oil burner t-stat location

greenskeeper

Well-known member
Joined
Dec 7, 2018
Messages
650
Location
PA
Going into the first winter season with an oil burner in the detached garage instead of a wood stove.

garage is 25x22 and the oil burner is obviously way over-sized since it came from a 1500 sqft house.

what is the best location for the t-stat? The burner is centered at one end of the garage pointing towards the two garage doors.
 
To avoid these ads, REGISTER NOW!

LS6 Tommy

Well-known member
Joined
Dec 27, 2013
Messages
26,162
Location
Northern NJ
Forced warm air? I'd put it on an inside wall if possible, roughly half way between the unit and the doors and not in direct contact with the heated air coming out of the unit.

Tommy
 

htmdude57

Well-known member
Joined
Apr 28, 2014
Messages
173
Location
Hudson Valley, New York
If the oil burner/furnace is over sized, ask your oil burner tech if it is possible for him to install a smaller nozzle. Of course, then he will need to test and adjust the air mixture. And check CO, CO2 and smoke.
 

LS6 Tommy

Well-known member
Joined
Dec 27, 2013
Messages
26,162
Location
Northern NJ
If the oil burner/furnace is over sized, ask your oil burner tech if it is possible for him to install a smaller nozzle. Of course, then he will need to test and adjust the air mixture. And check CO, CO2 and smoke.

Firing rate & efficiency should be checked regardless of whether he downsizes the nozzle or not.

Tommy
 

rlitman

Well-known member
Joined
Oct 18, 2010
Messages
24,624
Location
Long Island
Forced warm air? I'd put it on an inside wall if possible, roughly half way between the unit and the doors and not in direct contact with the heated air coming out of the unit.

Tommy

Exactly. You want to pick a spot where the cold of the exterior walls and the direct heat from the unit have the least influence on the thermostat.

Firing rate & efficiency should be checked regardless of whether he downsizes the nozzle or not.

Tommy

Well, to be fair, while they should be checked, there's a good chance that no adjustments will be required if the nozzle isn't changed.
 
OP
G

greenskeeper

Well-known member
Joined
Dec 7, 2018
Messages
650
Location
PA
Forced warm air? I'd put it on an inside wall if possible, roughly half way between the unit and the doors and not in direct contact with the heated air coming out of the unit.

Tommy

I'll try that. I'm guessing it will be slow to react being the burner is so over-sized for my application.
 
OP
G

greenskeeper

Well-known member
Joined
Dec 7, 2018
Messages
650
Location
PA
If the oil burner/furnace is over sized, ask your oil burner tech if it is possible for him to install a smaller nozzle. Of course, then he will need to test and adjust the air mixture. And check CO, CO2 and smoke.

Ideal but not practical. I'm only going to heat when I am out in the detached garage working. So maximum heat is a good thing in this application. I am thinking that once it's at temperature I shouldn't have to re-fire the burned that often.
 
To avoid these ads, REGISTER NOW!

LS6 Tommy

Well-known member
Joined
Dec 27, 2013
Messages
26,162
Location
Northern NJ
I'll try that. I'm guessing it will be slow to react being the burner is so over-sized for my application.

An oversized unit will just satisfy the stat faster. If you find that it's too hot closer to the unit or too cold further away, you can always relocate the stat. Closer to the unit if it's too hot, further away if it's too cold. Just make sure the discharge doesn't blow directly on the stat or it will short cycle.

Tommy
 
Last edited:
OP
G

greenskeeper

Well-known member
Joined
Dec 7, 2018
Messages
650
Location
PA
Did a test with the t-stat along the wall parallel to the furnace. Over-shot the temperature by 15 degrees by the time the thermostat caught up to the actual room temp. Going to have to rethink this or not use a t-stat at all and just use an on/off timer switch or something.
 

rodder98

Well-known member
Joined
Nov 9, 2011
Messages
65
Location
Ocala, Florida
The best place is away from the warm air supply. It needs to sense the coolest air in your garage. And, if mounted on a wall, be sure that any hole where the thermostat wire comes through, is sealed up. If you don't, it could sense the air behind it, and not the room temperature.
 
OP
G

greenskeeper

Well-known member
Joined
Dec 7, 2018
Messages
650
Location
PA
going to try putting the thermostat on the far wall, between the two garage doors in line with the airflow from the heater. This is obviously not an ideal situation with the heater being about 3x over sized.
 
Last edited:

LS6 Tommy

Well-known member
Joined
Dec 27, 2013
Messages
26,162
Location
Northern NJ
going to try putting the thermostat on the fall wall, between the two garage doors in line with the airflow from the heater. This is obviously not an ideal situation with the heater being about 3x over sized.

That may help with your overshooting problem. Sometimes the "conventional" thing isn't the best.

Tommy
 
OP
G

greenskeeper

Well-known member
Joined
Dec 7, 2018
Messages
650
Location
PA
below freezing now...I've learned to set the t-stat about 5 degrees below the desired temperature when the furnace cuts off. The furnace although oversized is working fairly well. I can raise the temperature in the garage from 45 to 65 in about 10 minutes. Colder weather is coming though.
 