Outlets series OK or parallel necessary

machsnell

Well-known member
Joined
Jun 12, 2010
Messages
942
Location
Northern Virginia
So I wired my garage with alternating 20 amp 12 wire and 20 amp outlets.

I wired them in series mostly and not in parallel unless I had an outlet separated from lower run and had 3 wires in the box

I have gfci outlets on the start of each circuit to protect the entire circuit.

My question is do I need to redo all of my outlets to have pigtails and be wire in parallel or am I safe the way they are?

I did a good job no backstabbing and tight circles and tightened well on all the screws.



Sent from my SM-G900V using Tapatalk
 
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,089
Location
Modesto, CA
Umm i think youre using the wrong terminology.

Outlets would have to be wired in parallel to work.

I think what youre referring to is that u connected them outlet to outlet instead of pigtailing?

Do u have a pic?
 
OP
M

machsnell

Well-known member
Joined
Jun 12, 2010
Messages
942
Location
Northern Virginia
Yes that is it. I connected the source wire on the top screws and the outgoing wire to the lower screws.

They are both connected with metal so I didn't think it mattered but I did so anyway



Sent from my SM-G900V using Tapatalk
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
You wired them like this...
two-wire-outlet.jpg
 
OP
M

machsnell

Well-known member
Joined
Jun 12, 2010
Messages
942
Location
Northern Virginia
Thank god. I enjoyed wiring them up but I really didn't want to have to do it again.

Thanks for the advice all!

Sent from my SM-G900V using Tapatalk
 

nadogail

Well-known member
Joined
Jan 23, 2009
Messages
32,061
Location
Coronado, CA
IMHO the blacks and whites should be connected like the grounds.
Wire nutted together with a third conductor going to the receptacle. This will allow the other receptacles to keep working if one should fail.

Also the other receptacles can remain in service if one has been removed for any reason.
 

zmaxmotorsports

Well-known member
Joined
Jan 11, 2013
Messages
11,948
Location
South of omaha
IMHO the blacks and whites should be connected like the grounds.
Wire nutted together with a third conductor going to the receptacle. This will allow the other receptacles to keep working if one should fail.

Also the other receptacles can remain in service if one has been removed for any reason.

:beer::beer::beer::beer:
 

Slowgsr

Well-known member
Joined
Nov 14, 2014
Messages
610
Location
Southern ontario
I usually bring both bonds under the bonding screw on the box, cut one flush and leave the other long to the device.

I never pigtail unless it's #10 or #8 for line loss and the wires too big to terminate.
 

Shiftless

Well-known member
Joined
Mar 9, 2014
Messages
14,600
Location
East Bay SFO
I usually bring both bonds under the bonding screw on the box, cut one flush and leave the other long to the device.

I never pigtail unless it's #10 or #8 for line loss and the wires too big to terminate.

I assume you are talking just about the grounding wires (green or bare) under the bonding screw on the box.
OP was asking about the black and white wires. I too like to pigtail for the above mentioned reasons.
 
Last edited:

CJ7VFR

Well-known member
Joined
Jan 13, 2015
Messages
2,941
Location
Central New Jersey
For the electrical jobs I have done around my house, I have done it 50/50 with pigtails or not.

If I am only adding in a few (two or three) receptacles, then I will just daisy chain the wires using the screws and bus bar on the receptacles.

If I am adding more than three, then I use pigtails everywhere. This has saved me more than once when I had to remove a receptacle but leave the rest of the circuit working. The pigtails made it easy to just remove the receptacle and wire nut off the ends of the wire going to that receptacle so that the entire circuit was still working until I had time to replace the removed receptacle.

Jim
 

ExxWhy

Well-known member
Joined
Dec 8, 2014
Messages
97
Location
NE Ohio
In the rare case of temporarily removing a receptacle, it's not too difficult to wire nut the wires together if you need to have power downline. For the small amount of electrical work I do, I prefer using the back clamp style receptacles, very secure connections and easy easy.
 

LS6 Tommy

Well-known member
Joined
Dec 27, 2013
Messages
26,162
Location
Northern NJ
IMHO the blacks and whites should be connected like the grounds.
Wire nutted together with a third conductor going to the receptacle. This will allow the other receptacles to keep working if one should fail.

Also the other receptacles can remain in service if one has been removed for any reason.

The "downstream" recepts will still work if one fails. No current flows through one receptacle to the next. I swear I posted this exact info a while back.
:dunno:

Tommy
 
Last edited:

checkthisout

Well-known member
Joined
Sep 5, 2008
Messages
5,232
It's fine.

Downfalls to pigtails:

1) more wire nuts

2) more connection points in circuit that increase resistance and can fail (I'll get burned on this one).

3) More wire to have to fit into the box

Benefits:

1) Easier to push the receptacle into the box since you only have to fold 3 wires instead of 5

2) Pigtailed outlets can be made up beforehand

3) Losing benefit #2, you can easily leave the outlet out or remove it and still maintain downstream power. This is handy if you are doing a remodel project and need nearby outlets working while you texture, paint and trim out a room.
 

Syberia

Well-known member
Joined
Jan 13, 2014
Messages
1,451
Location
Perris, CA
I've always used the screws. How exactly does a solid, immobile buss bar between two screws fail? Usually the thing that fails are the contacts inside, which have nothing to do with the connection between the screws.
 
To avoid these ads, REGISTER NOW!

zmaxmotorsports

Well-known member
Joined
Jan 11, 2013
Messages
11,948
Location
South of omaha
I've always used the screws. How exactly does a solid, immobile buss bar between two screws fail? Usually the thing that fails are the contacts inside, which have nothing to do with the connection between the screws.

Youve never seen one burned up? Ive seen more than one over the years.
The city of omaha wont sign off on a residential rough in unless all the wires are tailed out for the device to be installed,Its been that way since the 80s atleast.
 

Cmreschke

Well-known member
Joined
Feb 15, 2014
Messages
775
Location
North of Detroit
I have a q for the op. Are these part of a multi wire circuit (shared neutral between 2 circuits) or individual circuits (1 ckt per neutral)?
 

LS6 Tommy

Well-known member
Joined
Dec 27, 2013
Messages
26,162
Location
Northern NJ
What happens to the downstream outlets when he loses a jumper on one of those outlets ?;)
That wasn't the question. The question was what happens when the OUTLET fails.:lol_hitti

Seriously, it happens. It's happened to me. It's also really rare. When it does happen, you have to replace the receptacle regardless of what it's feeding down stream, so IMO, it's not really a benefit to use pigtails just for that reason.

Tommy
 

My Old Tools

Well-known member
Joined
Jun 4, 2014
Messages
5,450
Location
Hamrick Lake, TX
There is a difference between spring loaded back stab and back clamping. Back clamping work great, very secure, and save a ton of time bending wires around screws.
 

malibu101

Well-known member
Joined
Jul 1, 2005
Messages
3,909
Location
Walnutport PA
There is a difference between spring loaded back stab and back clamping. Back clamping work great, very secure, and save a ton of time bending wires around screws.

The difference is what you said above-- spring pressure stab versus screw clamp.
Nothing at all wrong with clamps. Very commonly used where stranded wires are used.
Spring pressure back stabs are a loose connection waiting to happen. Period.
 

Speedy Petey

Well-known member
Joined
Apr 22, 2012
Messages
1,430
Location
NY State
Youve never seen one burned up? Ive seen more than one over the years.
The city of omaha wont sign off on a residential rough in unless all the wires are tailed out for the device to be installed,Its been that way since the 80s atleast.
Sure, I've seen it. Literally as many times as I have seen a failed wire nut splice.
Do it right and it won't fail, either way you do it.

The arguments given for pigtailing are lame IMO. "If you have to remove a device they all keep working", or "If one fails the others keep working".
Again, legitimate but lame in the real world scope of things. Again, do it right and it won't fail.

Does Omaha have a written amendment for this overkill practice?
 

Cmreschke

Well-known member
Joined
Feb 15, 2014
Messages
775
Location
North of Detroit
And the main reason to pigtail is to dummy proof it for the morons. If you go to replace a device, it doesn't matter if you interrupt the circuit down stream, since, the circuit should be OFF!!!

Just like taping a recep or switch prior to installing it. I don't really care if someone works on it when I'm done, it's not taped, if they get shocked by it then that person has failed the most basic of safety rules. SHUT THE POWER OFF!!!
 

Slowgsr

Well-known member
Joined
Nov 14, 2014
Messages
610
Location
Southern ontario
I assume you are talking just about the grounding wires (green or bare) under the bonding screw on the box.
OP was asking about the black and white wires. I too like to pigtail for the above mentioned reasons.

Bonding wires, bonding screws. Terminology isn't that important - but the only ground wire is at a services point of entry.
 

zmaxmotorsports

Well-known member
Joined
Jan 11, 2013
Messages
11,948
Location
South of omaha
Sure, I've seen it. Literally as many times as I have seen a failed wire nut splice.
Do it right and it won't fail, either way you do it.

The arguments given for pigtailing are lame IMO. "If you have to remove a device they all keep working", or "If one fails the others keep working".
Again, legitimate but lame in the real world scope of things. Again, do it right and it won't fail.

Does Omaha have a written amendment for this overkill practice?

Every inspector Ive ever dealt with in omaha over the years has had the same rule,Im sure I could make a phone call and get a copy of it in writing.;)
 

zmaxmotorsports

Well-known member
Joined
Jan 11, 2013
Messages
11,948
Location
South of omaha
And the main reason to pigtail is to dummy proof it for the morons. If you go to replace a device, it doesn't matter if you interrupt the circuit down stream, since, the circuit should be OFF!!!

Just like taping a recep or switch prior to installing it. I don't really care if someone works on it when I'm done, it's not taped, if they get shocked by it then that person has failed the most basic of safety rules. SHUT THE POWER OFF!!!

Sometimes its not possible/feasable to turn the power off.
The main reason I tape outlets/switches is so I know that I did the job/was the last one in there if I have to come back 5 years later to look at something,it also slows idiots down from messing with things.
Its a habit from left over from my early days in the trades doing commercial work with metal boxes and plaster ears I guess.
And yes I do tape wire nuts on in machinery that rattles/shakes a lot,Again it also keeps maintenance monkeys from messing with stuff.:dunno:
 

egdede

ALLIANCE MEMBER
Joined
Dec 20, 2009
Messages
2,103
If you haven't pulled every single wire in the entire structure yourself you should pigtail. This is because breaking a circuit by disconnecting a outlet can cause sometimes cause serious problems in a shared neutral circuit (220v)!!!
Shared neutral circuits use one neutral wire to serve 2 circuits. These circuits are powered by the opposite side of the 110 legs feeding a structure. So, if the both breakers are not tripped, and a circuit is interrupted, the non-interupted circuit can be fed with 220v!!!

Tracking shared neutral circuits can be tricky at best (when they have been installed by professionals to the code requirements of their time), or impossible (when shade tree electricians have worked their magic). So, unless you really know how every outlet is powered (where each wire comes from), the only way to really ensure you don't send a 220 surge somewhere else by breaking a circuit when pulling an outlet even when a switch is thrown for the outlet you are working on is by throwing your main or using pigtails.

Pigtails need bigger boxes. But, done right, make for easier work in the future.
 
Last edited:

egdede

ALLIANCE MEMBER
Joined
Dec 20, 2009
Messages
2,103
The arguments given for pigtailing are lame IMO. "If you have to remove a device they all keep working", or "If one fails the others keep working".
Again, legitimate but lame in the real world scope of things. Again, do it right and it won't fail.


Please see my above post. Think of your whole house as being a shared neutral circuit. (One neutral and two hots). Think what happens if a neutral is disrupted at the pole!!!
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,089
Location
Modesto, CA
If you haven't pulled every single wire in the entire structure yourself you should pigtail. This is because breaking a circuit by disconnecting a outlet can cause sometimes cause serious problems in a shared neutral circuit even if the breaker is thrown for the circuit being worked on!

Shared neutral circuits use one neutral wire to serve 2 circuits. These circuits are powered by the opposite side of the 110 legs feeding a structure. So, if the both breakers are not tripped, and a circuit is interrupted, the non-interupted circuit can be fed with 220v!!!

Tracking shared neutral circuits can be tricky at best (when they have been installed by professionals to the code requirements of their time), or impossible (when shade tree electricians have worked their magic). So, unless you really know how every outlet is powered (where each wire comes from), [/b]the only way to really ensure you don't send a 220 surge somewhere else by breaking a circuit when pulling an outlet even when the breaker is thrown for the circuit you are working on is by throwing your main or using pigtails.[/b]

Pigtails need bigger boxes. But, done right, make for easier work in the future.

If one breaker is off on a MWBC, how would there be 240v? Thats not possible. Only 1 breaker is on. And nominal voltage is 120v/240v...
 

egdede

ALLIANCE MEMBER
Joined
Dec 20, 2009
Messages
2,103
Yeah, I see your point. I was translating the specific incident that learned me about shared neutral circuits to a general statement. Have edited my post to be accurate (I hope!).

I think I also learned why you don't throw switches to work on fixtures that time, or am mixing up the lessons I learned working on a then 50 year-old house 25 years ago!!!

Also, note I did not want call it a MWBC because people on the web sometimes think 'multi-wire' means 'romex'!!! That can lead to many side discussions.


In the end, we should use pigtails because fixture connection failures won't at best; disrupt downstream fixtures and, at worst (if on a shared neutral circuit); send 220v to downstream fixtures.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,089
Location
Modesto, CA
Yeah, I see your point. I was translating the specific incident that learned me about shared neutral circuits to a general statement. Have edited my post to be accurate (I hope!).

I think I also learned why you don't throw switches to work on fixtures that time, or am mixing up the lessons I learned working on a then 50 year-old house 25 years ago!!!

Also, note I did not want call it a MWBC because people on the web sometimes think 'multi-wire' means 'romex'!!! That can lead to many side discussions.


In the end, we should use pigtails because fixture connection failures won't at best; disrupt downstream fixtures and, at worst (if on a shared neutral circuit); send 220v to downstream fixtures.

MWBC is the correct term for a circuit with a shared neutral. If people are confusing MWBC with NM-b wiring then they have no idea what theyre talking about. NM-b is a multi-conductor CABLE.
 