No flow in radiant heat loops?

Oe478

Member
Joined
Dec 7, 2013
Messages
11
Location
Ct.
Hey everybody new here 1st post but have gotten lots of good info from site,anyway i have a radiant system in my garage which is t26x40 with 12' ceilings & r19 in walls & ceilings,the system is 4 loops of 1/2" pex app. 300'long with a 11kw titan tankless water heater for heat with rifeng manifolds,spiro air eliminator, taco 009 pump,&a radiant 12lb. Expansion tank. It does work but the flow meters show 0 flow & the return temp is 35-40 degrees cooler than supply so im thinking that theres obviously some flow through loops , have purged air twice btw,and mo change to flow meters.just kinda stumped at this point.
 

Attachments

  • image.jpg
    image.jpg
    135.8 KB · Views: 111
To avoid these ads, REGISTER NOW!

HummerJack7

New member
Joined
Jul 7, 2009
Messages
2
Turn the water supply on from the blue pex and then open the green water hose into a bucket while the circulating pumps are on. If it spits, you have air. When it runs a steady stream most of the air will be out. You will still have to bleed the expansion tank bleeder. *Make sure there is at least 12-15psi in the tank.

http://www.masterplumber.net/expansion_tank.htm

If the the pressure return flow is still low it cold be ice in the line or an an air lock further down the line. You could test each circuit loop by turning them all off and then turn one on and record the flow rate. Then repeat for all four loops.
 
OP
O

Oe478

Member
Joined
Dec 7, 2013
Messages
11
Location
Ct.
I posted more pics but they didnt come up for dome reason, ill try again. Right now its just straight water in it, it hasnt been real cold here & its 50 in the garage so pretty sure its not ice.thanks for quick replys.
 

Attachments

  • image.jpg
    image.jpg
    132.4 KB · Views: 86
OP
O

Oe478

Member
Joined
Dec 7, 2013
Messages
11
Location
Ct.
Trying to post more pics.
 

Attachments

  • image.jpg
    image.jpg
    140.7 KB · Views: 53
OP
O

Oe478

Member
Joined
Dec 7, 2013
Messages
11
Location
Ct.
Sorry for all the posts but i can only post 1 pic at a time for some reason.
 

Attachments

  • image.jpg
    image.jpg
    136 KB · Views: 49
OP
O

Oe478

Member
Joined
Dec 7, 2013
Messages
11
Location
Ct.
The blue is just regular pex but the loops are oxygen barrier pex.
 
OP
O

Oe478

Member
Joined
Dec 7, 2013
Messages
11
Location
Ct.
Oh,i forgot about that white pex, yes its only regular plumbing pex.
 

Champ49

New member
Joined
Mar 17, 2013
Messages
3
Location
NW Ontario
I have the same manifold, with no instructions, and it took a while to figure out the red rings lift up to allow adjustment of the flow. They came pretty much closed.
 
To avoid these ads, REGISTER NOW!

anthony666

Well-known member
Joined
Dec 29, 2007
Messages
987
Location
kirkfield ontario
no, i think it probably needs a good high pressure purge .. the plumbing pex will bite you in the *** later when your pumps seize and the boiler rots out
 
OP
O

Oe478

Member
Joined
Dec 7, 2013
Messages
11
Location
Ct.
Ya,the instructions arnt great to say the least,the only way i can even get the meters to show any flow is to totally shut off 2 loops then the other 2 will show about .25gpm, otherwise theyre all about half full with water but the little red plungers dont register any flow.and yes iguess another purge couldnt hurt either.
 

Spire

Well-known member
Joined
Apr 5, 2006
Messages
125
Location
Kenai, Alaska
I have those same manifolds and found that the little red plastic thing in the flow meters have a casting burr (for lack of a better term) that causes them to stick.

You will have flow, but the red guy will not lift accurately.

Unscrew the flow meter part (its pressure containing, block in the manifold first), pull them apart and cut or sand the burr off and they will move much more accurately.
 
OP
O

Oe478

Member
Joined
Dec 7, 2013
Messages
11
Location
Ct.
Oh, i guess i could try that too,never really thought about taking those apart but at this point i dont have anything to lose,i guess thats what u get for $139.99 these days.
 

atotalnincompoop

Well-known member
Joined
Apr 9, 2006
Messages
222
Location
thunder bay
i have a similar manifold, my flowmeters dont show anything, the little red discs are just stuck at the top of each one. mine didn't have any instructions regarding adjustment, i email the vendor and ,go figure, got no response:sad:
 
OP
O

Oe478

Member
Joined
Dec 7, 2013
Messages
11
Location
Ct.
I took flow meters out , they seem to move freely, didnt really see a burr on them, maybe theyre just junk& dont work.
 

Attachments

  • image.jpg
    image.jpg
    127 KB · Views: 31

HiItsMeJimmy

Well-known member
Joined
Sep 1, 2012
Messages
66
I have the same manifold! Had them cranked all the way in clockwise for 3 days... had no flow in any loops. Cranked them all the way out counterclockwise and gauges began to read.
 

The_Hun

Member
Joined
May 11, 2013
Messages
22
Don't forget that a lot of these manifolds also have flow adjusters on the cold return side of each loop on the manifold.. Make sure those aren't all shut too..
 