Not sure why breaker keeps tripping

OP
V

vern1

Well-known member
Joined
Mar 18, 2012
Messages
66
Ok i had another look. In the attached picture the black wire comes through a conduit from the house from a 30A breaker in the main panel. Crawled under the house and found 10AWG on the casing. The white wire it is spliced to goes in to the breaker box and is hooked to the main 40A breaker in the garage. It is 8-3

So i guess my options are:
- update the wire and breaker from the house to 8 and 40A
- stay with the 10 wire and just put a 40A breaker in the house
- status quo and will just have to manage the power use - which really means i cant run my 4800w heater while i am doing any work which is a drag. I am using a 60k btu propane heater to get the room warm and using the electric to maintian the heat
 

Attachments

  • IMG_00000001.jpg
    IMG_00000001.jpg
    147.5 KB · Views: 81
To avoid these ads, REGISTER NOW!
OP
V

vern1

Well-known member
Joined
Mar 18, 2012
Messages
66
PS i am assuming 10AWG means 10 guage although it looks identical to the 8-3. Maybe the difference in size is tough to discern to the untrained eye

Thanks
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,998
Location
Modesto, CA
Ok i had another look. In the attached picture the black wire comes through a conduit from the house from a 30A breaker in the main panel. Crawled under the house and found 10AWG on the casing. The white wire it is spliced to goes in to the breaker box and is hooked to the main 40A breaker in the garage. It is 8-3

So i guess my options are:
- update the wire and breaker from the house to 8 and 40A
- stay with the 10 wire and just put a 40A breaker in the house
- status quo and will just have to manage the power use - which really means i cant run my 4800w heater while i am doing any work which is a drag. I am using a 60k btu propane heater to get the room warm and using the electric to maintain the heat

Are u sure you have the cable and color combinations right? I've never seen a white jacketed #8 NM cable nor a black jacketed #10 NM cable. Usually, its the other way around but its possible I guess. Regardless though, you cannot protect #10 with a 40a breaker. So the only 2 options u have is: upgrade the #10 to #8 and splice it into the existing #8 that's feeding your garage or manage your load!
 
Last edited:
OP
V

vern1

Well-known member
Joined
Mar 18, 2012
Messages
66
I am in Canada, Toronto to be exact. I have the colour combos right ie the black says 10awg and the white says 8-3

So just putting a 40A on a #10 is a no no
 
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,998
Location
Modesto, CA
I am in Canada, Toronto to be exact. I have the colour combos right ie the black says 10awg and the white says 8-3

So just putting a 40A on a #10 is a no no

Sure! U could use a 40a breaker to feed a #10 wire. *sarcasm* But don't be surprised when u have a fire! Especially when running a continuous load such as a heater!
 
OP
V

vern1

Well-known member
Joined
Mar 18, 2012
Messages
66
Will have to monitor my usage given the current set up i guess

Thanks for all the help and info
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
I am in Canada, Toronto to be exact. I have the colour combos right ie the black says 10awg and the white says 8-3

So just putting a 40A on a #10 is a no no

I think that explains the color confusion. I believe Canadian building wire in some cases has different color jackets than what we see here in the US.
 

hotrod--willys

Well-known member
Joined
Jan 3, 2013
Messages
50
Location
Gig Harbor, Wa
One more thing Vern1. A circuit breaker is a mechanical device made to protect a given wire size/ load. But the breaker has an inherent design, that it's given amp rating each time it trips will be subjcted to a lower trip rating there on. So if one of your breakers has been triping on load, the noted current rating now has diminished current value. I would sugest replacing the breaker that has contunued to trip under load. Start new.
 