No flames from the burners ?

pauls340

Well-known member
Joined
Jan 27, 2009
Messages
321
Location
North of Motown
Mounted a 50K btu Ducane furnace, horizontally up in the garage storage. Everything seems to work fine, thermostat, gas flow, pilot light, blower, all but no flames coming from the burners...any ideas? Thanks.
 
Last edited:
To avoid these ads, REGISTER NOW!

bonneyman

Well-known member
Joined
Apr 22, 2010
Messages
8,857
Location
Desert SW
What type of igniton does it have? Intermittent spark, hot surface, or direct spark? Does the pilot light, and no burner at all - or does the burner try to light, but then go out? Need a little more info.
 

wbrian63

Well-known member
Joined
Mar 31, 2010
Messages
843
Location
Houston, TX
There should be at least 2 thermal overload switches - one in the heat exchanger area, one in the box where the flue connects.

You should be able to see the flue switch, the heat exchanger will be buried up in the case, but 2 wires should exit the case near the top of the exchanger.

It's possible on newer models that all these wires are buried up inside - I dunno.

The switches are wired in series into the main gas valve. Check each one across the poles with a continuity tester - at room temp, they should show no resistance. You could bypass these switches to test, BUT DO NOT LEAVE IT THIS WAY - they are a vital part of the control systems to prevent a runaway furnace in case of a thermostat failure.

Also - you need a signal from a thermostat to trigger the gas valve to open and ignite the burners - check to make sure the transformer is putting out (I think) 24v. Older units have an external transformer - newer models I believe have the transformer integral to the control panel, which is probably inside the case.

Finally - make sure the gas valve is turned to "on", and not just "pilot". Some of the valves are hard to read as to what is "on" and what is "pilot".

Hope this helps.
 
To avoid these ads, REGISTER NOW!

cowboyjosh

Well-known member
Joined
Mar 11, 2010
Messages
1,066
so is it like a UDAP power vented Reznor type heater? https://www.rezspec.com/catalog-udap.html if so, check the pressure switch in addition to the thermal overload switch. Again you can disconnect the wires from the pressure switch and short them, but don't leave it this way, but if there is a pressure switch and shorting the wires allows the unit to fire and work, find out if their is a blockage in the heat exchanger or vent / flue pipe.
 