Many 1980ish CNC machines from Japan ran on Dyn connected 3 phase 200 V on the secondary with the n point earthed.
Used adaption XF, which often had several tappings on the D. Rating 3-7 kVA. Now available for scrap price ( at least in Sweden).
Most of these machines are ruminating in "second hand " CNC places.
Go to a good place for used machinetools, and you may find the transformer that you need.

Ola
 
To avoid these ads, REGISTER NOW!

AZ Garage

Well-known member
Joined
Sep 23, 2009
Messages
82
Location
Mesa AZ
For Spec Suites, we typically have either a 200 or 400A 277/480V 3-Phase 4W transformer for lighting and HVAC, plus other warehouse equipment.

We use a 75kVA step-down transformer to a 225A 120/208V 3-Phase 4W panel.

Anything other than that is a special request.
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,856
Location
NW Iowa
A lot of places with 480v actually have fairly minimal 120v load. All the lighting is 277. Lots of other stuff can be 480v.

If you have mostly 120v load you probably get 208Y120 unless the place is huge.
 

BreeStephany

ALLIANCE MEMBER
Joined
May 19, 2012
Messages
865
Location
Oregon
So buildings wired for 480/277 "Y", where do the get their 120 from ? Big *** transformer ?
Yes, in a building with 480/277 3ph incoming power from the utility, a breaker rated for the load of the 480V 3ph primary / 120/208V 3ph "wye" secondary transformer (transformer rated for combined 120/208V loads) is generally run from the MDP (main distribution panel) to a transformer in an electrical room and then a secondary 120/208V 3ph panel with its own main disconnect to supply all 120/208V loads.

We generally ALWAYS go with 120/208V 3ph "wye" secondary transformers to ensure that all phases are 120V to ground. The reason being is that 120/240V 3ph "delta" secondarys have a "high leg" which has a higher voltage to ground than 120V, so you have to skip that phase on the panel for 120V single pole breakers, leading to needing larger spaced panels or additional sub panels from the main panel fed from the secondary of the transformer.

It's generally good practice to keep the transformer near the MDP / main grounding point of the service and to ensure that the transformers ground it run back to the main 277/480V MDP / main disconnect to ensure that potential for noise created from the transformer is reduced as much as possible on the system, since the neutral of the secondary side of transformer is bonded to ground within the transformer.

This is the reason many buildings have a centralized electrical room near the main point of entry/main disconnect/MDP. Helps keep the cost of larger feeders to a minimum.

On buildings with 480/277V power, it's good practice to have all of the lighting loads at 277V and as many of the motor loads, inductive heat loads, etc. rated for 480V to keep 'unnecessary' loads off of the 120/208 load so that you can minimize the required size of the transformer, size of the secondary panel and size of the secondary feeders.

I know my explanation is probably a little above and beyond the scope of your question, but hope it helps.

Just my two cents.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,192
Location
Modesto, CA
Yes, in a building with 480/277 3ph incoming power from the utility, a breaker rated for the load of the 480V 3ph primary / 120/208V 3ph "wye" secondary transformer (transformer rated for combined 120/208V loads) is generally run from the MDP (main distribution panel) to a transformer in an electrical room and then a secondary 120/208V 3ph panel with its own main disconnect to supply all 120/208V loads.

We generally ALWAYS go with 120/208V 3ph "wye" secondary transformers to ensure that all phases are 120V to ground. The reason being is that 120/240V 3ph "delta" secondarys have a "high leg" which has a higher voltage to ground than 120V, so you have to skip that phase on the panel for 120V single pole breakers, leading to needing larger spaced panels or additional sub panels from the main panel fed from the secondary of the transformer.

It's generally good practice to keep the transformer near the MDP / main grounding point of the service and to ensure that the transformers ground it run back to the main 277/480V MDP / main disconnect to ensure that potential for noise created from the transformer is reduced as much as possible on the system, since the neutral of the secondary side of transformer is bonded to ground within the transformer.

This is the reason many buildings have a centralized electrical room near the main point of entry/main disconnect/MDP. Helps keep the cost of larger feeders to a minimum.

On buildings with 480/277V power, it's good practice to have all of the lighting loads at 277V and as many of the motor loads, inductive heat loads, etc. rated for 480V to keep 'unnecessary' loads off of the 120/208 load so that you can minimize the required size of the transformer, size of the secondary panel and size of the secondary feeders.

I know my explanation is probably a little above and beyond the scope of your question, but hope it helps.

Just my two cents.
excellent explanation
 