Can you identify and tell me what, if anything is going on here? (lol)
Utility sink will be on the left and drain into the pipe with the spigot on the end. There appears to be a 'sleeve' with a hose clap securing it. It looks like too much trouble just to cap the pipe temporarily with a spigot...
Currently the drain pipe is connected to the shower and toilet as well as the vent system going to the roof. Outside, the drain pipe is not connected to the septic system since it doesn't exist yet. Water is not yet live. Is this for a "future" pressure test (hydrostatic or otherwise) or air gap test or something?
Thank you.
41057517761_0991d37af8.jpg
 
To avoid these ads, REGISTER NOW!

79firebird

Well-known member
Joined
Aug 19, 2008
Messages
385
Location
Victoria bc
Yes its to test the pipe for leaks they will fill the system with water tell it comes out the roof stack. Its done in all new houses.
 
To avoid these ads, REGISTER NOW!

NUTTSGT

Super Moderator
Staff member
Joined
Sep 14, 2009
Messages
50,864
Location
Northern Central Ohio
Yes its to test the pipe for leaks they will fill the system with water tell it comes out the roof stack. Its done in all new houses.

Interesting, never seen that done before.


So they hook a hose to the spigot and "back fill" the system ? I would hope they put a Fernco cap or glue a cap on the drain at the lowest point at the exit to prevent the water from escaping ?
 
OP
D

desert4wd

Well-known member
Joined
Feb 9, 2008
Messages
66
Location
Oregon
Thank 'you Everybody.

Northislander - all is good plus you answered another 'curiosity' I had!
79firebird - Thanks for the answer, also for including the mention of the roof stack remaining un-capped. I believe that small point is what was throwing me off as far as reaching a seal for pressurization. I understand that even though the system is passive, it still needs to perform as required.
NUTTSGT - I'm sure your last question is the case. The drain at the lowest point is exposed outside.
 

kbs2244

Well-known member
Joined
Nov 11, 2006
Messages
14,065
The pressure side is tested at 100 PSI for 24 hours.
The waste side with water to the roof for 24 hours.

That is why a new build toilet flange will often have a "knock out" blocking the hole.
 