Wow, just WOW! Now before you all get into a major ******* match and want to electrocute each other take a step back. What you are describing is seen over and over and over in homes. Sparky or handyman, from the older days, runs the romex up to the ceiling box, which happens to be one of the older fiber boxes, or a plastic box. He figures, hell, I'm using a non-metallic box, goes to a ceiling light, or fan no place for the ground wire on that fixture -- SNIP. Problem solved.
I cannot begin to relate how many boxes I've come across where some dumb handyman or an old school sparky clips the ground wire on a fixture where there is no landing area for it. Wrong thing to do, yet was done all the time.
The solution? Go back into the box. Check the end of the romex coming into the box very very carefully. I'll be money there is a stub of a ground wire in there. If there is, pull the romex cable further into the box, there should be a bit of slack, and wire nut a piece of ground wire to it and finish up as usual.
Hope this helps.
JimDon