New two post lift motor not working at all
Macintosh
Just finished installing an Advantage 2 post lift.When I went to power up the motor it wont do anything. 240 going in 240 going to motor when i push the contactor.Lift company said it was the capacitors,I tested the capacitors and they were in spec.Ran 12 gauge 3 wire two hots and a ground.Motor is totally silent...thanks for any help.My cousin is a union electrician and we are stumped.
Macintosh
Thanks, thats really all I needed to know before I call the lift company tomorrow. Just wanted to confirm. Disappointing all that work installing the lift and then it wont work. I had 0 help.
MBfreak
MEMBER EMERITUS
Linkoping , Sweden
Apply 220 V directly fused at 6 A to the motor leads for 1 second.
If it runs, circuits feeding are faulty
If it does not ru or hum, motor is faulty.
WORK SAFELY.
Ola
finn
The UP, God's country
Are you sure the motor is wired correctly?
I have two Advantage four post lifts. the larger, 11k lift came with a power pack wired for 240 v.
The smaller, 8k lift came pre wired for 120v, but Advantage offers 240v for an upcharge. Strangely, although the powerpack was wired for 120, the box said 120/240, so I presume they simply rewire the motor for the higher voltage. If so, my money is on there being a loose wire, or misplaced wire from the rework.
Mine both work flawlessly, and the power packs look to be of higher quality than my BendPac, which is a few years older.
I never did rewire the smaller lift to 240. It’s fast enough in the 120v configuration for my purposes.
Macintosh
Here's some pics for now
Macintosh
I tested at L2 and L3,both read 123 volts each.the white and black wire combined are over 220.
testing from line to ground doesnt tell us anything. you need to test line to line
also testing on the line side of the contactor doesnt tell us anything other than you have power at the line side of the contactor. you need to test on the output side of the contactor. should be T2 and T3
Macintosh
I did test on both sides,with the contactor pushed in the meter reads 123 V on each wire to the motor .
Macintosh
Heres some hopefully better plcs.l hard wired it,safety switch not hooked up yet.
justsam
Penngrove, California
When you say on each wire to the motor, just at what two points are you measuring? Please confirm that you are seeing 240VAC across the black and white wires coming from your panel, this would be L2 and L3 on the contactor, and T2 and T3 with contactor activated.
Macintosh
This is how I measured the wires coming from the panel
Norcal
If the OP used a twin/tandem breaker & it not a GE there is no way to get 240V, seeing the picture it's a Siemens panel & need a Quad breaker, use a Siemens ONLY, BR breakers are not UL classified for use in competitive panels & so there are two reasons to get rid of the BR/Zinsco II breakers
BillK
Beautiful Southern Maryland
This breaker only has one slot
So there is your answer. Need to call your union electrician back. That breaker is giving you two separate 120 circuits. That IS NOT the same as a single 240. Only other choice would be to use one side of the breaker and wire the lift for 120 v. if that is an option.
Macintosh
Thanks, I sent my cousin a picture of the current breaker, he said it would work. I will get the right breaker and post back.Thanks again!
AA/FC
That is not a 2 pole breaker. The proper 240 volt breaker will require 2 slots in the panel. Looks like you only had one slot available.
again, measuring line to ground (which is how u get 123v) tells us the wrong info because you could be connected to the same ungrounded conductor in the panel. this means that there isnt 240v potential and thus the motor wont run.
you need to be measuring line to line at the motor. if youre not getting 240v then that is your issue.
Here's a picture of the breaker, maybe the wrong type. this is a miniature type breaker.
thats your issue. that is a tandem breaker with only 1 stab. it will only give you 120v on both legs. you need a double pole breaker
had you followed my direction in post #11 you wouldve figured this out all ready
Macintosh
Its Alive! Went to town and got the right breaker.Got it resolved fast enough for my pace.Thanks for all your help.Will get it button up and post back.THANKS again
PCustoms
VT
What's the 100A on the left and 40A on the right feeding?