I have my 60 gal single stage compressor under the stairs by the back door to the shop (the door I mainly use).

I have this switch installed to turn the compressor on/off when I leave. It is still easy to forget:

C8A22B33-9560-4197-A3D3-1EA5C1992EF3.jpeg

I would like to wire in some sort Of indicator light as a reminder to switch it off. I’m pretty comfortable with basic wiring, but am baffled as to the best way to do this.

Any suggestions? I am open to suggestions on what type of light, etc.

Thanks
 
To avoid these ads, REGISTER NOW!

mikedodge

Well-known member
Joined
Jun 27, 2017
Messages
2,959
We have this motor switch for our outside plug for that very reason of having a light. You'd have to find the right amperage since they're multiple sizes.
 

Attachments

  • 1H388_AS01.jpeg
    1H388_AS01.jpeg
    29.2 KB · Views: 32

PoorUB

Well-known member
Joined
Mar 29, 2021
Messages
11,961
Location
Fargo, ND
It has been discussed before, but I wired my compressor pressure switch controls through a relay into the lighting circuit . No lights, not compressor. If you don't have a motor starter on the compressor you would have to rewire and add one.
 

MFortie

Well-known member
Joined
Aug 9, 2010
Messages
919
Location
San Diego County
I’d like to do the lighting relay for my compressor too, but am having trouble finding correct relay.

Mine’s a Quincy QT-54, 5HP, 24A draw per the cutsheet, and it’s connected to a 40A, 240V breaker (sits right next to the panel).

I can find 30A relays all day long, but no 40A (my GoogleFu must be weak).

Any help?
 
To avoid these ads, REGISTER NOW!

MFortie

Well-known member
Joined
Aug 9, 2010
Messages
919
Location
San Diego County
Search for "HVAC contactor".

here's an example. its 3 pole but has a 240v coil.

Thank you.

I’ve been doing a little reading on the forum about this. Since my comp has a magnetic starter, am I better off connecting a lower amperage relay into the starter circuit or doing the higher amperage contactor in the motor circuit?

I also am adding the ‘soft start’ ball valve to the system.

Never mind; it’s just a pressure switch, not a mag starter. I was looking at something different apparently.
 
Last edited:

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,243
Location
Modesto, CA
Thank you.

I’ve been doing a little reading on the forum about this. Since my comp has a magnetic starter, am I better off connecting a lower amperage relay into the starter circuit or doing the higher amperage contactor in the motor circuit?

I also am adding the ‘soft start’ ball valve to the system.

Never mind; it’s just a pressure switch, not a mag starter. I was looking at something different apparently.
If your compressor already has a magnetic starter then you woulsnt add another contactor to switch the motor load.

Just switch the coil side of the existing contactor. Make sure you get a 240v rated snap switch
 

PoorUB

Well-known member
Joined
Mar 29, 2021
Messages
11,961
Location
Fargo, ND
I’d like to do the lighting relay for my compressor too, but am having trouble finding correct relay.

Mine’s a Quincy QT-54, 5HP, 24A draw per the cutsheet, and it’s connected to a 40A, 240V breaker (sits right next to the panel).

I can find 30A relays all day long, but no 40A (my GoogleFu must be weak).

Any help?
A 5HP quincy should have a motor starter and a low amperage control citcuit coming off the pressure switch that handles just the load of the contactor, probably less than 1/2 amp. wire the relay to break that control circuit. Any relay with contacts rated for 240 volt and a 120 volt coil will do. I used a Rib relay U1C

I looked, wow! there is just a pressure switch rated for the motor load. I would have never guessed!

In that case you will need a 30 amp contactor with a 120 volt coil, and mount it inside some sort of electrical box.

https://www.amazon.com/dp/B001KGSJ74/?tag=atomicindus08-20
 
Last edited:

PoorUB

Well-known member
Joined
Mar 29, 2021
Messages
11,961
Location
Fargo, ND
some compressors just have a pressure switch even though a mag starter would be far better
Well aware of that, I was just surprised a "real" 5 HP compressor had just a pressure switch rated for the motor load. I have seen it done on smaller compressors.
 

Citation

Well-known member
Joined
Jan 20, 2016
Messages
3,263
Location
Indy
Several have suggested getting a relay. I'm not seeing why. My impression is the intent is to have a light that is on when the wall switch is sending power to the compressor. For that you just need to wire a 240V light in parallel to the compressor power line.

A relay powered by a switched 120V circuit would let you put lights or a switched out let + lamp on the same circuit that powered the relay. That may be helpful if the intent is to tie turning off the shop lights with powering down the compressor. However, it seems more complicated vs just adding a 240V neon or LED lamp. If the compressor is in a visible location the 240V light could be wired to the pressure switch instead of the wall power switch.

Here is a multi-voltage (including 240V) stack light. Attach this to the compressor and tie the power lines into the leads going into your pressure switch.
 

PoorUB

Well-known member
Joined
Mar 29, 2021
Messages
11,961
Location
Fargo, ND
Several have suggested getting a relay. I'm not seeing why.
There is two lines of conversation going on. One with just a light, another discussing controlling the compressor through the lighting circuit using a contactor or relay. Try to keep up! :ROFLMAO:
 

Steve W.

Well-known member
Joined
Mar 27, 2019
Messages
1,285
Location
Southwest oHIo
I took a different approach (of course). My compressor is virtually always ON, with pressure in the tank. I have a ball valve that will allow air into the lines that go through the shop. Just downstream of that ball valve is a regulator. There is a gauge on one side and a plug on the other, so you can move the gauge, if necessary. I removed the plug and installed a brake switch from a motorcycle, then connected a 12-volt wall wart power supply and a trailer marker light by the exit door. Now, if there is pressure in the lines, the light is ON. As I leave, that is a reminder to turn off the ball valve and bleed pressure at one of the drops. The compressor/tank assembly is tight enough that it might take a couple of days to lose enough air for the compressor to kick on, but if the ball valve is open, that time is reduced to just a few hours.

.
 

exranger06

Well-known member
Joined
Aug 9, 2015
Messages
1,686
Location
CT
I've posted this before, but this is how I did it (see pics). I ran a neutral wire to the switch to power the 120V light. The light turns on whenever the toggle switch is on. The automatic tank drain also runs every 20 mins or so, but only when the switch is on.
 