On YouTube: How to get 240v From Two 120V Outlets.

1Garageman

Well-known member
Joined
May 12, 2009
Messages
4,417
Location
Columbus, Ohio

WTF! How is this even safely on YouTube? I am reading the messages below the video of so many people supposedly doing this ****. He goes step by step on how to do this, making sure you get two separate breakers. I can't believe this $hit is on there!:eyecrazy:


Screen Shot 2020-09-10 at 3.51.28 PM.jpg
 
To avoid these ads, REGISTER NOW!

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
I don't see the big deal. What's so unsafe about it from a technical aspect if cord is sized correctly? Circuits have OC protection. The main thing I was surprised by was that the startup amps of the mill didn't trip the breakers.
 

Terry D

Well-known member
Joined
Mar 25, 2015
Messages
2,202
Location
St. Louis, MO.
I don't see the big deal. What's so unsafe about it from a technical aspect if cord is sized correctly? Circuits have OC protection. The main thing I was surprised by was that the startup amps of the mill didn't trip the breakers.

I would have to agree with you on this. He connected his grounds, the neutral is not a issue here. The only issue I see, is if the 2 circuits that he is plugged into are not on a 2-pole breaker, if one circuit would trip, it would not open the other. But those plugs serve as a disconnecting means for safety.
 

dogdog

Well-known member
Joined
Nov 15, 2011
Messages
12,711
It just seems so crazy, and could kill someone. I thought I would share it.:eyecrazy:

I don't think you have read / watch through the whole thing... he explained it how in the beginning of the video the concept of it... It works, just not electricmacode standard since the two breakers needs to be tied together. but it works.

If you haven't heard of that guy.. of his few months of frame... he is the guy that popularized "free" energy (not stanley meyer)... more specific on coils and leds ...wiind up in a star shape... convincing enough for some funds for "Free" energy research. some of the ideas and concepts were .... fringe science of sort, till it was debunked. I think...
 

mc4life27

Well-known member
Joined
Jul 2, 2014
Messages
404
One of the biggest issues I see is the wiring in the walls of most outlets is going to be either 14/2 or 12/2 and yes when running 220 current draw is lass then at 120 but most things that are 220 are high current draw. One reason why they run at 220. So if the breakers malfunction, I see some melty wires.


Sent from my iPhone using Garage Journal
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,089
Location
Modesto, CA
One of the biggest issues I see is the wiring in the walls of most outlets is going to be either 14/2 or 12/2 and yes when running 220 current draw is lass then at 120 but most things that are 220 are high current draw. One reason why they run at 220. So if the breakers malfunction, I see some melty wires.


Sent from my iPhone using Garage Journal

define high current draw

My 24K BTU window air conditioner that i just mounted in my living room wall is 240v but only draws 10a..... i dont consider that to be high current draw.

240v table saws, dust collectors, drill presses, etc dont draw a lot of amps...

The only thing in a garage that could be considered high current draw is a welder, heater, or electric vehicle charger
 

theoldwizard1

Well-known member
Joined
Feb 22, 2011
Messages
43,342
Location
SE MI
It just seems so crazy, and could kill someone. I thought I would share it.:eyecrazy:

My daughter hired a guy to re-finish her hardwood floors. The floor sanders was 240V. I did not do a close inspection, but he used some kind of alligator clips to get two hots directly from exiting breakers in the load center !

I have a "cheater" set up where I can remove two 120V coming coming out of a load center and then use those breakers to provide temporary power to a NEMA 6-20 outlet. Yes, there is a ground.
 

Terry D

Well-known member
Joined
Mar 25, 2015
Messages
2,202
Location
St. Louis, MO.
It "looks scary" Like an AR15 stock on a .22 rifle. Yes, it can kill someone if used incorrectly !
Looks doesn't make something unsafe. There is really nothing unsafe about it as long as the OCP is sized for the wire. The other issue is if the 2 circuits are not on a 2 pole breaker, but those plugs serve as a disconnecting means from power.

I personally wouldn't have the need for doing it, because being a electrician, i would just run a circuit

Sent from my SM-G960U using The Garage Journal mobile app
 
Last edited:
To avoid these ads, REGISTER NOW!

pi_guy

Well-known member
Joined
Jul 27, 2014
Messages
2,831
Location
N/A
In order to create 220 don't the legs have to be 90 degrees out of phase. So if you only had 120 service you could not take two circuit breakers to create 220? correct?
 

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
8,028
Location
Central Iowa
In order to create 220 don't the legs have to be 90 degrees out of phase. So if you only had 120 service you could not take two circuit breakers to create 220? correct?

True but 120 volt services are almost a thing of the past. I have seen two of them in my career. Both were upgraded to 120/240. I would also guess that if someone had a 120 service, the last thing on their mind would be how to jerry rig a 240 circuit.
 
OP
1

1Garageman

Well-known member
Joined
May 12, 2009
Messages
4,417
Location
Columbus, Ohio
Seems like to me with what he did it would of been possibly faster to go ahead and put in a 240/20 amp breaker and run it to his garage. All the stupid work he had to do to get it running was crazy and dangerous.
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
Seems like to me with what he did it would of been possibly faster to go ahead and put in a 240/20 amp breaker and run it to his garage. All the stupid work he had to do to get it running was crazy and dangerous.

Making up a cord should be quicker and easier in most cases than running a new circuit. Plus I don't get all the dangerous and somebody is going to die talk.
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,770
You Tube is still a bad place for electrical advice, at least with here there is someone to call out the bad advice, they may do it there but who reads the comments, sort of like who reads the instructions.
 

dave*99

Well-known member
Joined
May 5, 2009
Messages
4,289
Location
Coastal NJ
In order to create 220 don't the legs have to be 90 degrees out of phase. So if you only had 120 service you could not take two circuit breakers to create 220? correct?

In the typical single phase 240 V service the 2 line conductors are 180 degrees apart in phase. You get 240V across those legs.

In a 3 phase service the legs are 120 degrees apart in phase.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,089
Location
Modesto, CA
In order to create 220 don't the legs have to be 90 degrees out of phase. So if you only had 120 service you could not take two circuit breakers to create 220? correct?

no

the sum needs to be 360°.

its also not 220v in the US.... 120/240v

If one only has 120v service, then they arent getting 240v potential no matter how many breakers they use....
 

dogdog

Well-known member
Joined
Nov 15, 2011
Messages
12,711
no

the sum needs to be 360°.

its also not 220v in the US.... 120/240v

If one only has 120v service, then they arent getting 240v potential no matter how many breakers they use....

step up voltage transformers :) probably not efficient at all.. but they do have them up to 3000 watt... I think.
 

bad_idea

Well-known member
Joined
Jun 11, 2011
Messages
4,335
Location
Pasquotank, NC
Would I do it? Short term testing or quick job - sure. Long term fix - no. I can see this being useful doing mobile welding - not a business but a quick exhaust for a buddy kind of thing. I usually go for a dryer outlet, but sometimes they don't have one near the work.

I don't see the hazard. Only hazard I see is teaching an ignorant person this trick. The old saying, "know enough to be dangerous".
 

Showkey

"MEMBER EMERITUS"
Joined
Aug 9, 2014
Messages
8,638
Location
Wausau WI
I don't see the hazard. Only hazard I see is teaching an ignorant person this trick. The old saying, "know enough to be dangerous".


Isn’t that true about any quick fix, hack, or temporary solution.

He did warn multiple times. Life is full of risks and hazards.
 
OP
1

1Garageman

Well-known member
Joined
May 12, 2009
Messages
4,417
Location
Columbus, Ohio
So is there also a video out there where someone runs an extension cord from their neighbors house to get 3 phase electric motor to run?
 

Stuff

Well-known member
Joined
Aug 31, 2013
Messages
572
My daughter hired a guy to re-finish her hardwood floors. The floor sanders was 240V. I did not do a close inspection, but he used some kind of alligator clips to get two hots directly from exiting breakers in the load center !
Same when I had my floors done so appears to be standard practice. Alligator clips are easier/faster/cheaper than calling an electrician to install a receptacle that won't be used again.
 