I wanted to have these in the garage as the end result:
240V 40A (for welder, NEMA 6-50P receptacle)
120V 20A lift or power tool (but not the same time)
120V 20A (120V Air conditioner)
1) Should I have electrician put in a subpanel, the run the new receptacles off it.
2) or, use 20 40-40 20 breaker outside in the main then conduit into inside.
considerations:
I would like to take as little slots from the main where this is coming from, but I think both options would occupy just 2 blanks, with option 2 being a quad breaker.
With the subpanel, the cost will be higher (probably, much higher for professional install) and you are not allowed to put items or shelves in front to block access to the subpanel. Taking up that space is kind of a big deal for the amount of space I have in the garage.
One thing I did not think about is the wire fill rate in EMT, especially for option 2 , for 2 x 8 awg + ground 4 x 8 awg + ground?
240V 40A (for welder, NEMA 6-50P receptacle)
120V 20A lift or power tool (but not the same time)
120V 20A (120V Air conditioner)
1) Should I have electrician put in a subpanel, the run the new receptacles off it.
2) or, use 20 40-40 20 breaker outside in the main then conduit into inside.
considerations:
I would like to take as little slots from the main where this is coming from, but I think both options would occupy just 2 blanks, with option 2 being a quad breaker.
With the subpanel, the cost will be higher (probably, much higher for professional install) and you are not allowed to put items or shelves in front to block access to the subpanel. Taking up that space is kind of a big deal for the amount of space I have in the garage.
One thing I did not think about is the wire fill rate in EMT, especially for option 2 , for 2 x 8 awg + ground 4 x 8 awg + ground?