Panel box knockout

nwester

Member
Joined
Mar 21, 2020
Messages
11
Location
Washington State
CB94B2E8-C3A5-4BA7-B9DF-28CDCEDB6B56.jpeg

Hello everyone. I’m running a 10-3 with ground for a 30 amp breaker for a generator. I’m planning on using the bottom left opening which was put there when I had the house built. It runs into my 6 foot crawl space. My question is that after I run the wire through, there is still a ton of room in the hole. Any ideas how I can do this so I’m following code. The hole about 2 inches. Thanks guys for the help.
 
To avoid these ads, REGISTER NOW!

Dustball

Well-known member
Joined
Jun 25, 2011
Messages
2,081
Location
Hudson, WI
Pull the cord grip off, use two conduit reducing washers and a smaller cord grip to accommodate the cable you want.

 
Last edited:

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,856
Location
NW Iowa
Pull the cord grip off, use two conduit reducing washers and a smaller cord grip to accommodate the cable you want.


I'm assuming that's not a cord grip but a conduit chase that runs to the crawl space. I would run my wire inside the conduit, staple right after it leaves the conduit and tuck the insulation back around the wire inside the panel.
 

Terry D

Well-known member
Joined
Mar 25, 2015
Messages
2,202
Location
St. Louis, MO.
I'm assuming that's not a cord grip but a conduit chase that runs to the crawl space. I would run my wire inside the conduit, staple right after it leaves the conduit and tuck the insulation back around the wire inside the panel.

I second that
 
OP
N

nwester

Member
Joined
Mar 21, 2020
Messages
11
Location
Washington State
I'm assuming that's not a cord grip but a conduit chase that runs to the crawl space. I would run my wire inside the conduit, staple right after it leaves the conduit and tuck the insulation back around the wire inside the panel.

Sorry guys, I should have been more clearer for you. It is a conduit chase that runs down to the crawl space. And there is a joist right next to it so it will be really easy to staple. Thanks again guys!
 

Raisedonadeere

Well-known member
Joined
Jul 31, 2017
Messages
436
Location
Central KY
OK so OP now has a 10/3 cable through that chase, -- how many of what size cables can he additionally run down to that crawl space through that 2" "chase" or is it a "sleeve"? Lets just say he wants to power a sump pump and run a light circuit down there, maybe power a dehumidifier also.

And it has to pass inspection.
 

Terry D

Well-known member
Joined
Mar 25, 2015
Messages
2,202
Location
St. Louis, MO.
OK so OP now has a 10/3 cable through that chase, -- how many of what size cables can he additionally run down to that crawl space through that 2" "chase" or is it a "sleeve"? Lets just say he wants to power a sump pump and run a light circuit down there, maybe power a dehumidifier also.

And it has to pass inspection.

There is no chart that I am aware of how many NM-Bs can go in a certain size conduit. You just have to use your best judgment to keep it at around a 40% fill and calculate derating factors if the conduit is more than 24" long
 
To avoid these ads, REGISTER NOW!

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
38,398
Location
Richmond, VA
Bottom left? Interlock kits generally require the space closest to the main.

You are using an interlock, right?
 
OP
N

nwester

Member
Joined
Mar 21, 2020
Messages
11
Location
Washington State
Bottom left? Interlock kits generally require the space closest to the main.

You are using an interlock, right?

Yes, for my panel manufacture the interlock will be installed in the upper right corner. I’ll be moving a 40 amp breaker down to maker room for the 30 amp breaker I’ll be back feeding to my generator. The wire I’m feeding up through that conduit is for the 30 amp breaker.
 
OP
N

nwester

Member
Joined
Mar 21, 2020
Messages
11
Location
Washington State
You are correct, I hope he understands about interlocks

Thanks everyone for the help. I am familiar with the interlocks. I just installed one on the panel in my shop so I can run my well during an outage. The power goes out up where I live quite often and got tired of not having lights and water.
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
38,398
Location
Richmond, VA
Yes, for my panel manufacture the interlock will be installed in the upper right corner. I’ll be moving a 40 amp breaker down to maker room for the 30 amp breaker I’ll be back feeding to my generator. The wire I’m feeding up through that conduit is for the 30 amp breaker.

Awesome!
 