Off grid heat question

tmshort

Well-known member
Joined
Dec 10, 2012
Messages
393
Location
Central IN
I have an off grid cabin in the Rockies. We shut the place down and drain pipes etc when we leave. There are times where there is a month or so where no one is there.
It is all PEX, and even though we drain the pipes there is still some water that freezes.
The basement has a 300 gallon holding tank, when we have really cold spells this freezes.
We arrived yesterday, and with the cold weather lately it took forever to get things thawed out and functioning.

We have solar with batteries, but not enough to run any kind of electric heat. I do have a 1000 gallon propane tank.

I'd like to put a propane heater of some sort in the basement just to keep it above freezing and am interested in thoughts on what would be best as well as safe to run when the place is unoccupied. We have starlink and robust wifi as well as cameras and other monitoring, so I can keep an eye on things remotely.

Thanks in advance...
 
To avoid these ads, REGISTER NOW!

PoorUB

Well-known member
Joined
Mar 29, 2021
Messages
11,616
Location
Fargo, ND
I'd like to put a propane heater of some sort in the basement just to keep it above freezing and am interested in thoughts on what would be best as well as safe to run when the place is unoccupied. We have starlink and robust wifi as well as cameras and other monitoring, so I can keep an eye on things remotely.
Do you have electrical service, or some other source for power, wind generator, solar? Oops! Solar!

A Reznor or Modine shop heater will work if you have a place you can vent out the exhaust, but they consume a bit of electricity.

There are other heaters that will work, but watch out on how they vent. Some will direct vent right out the wall, but you can not go up and out. Most need 120 volt.

Some small heaters do not use electricity, will vent straight up with B-vent, but you need to find a place to run the venting straight up through the roof.
 
Last edited:

ipgenie

Well-known member
Joined
Jan 29, 2020
Messages
560
Location
Idaho
If your solar is 12v, you could use an RV furnace. They are all propane fueled, direct vented and DC powered and most are compatible with smart thermostats. If you use a higher voltage system, a buck converter and 12v battery would be needed.

Edit to add that they can also be found cheap at wrecking yards. Last one I bought was $25 from a couple year old motorhome that had been rolled. Should produce plenty of heat to keep a basement above freezing. They vent directly through the wall but are low profile and can be mounted near the ceiling.
 
Last edited:

HoosierBuddy

Well-known member
Joined
May 9, 2006
Messages
2,915
Location
Southern Indiana
Williams propane direct vent wall heater
Martin makes them as well.

This is the proper solution. Get a propane direct vent that doesn't require power. Install properly and set the t-stat as required to protect against freezing. Monitor with an ap of some kind.

This will be more effective if you give some thought to insulation.
 
OP
T

tmshort

Well-known member
Joined
Dec 10, 2012
Messages
393
Location
Central IN
Thanks for all of the input.
Currently looking at the direct vent options. Does anyone know of a unit that can be controlled remotely, or do they all have a piezo lighted pilot and built in thermostat?

Also, altitude may be a factor - the cabin is at 10,000'; some of the units say "up to 2000' altitude".
 
OP
T

tmshort

Well-known member
Joined
Dec 10, 2012
Messages
393
Location
Central IN
You might be better off looking at a stock tank heater, rather than trying to heat the entire basement.
We had considered something like this, but we don't have a ton of electrical reserve. Certainly not enough to run a resistance type heater.
 
To avoid these ads, REGISTER NOW!

dcg9381

Well-known member
Joined
Jun 20, 2018
Messages
11,627
Location
Austin, TX
If your solar is 12v, you could use an RV furnace. They are all propane fueled, direct vented and DC powered and most are compatible with smart thermostats. If you use a higher voltage system, a buck converter and 12v battery would be needed.
They go through propane for sure. Once the start cycle fails, they likely do not auto-reset without intervention.

How about a simple "ventless" deal mounted on the wall? Ventless would be better. At 10k elevation, that might be a little tricky.

10K BTU is .45 gallons propane per hour though...
 

dcg9381

Well-known member
Joined
Jun 20, 2018
Messages
11,627
Location
Austin, TX
Burning a gallon of propane yields 91K BTU; it would be more like .12 to .2 gallons/hr depending on efficiencies, etc.
Thanks.. I'm going drop using the AI answers. Seems like it confused gallons with pounds. Your calculation is right.

1738172999758.png
 

LopezBart

Well-known member
Joined
Oct 13, 2023
Messages
2,519
Location
Lopez Island, WA
Thanks.. I'm going drop using the AI answers. Seems like it confused gallons with pounds. Your calculation is right.

1738172999758.png
As you saw, don't trust AI. It's simply wrong too much of the time. These systems hallucinate frequently... try asking questions on a subject when you know a lot about; you'll wonder why anyone would trust these systems.
 

Firebrick43

Well-known member
Joined
May 12, 2015
Messages
13,975
Location
West central Indiana
We had considered something like this, but we don't have a ton of electrical reserve. Certainly not enough to run a resistance type heater.
They make resistance immersed heaters to hook up directly to a solar panel. No batteries, no inverters.

It doesn’t take much to keep it thawed out of there is any insulation on the tank. I would still drain the lines.

A panel or two hooked to one would suffice


 
Last edited:

u3b3rg33k

Well-known member
Joined
Dec 18, 2017
Messages
4,047
We had considered something like this, but we don't have a ton of electrical reserve. Certainly not enough to run a resistance type heater.
have you considered a dump load for the solar into the 300gal tank? presumably it's insulated, it should not take a ton of kWh to keep it at 33F. also maybe heat trace on some lines you can switch on for easy startup.
 

Jackfre

Well-known member
Joined
Dec 26, 2010
Messages
4,406
Location
N CA
Ahh, Leadville! 10,000 elevation. I would suggest a Rinnai EX-22. It modulates from 8200-20,500 And draws from 33-52 watts. Direct Vent requiring only a 2.75” hole in the wall for the vent which is included. You will have to de-rate for the elevation and you MUST have a differential pressure manometer to do so. Ther are many of them in the Leadville area.
 
Last edited:
OP
T

tmshort

Well-known member
Joined
Dec 10, 2012
Messages
393
Location
Central IN
In answer to some of the questions:

- the tank is not currently insulated.
- we have some work to do on insulating the basement, but overall it is not terrible. about 2/3 of it is below grade, the rest is 2x6 with R19 batts.
- I really only need a few degrees of heat ... I have remote temp sensors there. The temp hovers around 32, and drops lower at times when the OAT is much lower. Even getting it to a consistent 35 would solve the problem.
- was not aware of the DC heating elements. this is an interesting option for keeping the tank from freezing...

Thanks for the Rinnai suggestion - researching that more now.
 

locomotiveman

Member
Joined
Feb 11, 2025
Messages
20
OFF-GRID?? IMG_1927.jpegSimple. EMPIRE propane-fired direct vent wall heater with a Milli-Volt thermopile wall thermostat. I have similar situation and it is heavenly ( and SAFE!! ) I have the DV-215
 