When running a vertical exhaust up and out of a 12/12 pitch roof, what determines the needed height of the exhaust pipe above the roof? Is it a specific height or a relationship with the peak?
Without opening the code book, I believe here it needs to terminate 24" higher then anything within 10'.
So on a 12/12 roof, you would need to have a 12' stack? A 10' stack would be 10' from the roof (equal length legs of an equilateral triangle on a 12/12 roof) so add 2' to be 24" higher and I need a 12' stack sticking out of my roof? That would look awfully stupid. If that is the case, I will look into a different heating system.
Hopefully someone else can chime in and either verify this or tell me a better option.
The 10' rule used to be used as a rule of thumb for wood burning, I believe. The book I have shows 4' above the roof for a gas appliance on a 12/12 pitch.
Here is the one from the International vent code, i believe California requires 5'.
No sparks from a gas fueled heater. The op says Ng, so the 4' would suffice
OK - 4' sounds much more reasonable. I would have gone with a different system before putting a 10' stack out the roof.
No sparks from a gas fueled heater. The op says Ng, so the 4' would suffice
It depends on what codes the AHJ uses and if in fact you want to be code compliant. It is as I stated here in NJ. I don't know the code structure in KY, but I suspect it reads similar. We are under the IFGC. Here is what it states:
503.5.4 Chimney termination. Chimneys for residential-type or low-heat appliances shall extend at least 3 feet (914 mm) above the highest point where they pass through a roof of a building and at least 2 feet (610 mm) higher than any portion of a building within a horizontal distance of 10 feet (3048 mm) (see Figure 503.5.4). Chimneys for medium-heat appliances shall extend at least 10 feet (3048 mm) higher than any portion of any building within 25 feet (7620 mm). Chimneys shall extend at least 5 feet (1524 mm) above the highest connected appliance draft hood outlet or flue collar. Decorative shrouds shall not be installed at the termination of factory-built chimneys except where such shrouds are listed and labeled for use with the specific factory-built chimney system and are installed in accordance with the manufacturer's installation instructions.