Of Compressors, Breakers and Amps

SwedeChariot

Member
Joined
Sep 9, 2012
Messages
9
Hi folks,

This is my first time posting on this forum.

I recently bought a used DeWalt/Emglo D55170 8 gallon pontoon-style air compressor. It's a belt driven, 1.5 hp, 7.5 amp unit. I believe it's dual voltage but it came to me set up for 115 volts. I don't have a 220 outlet in my garage.

My problem is that about half the time I fire it up it trips the breaker. It runs for 3 or 4 seconds, then dies. The breaker is 15 amps. The house is 10 years old.

Any theories about what's going on here and how to correct it? I'm not especially knowledgeable about household electrics, so I don't know if swapping out the breaker for one of higher amperage is advisable or whether I'm liable to burn down the garage and/or house.

Since this is a roofer compressor, I assume it's rated for a standard household amperage. I guess that means that either my electrical setup is substandard, or else I have a maintenance issue with the compressor.

Thoughts?
 
To avoid these ads, REGISTER NOW!

Jbullfrog

ALLIANCE MEMBER
Joined
Jan 9, 2007
Messages
2,347
Location
Avoca, Iowa
Did you plug it in before you bought it? It maybe rated at 7.5amps running but probably pulls 2x that when it starts. The outlet you are using may have other loads on it and not have enough left to start the motor.
 
OP
S

SwedeChariot

Member
Joined
Sep 9, 2012
Messages
9
Thanks guys.

There are lights on the circuit but I had the lights off during some instances of the breaker failure. Also, I have succeeded in running the compressor with the lights on, although they dim and flicker.

The unit was plugged into an extension cord. I moved it and plugged it straight into the wall, at which point it worked. I guess I'll try it a few more times and see if it continues to work without tripping the breaker.

I don't have any 20 amp circuits in the house, just 15, 40 and 60.
 
To avoid these ads, REGISTER NOW!

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
If using too long and too small gauge extension cord can cause a voltage drop causing the amps to increase, tripping the breaker.
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,754
A 1 1/2 HP motor should draw around 15 amperes at 115V are you sure the nameplate data was posted correctly? Some Emglo compressors had a switch to change over from 115V to 230V so they could be run at either 120V or 240V, if that was the case w/ a compressor being a hard starting load, it would be EZ to trip a breaker if the switch was in the incorrect position.
 
Last edited:
OP
S

SwedeChariot

Member
Joined
Sep 9, 2012
Messages
9
Norcal you're right: they market the compressor at "7.5 amps" but the nameplate says "FLA: 15.2/7.6." So I guess my breaker is borderline. Would it be unwise to replace my 15 amp breaker with a 20 amp breaker?

The extension cord I was using was pretty long and of finer gauge than the compressor cord. Now that I'm plugged into the wall, maybe be okay if i keep the lights off at start up.
 
To avoid these ads, REGISTER NOW!