I'm installing fluorescent lights in the garage. before sheetrocking, i installed 14awg romex, daisychaining to each light location, leaving a 2' hangwire. then the rockers came through, and drilled a 1" hole and poked the wire through. Now I've bought my lights, and i think there supposed to have a box behind them. I'd like to use either 1/2" or 3/4" x 4" diameter pan boxes, but I'm in the US, and it doesn't look like either one of these pan boxes has the cubic inch capacity to install two 14awg romex wires. So all in all I have:
2-14 awg ground wires (one with each run of romex)
2-14 awg hot wires plus the 18 awg fixture hot wire
2-14 awg neutral wires plus the 18 awg fixture neutral wires.
Is there some provision in the NEC for needing less cubic inches when using pan boxes for lights? i just don't see how they can be used at 2 cubic in per conductor, for me that's already 8 cubic inches without counting for the rest...?