI protected. BTW you should have a real electrician take a look at what this guy did just to be safe.

James
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,764
Wiring my new garage and my electrician told me to use 2-2-4 from sub to main panel. I asked him about a ground rod or water pipe ground, he said only if i really want to? also when he wired the house he did'nt ground it, he said it is better to have it go back to the source, the pole? Am I going to die?

What size circuit breaker? I am assuming that it's aluminum which is 90A max for your application. Is the garage attached or detached & are you in a no inspection area?
 
OP
A

adam64850

Member
Joined
Jul 24, 2011
Messages
5
I have a 100amp sub but i'm only going to have a 60 amp in the main. don't need that much power. In the main panel he has grounds and neutrals on the same bus, but the bonding screw is in place. So at the sub I need to install a bus for the grounds only to go on to the ground rod?
 
To avoid these ads, REGISTER NOW!
OP
A

adam64850

Member
Joined
Jul 24, 2011
Messages
5
Also in the main, when I install the two grounding rods should I take out the bonding screw and have a new bus just for the grounds?
 
OP
A

adam64850

Member
Joined
Jul 24, 2011
Messages
5
It is a detached garage 40ft from the house and not in a inspection area. oh one other thing he said run the 2-2-4 al to the main panel, no conduit. I know that is a no no so I'm ging to put in conduit.
 

Aceman

Well-known member
Joined
Jan 28, 2007
Messages
2,513
Location
Eastern Oregon
Like the other poster said, your electrician doesn't have a clue.

If you have to question his installation methods, it's obvious the person you're hiring isn't qualified.
 

Charles (in GA)

Well-known member
Joined
Jan 11, 2006
Messages
12,489
Location
50 mi south of Atlanta
Direct burial rated 2-2-2-4 or 2-2-2-2 is perfectly acceptable for direct burial. Its commonly called Mobile Home feeder, or quadplex.

You seriously need to find a new electrician, and don't take any info from this guy as the gospel. If he doesn't understand the code requirements and grounding any better than that, I wonder if he is even licensed.

In your main panel, if it has the main disconnect in it (and not before it such as at the meter) then you need to leave the ground and neutral bonded together at the main. If you have a disconnect outside at the meter, or somewhere before the panel, then the neutral and ground needs to be completely separated in your main panel.

Charles

Charles
 