If you put the cover back over the filter, I assume the noise remains? It sounds like something is vibrating... like when kids put a piece of grass between their fingers and blow through it.
Is the filter air flow directional? Have you tried flipping it or rotating it?
I couldnt get the video to work but from the description and the filter looking like its halfway out, does sliding the filter in and out change the sound? I have run into this sort of thing before, I'm guessing you have a variable speed fan motor, they vary speed to get the right amount of air through the furnace and if the ductwork is undersized the motor works very hard to achieve the airflow. This is very bad, not just annoying. It will cause premature failure of the motor and possibly the heat exchanger if its restricted enough. Hopefully your installer knows a thing or three about static pressure and can offer some options, likely will need more return air, that's usually the problem. But I'm just some guy on the internet that can't get the video to work so I might be way off.
It's noise caused by the change in static pressure, a filter severely restricts the airflow. I have customers ***** all the time in new homes that their zoned system sounds funny, and its due to the dampers and the static pressure. Might have your HVAC guy check the blower speed and give everything a once over.
I guess this is what happens when you put a new system in a old house with Old ducts. I did install a new return larger than the original. I am wondering how bad it would be to run with a less restricted or no filter?
I couldnt get the video to work but from the description and the filter looking like its halfway out, does sliding the filter in and out change the sound? I have run into this sort of thing before, I'm guessing you have a variable speed fan motor, they vary speed to get the right amount of air through the furnace and if the ductwork is undersized the motor works very hard to achieve the airflow. This is very bad, not just annoying. It will cause premature failure of the motor and possibly the heat exchanger if its restricted enough. Hopefully your installer knows a thing or three about static pressure and can offer some options, likely will need more return air, that's usually the problem. But I'm just some guy on the internet that can't get the video to work so I might be way off.
It's noise caused by the change in static pressure, a filter severely restricts the airflow. I have customers ***** all the time in new homes that their zoned system sounds funny, and its due to the dampers and the static pressure. Might have your HVAC guy check the blower speed and give everything a once over.
it sounds like air restriction. try using a 1" filter. have your contractor measure the stratic pressure across the filter then across the filter and the outlet of the unit.
Have you removed the filter and run it to verify it is actually the filter causing the noise?
Try a different style filter that has less air restriction.
Put in a cheap 1" filter with lots of airflow and see what happens.
Then apply that logic and get appropriate "block" filter like the one you have now (ie except better flow filter).
My old house only had 1" space and we installed an electrostatic filter housing that used affordable cut-to-size filter material. It really worked as it grabbed up the dust and needed changed every couple months.
Good luck with resolving your noise / airflow problems.