To avoid these ads, REGISTER NOW!

Notching truss for 2 post lift

Maine

Well-known member
Joined
Dec 11, 2009
Messages
107
I built my 28x30 garage this past fall and planned on using an Atlas 9OHSC lift. My build allowed for 12' of ceiling height but I just went and measured and I am actually at 11' 8", due to an overly thick slab (must be 6-8" thick?!)

I have 60 PSF rated attic trusses with 2x10 bottom cords. I hate to ask this, but I need to notch out 2" on 4 of the cords to allow for the overhead bar- (the main support posts fall between trusses).

My rational for even considering this is that the trusses that are notched will be supported by the overhead lift bar.

Any feedback on this guys? I know this is a no-no but the trusses are heavy duty with 2x10 bottom cords (i've seen them as small s 2x6 cords).

Thanks for the feedback.
 
To avoid these ads, REGISTER NOW!

wedge40

Well-known member
Joined
Oct 31, 2009
Messages
335
Location
Bloomington, IN
We could use a little more info. Are the trusses going be notched more then once per truss. You can't get the lift between the trusses?

Garage dimension, where the doors are located, and which direction the trusses run would help.

Wedge
 

theoldwizard1

Well-known member
Joined
Feb 22, 2011
Messages
43,132
Location
SE MI
The short answer is "yes" , but the integrity of the truss will be compromised.
******** !

The answers is noy just No, but HELL NO !

The bottom edge of truss, called the bottom chord, cares the HIGHEST tension load of the whole truss.
 

rslaback

Well-known member
Joined
Jul 24, 2010
Messages
4,068
Location
Westcentral Wisconsin
Give me some more specs on the building. It may not be doable, but my first suggestion would be to add material between the wall's tie plate and the trusses. Essentially, raise the roof 4 inches or so.
 

djjsr

Well-known member
Joined
Sep 4, 2006
Messages
4,796
Location
In the cornfields
When it comes to the structural integrity of your building, do you really want to take the advice of some do-it-yourselfer that sounds like he knows what he's talking about?

Seek professional help. Maybe someone here is qualified, maybe not.
 

WNYflyer

Well-known member
Joined
Sep 13, 2009
Messages
2,119
Location
Lockport, NY
As you know trusses are engineered to specific loads and dimensions. Any alteration to them that is not engineered is a no-no. Not to say folks haven't gotten away with altering them themselves but the correct way is to have an engineered alteration.

If the location of the proposed notching is out in the area of the attic/60 psf floor load then you are indeed in the location of maximum axial tension in the bottom chord when talking about gravity loads. The even bigger problem would be fact the bottom chord is also seeing significant beam action in the attic area. Notching 2 inches out of a 2x10 reduces its "beam" capacity by about 40% +-. Yes of course notching the bottom chord out 2 inches can be done but you really need someone who knows what they are doing from both an engineering and construction aspect to get it properly altered/reinforced.
 

zcar751

Well-known member
Joined
Apr 15, 2013
Messages
831
Location
Knoxville, TN
A picture would help with some mark ups, where in the structure do you want to notch.

I would say yes you can notch the trusses but you will need to add support to those trusses. My suggestion is to take 3/4 inch ply wood of at least 7 layers and sandwich the bottom cords using 3/8s nuts & bolts with thick fender washers. You will want to carry the plywood at least a foot past the notch on each side.
 

KPSquared

Well-known member
Joined
Aug 18, 2010
Messages
2,750
Location
Wetaskiwin, Alberta, Canada
Talk to the conmpany that designed your trusses. Don't take critical design advice from a bunch of armchair structural engineers.

This is the exact reason I went 12'6"... always leave room for error.
 

Sureshot

ALLIANCE MEMBER
Joined
Jan 3, 2011
Messages
3,134
Location
Bridge Creek, OK
******** !

The answers is noy just No, but HELL NO !

The bottom edge of truss, called the bottom chord, cares the HIGHEST tension load of the whole truss.

Because it is in tension I would add to the top and remaining side to carry the tension across the compromised spot.

Since the issue is the walls spreading you could add a metal bar from one side to the other of the entire building. Maybe an I beam you could also use as a light trolley.
 

mds5951

Well-known member
Joined
Aug 15, 2010
Messages
322
Personally this would be a question I'd ask whoever engineered the trusses, maybe even have them stop out...Im sure theres a way. Don't quote me on this but I always thought an engineer had to "sign off" on any notches to pass code.
 

Quijote

Well-known member
Joined
Feb 27, 2013
Messages
179
Location
Greater Boston
You can't get the lift between the trusses?

This.

Because my town has height limits on accessory buildings I could not do a 12' ceiling. So I went with a 10' ceiling and I am going to stick the lift between the trusses (16 on-center which is enough to fit a Bendpak XPR-10A if my calculations are correct).
 

hd54kh

Well-known member
Joined
Jul 19, 2012
Messages
131
Location
Mooresville N.C.
I have no knowledge of your truss design or lift but can your overhead crossover of the lift be extended to go between the trusses and cross over above your ceiling?

Terry
 

JakeKohl

Well-known member
Joined
Feb 23, 2012
Messages
1,365
Location
Greenville, SC
This.

Because my town has height limits on accessory buildings I could not do a 12' ceiling. So I went with a 10' ceiling and I am going to stick the lift between the trusses (16 on-center which is enough to fit a Bendpak XPR-10A if my calculations are correct).


I'm pretty sure the top xbar on the lift is perpendicular to the trusses if I understand his question properly...so while you could probably get the main posts between them, the cross bar is a problem.

You may be able to get away with notching the bottom chord of the truss - but you should consult the truss manufacturer to get their input. The other idea that someone mentioned may have merit and be easier than all this notching stuff. If you have the lift shortened slightly, you don't loose much lift and it's probably cheaper than all this notching and refinishing (assuming that you have a finished space).
 
To avoid these ads, REGISTER NOW!

DekeT

Well-known member
Joined
Aug 12, 2011
Messages
2,234
Location
USA
A picture would help with some mark ups, where in the structure do you want to notch.

I would say yes you can notch the trusses but you will need to add support to those trusses. My suggestion is to take 3/4 inch ply wood of at least 7 layers and sandwich the bottom cords using 3/8s nuts & bolts with thick fender washers. You will want to carry the plywood at least a foot past the notch on each side.

Don't do this.
 

ez-duzit

Well-known member
Joined
Jun 24, 2013
Messages
5,096
Location
Marina del Rey
...My rational for even considering this is that the trusses that are notched will be supported by the overhead lift bar...

The trouble with this rationale is that the bottom truss element you want to cut into is not a compression member but works in tension--the lift will not make up for that. And I assume you live in an area that regularly gets high snow loads.
 

Bob C

Well-known member
Joined
Jul 17, 2012
Messages
572
Rotary Lift SPOA10 Two Post - Overall height 11' 10-1/2"

Costs alot more but save money on things you work around NOT under!
 

vhol5

Well-known member
Joined
May 24, 2011
Messages
358
Location
West Texas
Fishplates. Simple.
fig112.jpg
 
OP
M

Maine

Well-known member
Joined
Dec 11, 2009
Messages
107
Okay guys heard you all loud and clear, I won't cut any of the truss.
 
OP
M

Maine

Well-known member
Joined
Dec 11, 2009
Messages
107
just move the bar down ! redrill it or fab brackets , not a big deal !

I would love to just do this- when I asked Greg Smith about it they wouldn't discuss any modifications with me, is it really as simple as re-drilling for bolts? There are cables, hoses in the overhead span.


Maybe I should just get the 9KOH lift.... really wanted the super symmetric arms and single point release. Anyone own the 9kOH?
 
Last edited:

Diesel Dan

Well-known member
Joined
Jul 21, 2013
Messages
2,459
Location
TN
If you were to get an engineer involved could the current trusses be safely modified into higher clearance scissor style trusses?

There are always options.
Just depends on the $$ to implement them.
 
OP
M

Maine

Well-known member
Joined
Dec 11, 2009
Messages
107
Hi Dan,

I've got a room above the garage so that wouldn't be an option.
 

Sureshot

ALLIANCE MEMBER
Joined
Jan 3, 2011
Messages
3,134
Location
Bridge Creek, OK
I would take another look at your original plan. You want to take 2" out of a 2x10. You could sister a 2x8 on each side of the 2x10. What would be stronger a single 2x10 or three 2x8 sistered together?

Glue and screw.

People need to look at it rationally and not react with the "engineered" storyline. Sometimes you need Swiss watch and sometimes a sundial will do.
 
OP
M

Maine

Well-known member
Joined
Dec 11, 2009
Messages
107
Cant move the bar down, it has plates welded to it that rest on top of the columns. Thank you for that link!
 

zack99

Active member
Joined
Apr 27, 2013
Messages
37
Location
Jacksonville FL
Anyone who has lived in an old house has probably noticed how much bounce there is to the floors. Floor joists used to be commonly done using 2x8 lumber. I once lived in a house with 2x6 floor joists and things on the table would rattle every time I walked across the room.

I sistered the joists with 2x10 boards and problem solved. It was an 80 year old house and no cracks or signs of impending collapse. Just an annoying amount of bounce.

Sent from my XT907 using Tapatalk 2
 

Spudland_Dave

Well-known member
Joined
Mar 12, 2010
Messages
3,025
Location
Maine
I would take another look at your original plan. You want to take 2" out of a 2x10. You could sister a 2x8 on each side of the 2x10. What would be stronger a single 2x10 or three 2x8 sistered together?

Glue and screw.

People need to look at it rationally and not react with the "engineered" storyline. Sometimes you need Swiss watch and sometimes a sundial will do.

Best post of the bunch...Quick call to your truss co. will get you a free answer, and I bet that sistering a 2x8 or a small LVL/LSL will be sufficient...combined with a couple tubes of Liquid Nails and a box of screws, those 4 modified trusses would probably end up stronger then the rest of them.
 

KPSquared

Well-known member
Joined
Aug 18, 2010
Messages
2,750
Location
Wetaskiwin, Alberta, Canada
Ok, no modifying lift.

Either hack it up and hope, call the truss company for a likely free answer, or buy a lower lift.

There are baseplate lifts with the super-symmetric arms. Unless you really want an overhead.
 

theoldwizard1

Well-known member
Joined
Feb 22, 2011
Messages
43,132
Location
SE MI
Best post of the bunch...Quick call to your truss co. will get you a free answer, and I bet that sistering a 2x8 or a small LVL/LSL will be sufficient...combined with a couple tubes of Liquid Nails and a box of screws, those 4 modified trusses would probably end up stronger then the rest of them.

While your comments on sistering a couple of 2x8 on the sides may be correct, I guarantee you no truss company would ever approve it, even verbally. To much liability at stake.
 

JakeKohl

Well-known member
Joined
Feb 23, 2012
Messages
1,365
Location
Greenville, SC
While your comments on sistering a couple of 2x8 on the sides may be correct, I guarantee you no truss company would ever approve it, even verbally. To much liability at stake.

I don't know about that...the opportunity to sell some more LVLs? It's a pretty pure and safe science with a lot of history and safety factor. I bet they would look at it. There's only one way to find out. If the liability were that much of a problem, they probably wouldn't be in business to begin with.
 

ez-duzit

Well-known member
Joined
Jun 24, 2013
Messages
5,096
Location
Marina del Rey
While your comments on sistering a couple of 2x8 on the sides may be correct, I guarantee you no truss company would ever approve it, even verbally. To much liability at stake.

And no building inspector would ever approve it.

Another thought is that you could probably jack up the lower truss element 2" near the center of its span.
 

JakeKohl

Well-known member
Joined
Feb 23, 2012
Messages
1,365
Location
Greenville, SC
And no building inspector would ever approve it.

Another thought is that you could probably jack up the lower truss element 2" near the center of its span.

You have to sister floor joists occasionally because of plumbing and other penetrations - that passes code. You guys are being overly difficult.
 
To avoid these ads, REGISTER NOW!