this is the short version
just go back to the basics isolate and test each component (the 8' section, the service panel, the breakers) separately starting at the 8' 2-2-2 make sure there is nothing grounded / broke / shorted in the wire that he can't see. that is continuity test with power OFF.
2 continuity test here.
no beep test. POWER OFF, meter to continuity. assume you have red black white for your 2-2-2, and RMC (rigid metal conduit)
test between
white-red , white-black, white-ground, red-black, red-ground, black-ground. it should not beep.
beep test.
power off meter to continuity
jumper two wires at a time on one end and test on the other make sure you get beep.
go through all combinations.
continuity test your service panel make sure you didn't accidentally screw in something that shorted the hot to ground/neutral.
continuity test on your breakers make sure they have that continuity beep when it is on.
assuming you know the basic electricity safety.
Then with the power on, and do a voltage test, after you put back everything. Test if you see 120 ish between each of the hots and neutral, 240 ish between two hots. at the service panel legs.
if all these checked out then you can rule out it's your 8' and service panel, but you have some where else shorted wires and your fuse is not blowing.