DaffyJeffy
Member
Hi everyone. I've been lurking on here for a while and I finally need your help. I'm building a 22' x 34' barn next to my home (which I spent the last four years building). I need to run power from the 200A main panel in my house to the location where the barn will be built. I wired my own service entrance for my house and did all of the electrical work (no contractors were involved) and I passed my inspection (by a state inspector) so running a sub-panel is within my abilities.
The total conductor distance is 80'. I've priced different conductors and I'm going to be running 2-2-2-4 Aluminum Type Use-2, RHH, RHW-2. I know many prefer copper, but I don't have a problem with Aluminum (my main service entrance is SER Aluminum after all).
USE can be buried directly and I have nice, soft, sandy soil so that's what I intend to do. It's my understanding that I can simple sleeve these conductors in 1-1/2" PVC conduit from 24" below grade up to the point of entry in the wall where there would be a LB fitting. Is that correct?
Now here's where it gets tricky: Since these conductors are listed RHH+RHW-2, I believe they can be run inside the home (whereas a non-flame retardant aluminum conductor would need to transition to an appropriate conductor in a J-box OUTSIDE the house). Is this correct and if so, do they need to be in conduit in the short distance inside the wall cavity to the main panel? If so, how the heck do I make a 90 degree turn in a 5-1/2" wall cavity?
Finally, I'm not entirely sure what size breaker I should use in the main panel. I'm finding contradictory opinions. I don't think I need to make adjustments for the 80' run but could be wrong. Some seem to say that I can use a 100A breaker, others 80A. I only really need 60A but want the largest size allowable. THANKS!
The total conductor distance is 80'. I've priced different conductors and I'm going to be running 2-2-2-4 Aluminum Type Use-2, RHH, RHW-2. I know many prefer copper, but I don't have a problem with Aluminum (my main service entrance is SER Aluminum after all).
USE can be buried directly and I have nice, soft, sandy soil so that's what I intend to do. It's my understanding that I can simple sleeve these conductors in 1-1/2" PVC conduit from 24" below grade up to the point of entry in the wall where there would be a LB fitting. Is that correct?
Now here's where it gets tricky: Since these conductors are listed RHH+RHW-2, I believe they can be run inside the home (whereas a non-flame retardant aluminum conductor would need to transition to an appropriate conductor in a J-box OUTSIDE the house). Is this correct and if so, do they need to be in conduit in the short distance inside the wall cavity to the main panel? If so, how the heck do I make a 90 degree turn in a 5-1/2" wall cavity?
Finally, I'm not entirely sure what size breaker I should use in the main panel. I'm finding contradictory opinions. I don't think I need to make adjustments for the 80' run but could be wrong. Some seem to say that I can use a 100A breaker, others 80A. I only really need 60A but want the largest size allowable. THANKS!
My LB fitting would be right next to (practically touching) my meter box. I don't see a problem with that. Any reason why I can't have this fitting right next to a meter box? I should be good to go. Thanks everyone for the ideas and suggestions.