Pancake box under exterior light canopy

ycgoat

Well-known member
Joined
Mar 28, 2020
Messages
971
Location
S.E. Va
I keep going back and forth on this and was again corrected (reasonably) that you can not use a pancake box outdoors. The lights I am installing are advertised as waterproof and seal to the wall not the box, so would the space inside the fixture that is sealed to the wall be protected. Wet Location is A location in which water or other liquid can drip, splash, or flow on or against electrical equipment.

Is this reasonable thinking or am I reaching; trying to justify what I already want to do.
 
To avoid these ads, REGISTER NOW!

Zeke

Well-known member
Joined
Aug 13, 2009
Messages
17,176
Location
Long Beach CA, the sewer by the sea.
You would think yes, but not all fixtures have that feature. So the next guy changes the fixture and the pancake is not protected — so, no.

There are 2 other threads on the first page of this forum dealing with this.
 

Zeke

Well-known member
Joined
Aug 13, 2009
Messages
17,176
Location
Long Beach CA, the sewer by the sea.
If the box is recessed so that the face is flush with the wall, you're ok. You can't surface mount the pancake box outside.
One would wonder why if a person could recess a pancake, why not a 4" octagon?

OK, I know sometimes there are headers, etc. But in general, most things like that can be avoided. I guess what I'm saying is >90% of the time pancakes are laziness.
 

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
8,129
Location
Central Iowa
One would wonder why if a person could recess a pancake, why not a 4" octagon?

OK, I know sometimes there are headers, etc. But in general, most things like that can be avoided. I guess what I'm saying is >90% of the time pancakes are laziness.
I do it all the time on garages that aren't going to be finished on the inside. I run a 4" hole saw through the siding, but stop at the sheathing. The pilot bit goes into the sheathing far enough to mark the center, I then ran a hole saw through the sheathing that was just large enough for a rigid coupling to fit into. Attach the rigid coupling to the box via a chase ******, screw the box to the sheathing with the coupling poking through on the inside, screw a flex connector (usually a 90°) into the rigid coupling. Done, and it's way faster than setting blocking to mount the octagon to.
 

Zeke

Well-known member
Joined
Aug 13, 2009
Messages
17,176
Location
Long Beach CA, the sewer by the sea.
That sounds good ^^^^ but the thing you said was '"siding" and I was talking about masonry. If siding, I too would go about it differently taking the easiest path, which it sounds like you've perfected.
 
To avoid these ads, REGISTER NOW!

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
8,129
Location
Central Iowa
That sounds good ^^^^ but the thing you said was '"siding" and I was talking about masonry. If siding, I too would go about it differently taking the easiest path, which it sounds like you've perfected.
I was answering your question as to why someone would recess a pancake vs. an octagon. I have no idea what the OP has on the exterior.
 
OP
Y

ycgoat

Well-known member
Joined
Mar 28, 2020
Messages
971
Location
S.E. Va
Its a metal building, I am likely going to recess a single gang, since I can’t surface mount a box that will be concealed under the fixture.
 

Zeke

Well-known member
Joined
Aug 13, 2009
Messages
17,176
Location
Long Beach CA, the sewer by the sea.
I was answering your question as to why someone would recess a pancake vs. an octagon. I have no idea what the OP has on the exterior.
Yeah, I was crossing my posts with another thread. Still, pancakes limit wire fill so you must plan your runs accordingly. As I said, it sounds like you've got a good thing going there that saves time finding blocking, etc. Being hard in a SoCal city, I run into metal siding about once a decade.
 
Last edited:

yeldogt

Well-known member
Joined
Jan 2, 2012
Messages
18,184
I do it all the time on garages that aren't going to be finished on the inside. I run a 4" hole saw through the siding, but stop at the sheathing. The pilot bit goes into the sheathing far enough to mark the center, I then ran a hole saw through the sheathing that was just large enough for a rigid coupling to fit into. Attach the rigid coupling to the box via a chase ******, screw the box to the sheathing with the coupling poking through on the inside, screw a flex connector (usually a 90°) into the rigid coupling. Done, and it's way faster than setting blocking to mount the octagon to.
I'm trying to picture this .... ??

What type of box and why the need for flex?

I like the hole saw retrofit and using the hold saws pilot hole to drill for the wire ... are you doing exposed conduit inside?
 