If you run NM cable to a wall mounted box and if you want to protect the section of cable that is ran on the wall with EMT, what is the best way to protect the cable as it enters the EMT? I know that is would be best to mount a junction box and transition from the NM to THHN/THWN, but sometimes running the NM directly into the EMT makes for a much cleaner and simpler installation. What I wonder about is the use of these NM to EMT connectors.
They are UL listed, but I wonder if you use them, does this then make your EMT a close conduit system, and then you would be required to de-rate the wire. So the 12AWG NM would not be rated for 20 amps then?
They are UL listed, but I wonder if you use them, does this then make your EMT a close conduit system, and then you would be required to de-rate the wire. So the 12AWG NM would not be rated for 20 amps then?