Non grounded gfci’s in a kitchen.

acer66

Well-known member
Joined
Dec 4, 2010
Messages
4,443
Location
Western North Carolina
Hi there,

Helping a friend selling her 1947 house in western NC which I think is still under NEC 2014.
Home inspector pointed out the gfci’s without ground, they have the proper sticker on them, that were put in by some prior owner to replace two prong receptacles as unsafe.

As far as I know that is a code approved method of replacing 2 prong receptacles but does also apply to kitchen counter top receptacles within 6’ from the sink?

Thank you.
 
To avoid these ads, REGISTER NOW!

Terry D

Well-known member
Joined
Mar 25, 2015
Messages
2,202
Location
St. Louis, MO.
There is nothing wrong having a GFCI on a 2-wire system. The GFCI does not need a ground to function properly. The GFCI monitors the current coming in and out of it. If there is a 5ma difference, it will trip. It is completely legal to have a 3-prong GFCI on a 2-wire system
 
Last edited:

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,257
Location
Modesto, CA
There is nothing wrong having a GFCI on a 2-wire system. The GFCI does not need a ground to function properly. The GFCI monitors the current coming in and out of it. If there is a 5ma difference, it will trip. It is completely legal to have a 3-prong GFCI on a 2-wire system

:+1:
 
OP
A

acer66

Well-known member
Joined
Dec 4, 2010
Messages
4,443
Location
Western North Carolina
Just another idiot home inspector.

He also mistook a utility line crossing the property to feed properties in the back with the one feeding the house in question.

Following was his remark on a properly installed two prong receptacle.
“ An equipment ground provides an extra safety feature to prevent electrical shock hazards and property damage. A licensed electrical contractor should be consulted for a complete evaluation to determine the significance of this concern and make necessary repairs to correct defects and prevent safety hazards.”
 

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
23,684
Location
VT
He also mistook a utility line crossing the property to feed properties in the back with the one feeding the house in question.

Following was his remark on a properly installed two prong receptacle.
“ An equipment ground provides an extra safety feature to prevent electrical shock hazards and property damage. A licensed electrical contractor should be consulted for a complete evaluation to determine the significance of this concern and make necessary repairs to correct defects and prevent safety hazards.”

Translation: any moderately educated individual can put together that grounded outlets are required now. But since I have no specific skills I am just looking at the missing hole on the recepticle and noting that a true professional should evaluate.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,257
Location
Modesto, CA
A ground wire only provides safety for a grounded appliance or utilization equipment.

The ground terminal on an outlet does diddly for 2-wire appliances and equipment
 
To avoid these ads, REGISTER NOW!

reader2580

Well-known member
Joined
Dec 31, 2014
Messages
14,652
Location
Minneapolis, MN
Home inspectors seem to think that every house should meet the latest NEC even if the house was built in 1947 and met code when built. The buyers see the electrical recommendations from the home inspector and think that recommendations mean the seller must fix those items.

Buyers who are buying a 1947 house need to understand that a 1947 house is not going to be up to modern "standards". Lots of home inspectors include things in reports on older houses that met code when built and are not required to be upgraded to modern code as long as not touched.

I think in some cases it would cost less to tear down and rebuild an older house than to "fix" everything a home inspector says is not correct. If buyers are looking for a modern house that meets every current building code they should be buying a new 2020 house.
 

Jim greengo

Well-known member
Joined
Sep 3, 2018
Messages
7,415
Location
Behind my house
A ground wire only provides safety for a grounded appliance or utilization equipment.

The ground terminal on an outlet does diddly for 2-wire appliances and equipment

Exactly.
If I had a dollar for ever obvious code violation I saw a home inspector walk by to write up some trivial bs I'd be rich!:lol:
Theres no license required by those clowns in the state of nebraska,i remind them that my licenses trump their 4 hr online class they took from an online home inspector diploma mill!
 
Last edited:

Innovate1

Well-known member
Joined
Jul 28, 2014
Messages
4,330
Location
Illinois near St. Louis, Missouri
Inspectors don't always know the details of things. If it were me before I got an electrician involved I would write a note to explain that this is perfectly acceptable by code and safe and note the section of the NEC that covers it with the NEC item quoted. Might save you an electrician bill.
 

Jim greengo

Well-known member
Joined
Sep 3, 2018
Messages
7,415
Location
Behind my house
Home inspectors seem to think that every house should meet the latest NEC even if the house was built in 1947 and met code when built. The buyers see the electrical recommendations from the home inspector and think that recommendations mean the seller must fix those items.

Buyers who are buying a 1947 house need to understand that a 1947 house is not going to be up to modern "standards". Lots of home inspectors include things in reports on older houses that met code when built and are not required to be upgraded to modern code as long as not touched.

I think in some cases it would cost less to tear down and rebuild an older house than to "fix" everything a home inspector says is not correct. If buyers are looking for a modern house that meets every current building code they should be buying a new 2020 house.
Exactly.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,257
Location
Modesto, CA
The inspectors opinion depends on who is paying some of them.

bingo

my friend got screwed on a sale because the buyers inspector wrote up all kinds of **** that was BS and my friend needed to sell due to a divorce. he had no choice but to take a hit on the price because of this BS
 

nadogail

Well-known member
Joined
Jan 23, 2009
Messages
32,362
Location
Coronado, CA
I have been called to the home of a rookie home inspector who diagnosed an electrical problem in his own home.

He paid my employer for my teaching him how to properly use his test equipment. Having a Mail Order Diploma, does not make you a competent home inspector.
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
Owners, especially landlord flipper types are just as bad. Well the guy said it was good,, does this look right, Ray Charles could tell. Whole house on 3 30A fuses with a fistful of wires hanging out, no cover cause the wires all hooked on, kt wire poked in no connectors. I don't think to get pic sometimes. 2 little strands of N left at weatherhead, about number 16 if that.
Realtor found an inspector to sell it. Everything in the house broke except the furnace, put a new toilet on to work in the place.
Owner looks at me, says guy inspected it,,, I said, got nothing to do with me, don't care what he said, cost 15 large to fix it.
 
Last edited:

Jim greengo

Well-known member
Joined
Sep 3, 2018
Messages
7,415
Location
Behind my house
I have been called to the home of a rookie home inspector who diagnosed an electrical problem in his own home.

He paid my employer for my teaching him how to properly use his test equipment. Having a Mail Order Diploma, does not make you a competent home inspector.
Yep.
 

Terry D

Well-known member
Joined
Mar 25, 2015
Messages
2,202
Location
St. Louis, MO.
Cant tell you how many times a home inspector has told the homeowner that their older split buss panel was a violation and had to be replaced. I go there to look at it, and told them no violation. As long as there is 6 or less brekers on the top half, it is completely legal.

Sent from my SM-G960U using The Garage Journal mobile app
 