Someone gave me a Lincoln AC/DC 225 welder and I am going to put in an outlet for it near the large door in my shop. It requires a 50 amp plugin and the total distance is right about 100' so I thought about using #8 wire rather than #10 because of the distance. I also have an abundance of 1/2" EMT and thought about using it, but 3 #8 wire in 1/2" is the limit so I am also assuming it might be a ***** to pull. So I guess I have 2 questions, should I go up to #8 and if I do would you use 1/2 EMT? Thanks
 
To avoid these ads, REGISTER NOW!

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,584
Location
Fullerton, CA
You need 2-#8s not 3. The ground wire can be a #10 if you want to install one.
The EMT itself is approved as a grounding conductor, but the EMT must be installed correctly.

Expect the pull to be a breeze. (I've pushed, not pulled 2-#8s 40' with 2-90° bends in it and it was super easy.)
 
OP
D

dfiler2

Well-known member
Joined
Dec 15, 2014
Messages
2,858
Location
NW Minnesota
Thanks, I forgot about downsizing the ground. For some reason I just feel better running a separate ground, so I probably will. I will be actually pushing it as you suggest.

Thanks again for your help

Are most other people comfortable not running a ground when using EMT?
 
OP
D

dfiler2

Well-known member
Joined
Dec 15, 2014
Messages
2,858
Location
NW Minnesota
Haha, ok, I have had pretty good luck pushing wire and my plan was to push it up around 2- 90's about 20', then pull it and push it through the pipe as I hang it. The pipe will be hung on the wall about 12' up. Sound reasonable?

Thanks
 

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,584
Location
Fullerton, CA
No. It's against the Code to do that

300.18 Raceway Installations.
(A) Complete Runs. Raceways, other than busways or exposed raceways having hinged or removable covers, shall be installed complete between outlet, junction, or splicing points prior to the installation of conductors.
 
OP
D

dfiler2

Well-known member
Joined
Dec 15, 2014
Messages
2,858
Location
NW Minnesota
Got it, I will go to a junction box, then pull it the rest of the way after the run is complete. Thanks
 

Aceman

Well-known member
Joined
Jan 28, 2007
Messages
2,513
Location
Eastern Oregon
Is there a reason for that?

1. It's easier to pull.
2. I can add a couple 120v circuits in the pipe if need be for general purpose receps, etc.
3. It's really not any harder to bend and there is very little price difference.


And to be honest, I use 3/4" pipe for most everything in a shop, warehouse, etc. I will use 1/2" for thermostat wire sleeves and lighting conduits in the ceiling where I know it'll most likely never have any more wires pulled into it, but that's about it.
 

crusher13

Member
Joined
Mar 30, 2015
Messages
9
Pretty sure a 50 amp receptacle requires #8 regardless of distance.


Sent from my iPhone using Tapatalk
 

TheEquineFencer

Well-known member
Joined
Jan 15, 2009
Messages
9,278
Location
Farmville, NC 27828
1. It's easier to pull.
2. I can add a couple 120v circuits in the pipe if need be for general purpose receps, etc.
3. It's really not any harder to bend and there is very little price difference.


And to be honest, I use 3/4" pipe for most everything in a shop, warehouse, etc. I will use 1/2" for thermostat wire sleeves and lighting conduits in the ceiling where I know it'll most likely never have any more wires pulled into it, but that's about it.

I second the above. I used 3/4 even for just 12 gauge for the lighting. Less fittings to stock, more room for future use.

After I ran the wall outlets, then I decided to wire outside the shop. I already had the conduit and boxes in place, alI had to do was pull the fish tape and knock a few holes it existing boxes to get it where I wanted it.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,041
Location
Modesto, CA

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,584
Location
Fullerton, CA
A problem with running 100' of #12s on a 50mp load is voltage drop.

With 100' of 12 you would have a voltage drop of 6.62% (5% is generally accepted as the maximum, although it's only a Fine Print Note in the NEC and is unenforceable)

If the conductor size is increased to a #10, there would only be a 4.16% drop.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,041
Location
Modesto, CA
A problem with running 100' of #12s on a 50mp load is voltage drop.

With 100' of 12 you would have a voltage drop of 6.62% (5% is generally accepted as the maximum, although it's only a Fine Print Note in the NEC and is unenforceable)

If the conductor size is increased to a #10, there would only be a 4.16% drop.

Yup youre right. I hastily typed my comment and was gonna say to use #10s at the end to combat VD, hit submit and forgot all about it! If the run was shorter, #12 would be fine!
 
To avoid these ads, REGISTER NOW!

crusher13

Member
Joined
Mar 30, 2015
Messages
9
OP- that welder:

http://www.lincolnelectric.com/assets/global/Products/K1170/e230.pdf

has a 20% duty cycle. The input current is 50a.

So u multiply the input current by .45 (20% duty cycle correction factor) to come up with circuit wire size.

.45 * 50a = 22.5a. This means #12 THWN in conduit can be used. Use 3 #12 or use 2 #12 and the conduit as the ground.

Use 6-50r and a 50a breaker.

http://m.ecmweb.com/qampa/code-qa-45


I am by no means a code guy electrical engineer not electrician but how is an inspector going to pass #12 or #10 for that matter hanging out a 50 amp breaker? You might put a 20% duty cycle welder on that outlet then go sell the place and the next guy says great welder outlet and put a 100% duty cycle machine on it. I don't buy an inspector would let that fly and if they would my conscience would let me save that few dollars on wire size
 

driz

Well-known member
Joined
May 22, 2008
Messages
701
Location
Northern NY
I did mine the easy way. I measured everything and drew up a nice little map of everything . Then I went down to the local electrical supply and said make it so. Easy peasy lemon squeezy and they just do it all on the fly because they do this stuff every day. I walked out the door with everything I needed and didn't have to even think about it. Sure I could have saved a couple bucks at Lowes but not all that much and it was simple:bowdown::shocking:without even having to calculate anything.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,041
Location
Modesto, CA
I am by no means a code guy electrical engineer not electrician but how is an inspector going to pass #12 or #10 for that matter hanging out a 50 amp breaker? You might put a 20% duty cycle welder on that outlet then go sell the place and the next guy says great welder outlet and put a 100% duty cycle machine on it. I don't buy an inspector would let that fly and if they would my conscience would let me save that few dollars on wire size

Maybe u should read the code instead of questioning what i wrote!
 

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,584
Location
Fullerton, CA
I am by no means a code guy electrical engineer not electrician but how is an inspector going to pass #12 or #10 for that matter hanging out a 50 amp breaker? ......... I don't buy an inspector would let that fly

You have no idea at all as to what an inspector would or would not approve. It's done all the time....... and it's right
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
No one really thinks 12 is a great idea but it is legal to 65 ft I believe for that machine. 10 is so much better and any machine comes with a fak pak cord wont overheat it. As I mention earlier only 250 feeders call for 8 and even then they wont burn up a 10 in a home shop.
 
OP
D

dfiler2

Well-known member
Joined
Dec 15, 2014
Messages
2,858
Location
NW Minnesota
Thanks sberry,

So it sounds like #10 would do fine, but I'm wondering if there is any reason not to go with #8. There would be about a $36 cost difference if I pull three wires and of course it would be harder to work with. It also sounds like most are comfortable using the conduit for a ground, so that would reduce the savings to $24. It just seems to me with so many connections, over time you risk having an issue.

After finding GJ last year and reading a lot, I decided to use EMT for all my electrical and that has worked out really well. It allowed me to spend some time working in the shop and adding electrical just where I needed it. This was my first experience using EMT and it is a little more work but I know I have saved money and time overall. My point here is that it just seems like I should run a separate ground wire but I really don't have enough experience with it to say for sure.

Comments and Opinions welcome
 
Last edited:

slodat

ALLIANCE MEMBER
Joined
Feb 6, 2010
Messages
3,682
Location
Central-ish, WA
I pull in a ground personally. The way I see it, I want the breaker to trip on a fault. Pulling in a ground gives me peace of mind that there is a low impedance short circuit current path back to the source and that the conduit is at ground potential. I'm a high voltage relay technician.. I think about this stuff :)
 
Last edited:

crusher13

Member
Joined
Mar 30, 2015
Messages
9
I understand how some of you can feel threatened when someone new comes along but you got to be superdicks right off the bat?


I don't know if you thought I was the superdick wasn't trying to be I thought he was a bit sarcastic I am not threatened as I said I know how to find things in the code and was just surprised it was legal obviously it is and it is right who knew? I still wouldn't do it as it isn't worth it in my eyes.



Sent from my iPhone using Tapatalk
 

Jlarson

Well-known member
Joined
Mar 27, 2015
Messages
738
Location
AZ
I pull in a ground personally. The way I see it, I want the breaker to trip on a fault. Pulling in a ground gives me peace of mind that there is a low impedance short circuit current path back to the source and that the conduit is at ground potential. I'm a high voltage relay technician.. I think about this stuff :)

Actually a properly installed metallic raceway is a better path for fault current. Tests have shown the majority of current will be on the conduit.
 

Kevin C

Well-known member
Joined
Aug 4, 2011
Messages
1,653
Location
Portland OR
Actually a properly installed metallic raceway is a better path for fault current. Tests have shown the majority of current will be on the conduit.

Good point, I still like using a separate ground inside the raceway. Just incase the conduit ever gets separated (or has a loose connection), I still have a ground path.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,041
Location
Modesto, CA
Don't be a jackass the last part of my post said even if that was true I wouldn't do it. Just because it is code doesn't make it right

I wasnt meaning to be a jackass.

However, if u think the code isnt right for this particular subject then please explain how millions of shops have been wired for welders in this regard and have had no issues!
 
To avoid these ads, REGISTER NOW!