This is the main panel for my old 1950s house. I haven’t been in this thing for 30 years.

When I moved in in the early 90s, there was a split phase plug for the oven. My memory is a little hazy, but I recall pulling that up into the attic and dropping it back down into the wet bar for possible installation of a split phase, espresso machine. The stove is gas.

I didn’t end up getting the espresso machine. And looking up above the web bar all I see is a standard 120 V plug. I’m guessing I pulled that big split phase line back up into and capped it. [Edit – this is incorrect. See below.]

It’s hotter than heck. Before I go up there in the attic and start hunting around for a capped split phase line buried in the blown insulation, I wanted to check if there was a way looking at these breakers to guess which one would’ve controlled that circuit.

I thought I’d be able to spot it. But I’m not much of an electrician.

My other alternative is just to shut down the whole house and then go find it. Which is fine, but I’d rather keep the AC on.

Any insight appreciated. Thanks




IMG_5313.jpeg
 
Last edited:
To avoid these ads, REGISTER NOW!

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
22,765
Location
VT
What do you mean by split phase?

Are you using the plug?

What are you looking to do?

Plug a loud radio in and go flip a couple breakers....

Btw, a splice burried in insulation is a no-no
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
5,909
Location
NJ
Possibly the first red 20a cb has what could have had stove cable connected to it. It looks like it has been repurposed for 120v circuit. The black conductor with red stripes is connected to the neutral.

I can't determine if there is a neutral wire for that cable.

There are other problems in that panel. I'll list separately.
 
OP
B

bluedog225

Well-known member
Joined
Jan 31, 2012
Messages
3,280
Location
Texas
Spit phase-Line 1, line 2, neutral, and ground. It’s my understanding that’s what would’ve been provided to an oven.

I don’t think I’ve used the plug since then. I may have never used it. And I don’t stand behind any work. I did 30 years ago. I knew even less than that I know now.

I want to reestablish split phase power at the oven location to run an oven/microwave combo unit. Photos below. I believe the plug for the new unit is called NEMA 14–30.

I went ahead and pulled the plug above the web bar. I thought I would find 12 gauge romex from some other circuit. Instead, it’s got a black insulated wire, black insulated wire with a white piece of tape on it, and a ground wire. If I had to guess I’d say it’s 8 or 10 gauge (stranded).

So maybe I didn’t pull the wire back up. Though I can’t quite make sense of a three wire set up providing split phase. Unless it’s 1, line 2, neutral, and neutral with no ground.

And thanks for the reply.

IMG_5316.jpeg
 
OP
B

bluedog225

Well-known member
Joined
Jan 31, 2012
Messages
3,280
Location
Texas
Possibly the first red 20a cb has what could have had stove cable connected to it. It looks like it has been repurposed for 120v circuit. The black conductor with red stripes is connected to the neutral.

I can't determine if there is a neutral wire for that cable.

There are other problems in that panel. I'll list separately.

I’ve never messed with the panel.

But the previous owner was an electrician. And I have had electricians out here since 1995 trying to figure out some unusual wiring.

It’s entirely possible that one of the electricians out here since 95 made some changes.
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
5,909
Location
NJ
Is the white cb rated at 40 amps? What load is connected to it? Conductors look way undersized. Maybe ac unit?

The ground wires need to terminate on a dedicated ground bar because this is a sub panel.

Really time for a panel upgrade.

Can you take a pic of the panel on the right with cover off and how it connects to this one?
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
5,909
Location
NJ
There should be a 3 conductor cable going up to the stove. It may be the 2 black and a bare ground wire as the cable or a cable w/black, red, white.

Hopefully, the latter. The 4 wire plug should not be used with a 3-wire feed.

Also, a 3 wire cable with an uninsulated neutral should not be used with a subpanel for a stove or dryer.

Edited based of OP'S recent reply.
 
Last edited:
OP
B

bluedog225

Well-known member
Joined
Jan 31, 2012
Messages
3,280
Location
Texas
Is the white cb rated at 40 amps? What load is connected to it? Conductors look way undersized. Maybe ac unit?

The ground wires need to terminate on a dedicated ground bar because this is a sub panel.

Really time for a panel upgrade.

Can you take a pic of the panel on the right with cover off and how it connects to this one?

Yes, white cb is 40 amps. Close-ups of the breakers are below.

I don’t know what the white CB powers. It may not be labeled correctly.

I believe this is the main panel as a fed directly by the meter panel. Photo below.

Following the circuit breaker close-ups, and the overview of the meter in this panel, is a picture of a subpanel. I’ve had the subpanel replaced in recent memory. Maybe 10 years ago.

The last photograph is the inside breaker panel. It was also replaced 10 years ago.

It would make sense if someone changed panel I was originally talking about. My memory from back in the day is that turning off the stove circuit was easy and straightforward.

IMG_5317.jpegIMG_5318.jpegIMG_5319.jpegIMG_5321.jpeg

IMG_5320.jpeg
 

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
22,765
Location
VT
Possibly the first red 20a cb has what could have had stove cable connected to it. It looks like it has been repurposed for 120v circuit. The black conductor with red stripes is connected to the neutral.

Kind of looks like it, especially given this:


I went ahead and pulled the plug above the web bar. I thought I would find 12 gauge romex from some other circuit. Instead, it’s got a black insulated wire, black insulated wire with a white piece of tape on it, and a ground wire. If I had to guess I’d say it’s 8 or 10 gauge (stranded).

Really does seem like it's time for an upgrade, probably an electrician
 
OP
B

bluedog225

Well-known member
Joined
Jan 31, 2012
Messages
3,280
Location
Texas
I’ve pulled the plug above the wet bar.

One black wire, one black wire with a white stripe, one ground wire. I will note that much of the house is ungrounded from the 50s.

White to black 120 V
black ground 120 V
White to ground zero V
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
5,909
Location
NJ
Haha, yes, that panel exceeds 6 throws of hand so changing it out to non-Zinsco with main cb is needed.

OP posted the 4wire cord as I was replying.
 
OP
B

bluedog225

Well-known member
Joined
Jan 31, 2012
Messages
3,280
Location
Texas
I took that pic as his new plug, that's he's trying to figure out how to install
Yes. That plug is the new plug on the new appliance. The appliance I’m now thinking of selling. Because upgrading the main panel will be a **** show. I suspect. I was hoping to die or move before that was necessary. 😁
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
5,909
Location
NJ
I’ve pulled the plug above the wet bar.

One black wire, one black wire with a white stripe, one ground wire. I will note that much of the house is ungrounded from the 50s.

White to black 120 V
black ground 120 V
White to ground zero V
Pic of that cable possible?

The ac unit appears to be on the 40A.

Could that cable come out the subpanel with the spare 30a?
 

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
22,765
Location
VT
I’ve pulled the plug above the wet bar.

One black wire, one black wire with a white stripe, one ground wire. I will note that much of the house is ungrounded from the 50s.

White to black 120 V
black ground 120 V
White to ground zero V

I went ahead and pulled the plug above the web bar. I thought I would find 12 gauge romex from some other circuit. Instead, it’s got a black insulated wire, black insulated wire with a white piece of tape on it, and a ground wire. If I had to guess I’d say it’s 8 or 10 gauge (stranded).

Well which is it?

Post a pic...
 
To avoid these ads, REGISTER NOW!

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
5,909
Location
NJ
Standby. It’s two black wires. One of the black wires has a white piece of tape around it.

What’s nine throws of hand?
The white tape may be covering the red dashes if it's the same cable.

Your panel has 9 independent cbs that need to be turned off to isolate the house. 6 is the limit, and 1 is preferred.
 
OP
B

bluedog225

Well-known member
Joined
Jan 31, 2012
Messages
3,280
Location
Texas
The white tape may be covering the red dashes if it's the same cable.

Your panel has 9 independent cbs that need to be turned off to isolate the house. 6 is the limit, and 1 is preferred.

Got it. Thanks.

I don’t see any red stripe on either black cable.

I’m guessing if I pull a permit, I’m opening up a whole can of worms with a city inspection. As in the possibility of having to rewire the entire house.

Am I thinking correctly?

Is there an opportunity to pull split phase from one of those spares in the subpanel?


Or just abandon ship? Pretty sure I can sell this microwave/convection oven and I picked up a Restore for a profit.



IMG_5323.jpeg
 

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
22,765
Location
VT
Got it. Thanks.

I don’t see any red stripe on either black cable.

I’m guessing if I pull a permit, I’m opening up a whole can of worms with a city inspection. As in the possibility of having to rewire the entire house.

Am I thinking correctly?

Is there an opportunity to pull split phase from one of those spares in the subpanel?


Or just abandon ship? Pretty sure I can sell this microwave/convection oven and I picked up a Restore for a profit.



IMG_5323.jpeg

That's not fed from the panel you opened as far as I can tell.

Are you able/comfortable taking the cover off the sub panel?

Or, as I said before, plug a loud radio in and go flip a few breakers
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
5,909
Location
NJ
Not sure that is the same cable.

Open up the sub panels.

Do the appliance instructions have an option for a 3-wire cord? And you just chose the 4wire?
 
OP
B

bluedog225

Well-known member
Joined
Jan 31, 2012
Messages
3,280
Location
Texas
Edit

That black wire with the white tape on it does have a red stripe.

I had to get the iPhone up there and take pictures from behind. It’s coming out of the ceiling and not that easy to get to.

Sorry not to catch that earlier.

It makes more sense that it didn’t just disappear.
 
OP
B

bluedog225

Well-known member
Joined
Jan 31, 2012
Messages
3,280
Location
Texas
That's not fed from the panel you opened as far as I can tell.

Are you able/comfortable taking the cover off the sub panel?

Or, as I said before, plug a loud radio in and go flip a few breakers
Sorry. Yes. One black wire has a red stripe. I missed it.

Yes, I put the wire nut on there.

It looks like it requires the split phase power. See below. I didn’t choose the plug. I simply looked at what was coming out of the back of the appliance.

IMG_5335.png
 
OP
B

bluedog225

Well-known member
Joined
Jan 31, 2012
Messages
3,280
Location
Texas
Back to this image. One black wire, one black wire with a red stripe, and one ground wire run from this panel to the plug.

I don’t know why they black wire with the red stripe was taken to the ground bar.

As I mentioned earlier, much of this house is ungrounded. But I have run across bare 12 gauge grounding wire run here and there to a couple of loads like ceiling fans. I think this was done by the previous owner.

I am comfortable, running a wire if I can reestablish the split phase circuit. I’ll have to go out and check tomorrow morning, but I believe the single ground rod is below the subpanel. [edit-ground rod at main where it should be] But it won’t be that big a project to run something through the attic and join up with this three wire run.

Though I’lll admit to being confused about the neutral ground connection location and how it works in this situation.

And yes, I can open the subpanel and photograph in the morning. [see below]

And many thanks to you all.

IMG_5313.jpeg
 
Last edited:

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
5,909
Location
NJ
Sorry. Yes. One black wire has a red stripe. I missed it.

Yes, I put the wire nut on there.

It looks like it requires the split phase power. See below. I didn’t choose the plug. I simply looked at what was coming out of the back of the appliance.

IMG_5335.png
The voltage spec reads as though it is straight 240v, no 120 needed. Not common.
Then mfr pre-wired with an L14-30P.

I'm not sure what you need.

Take pic of nameplate.
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
5,909
Location
NJ
Back to this image. One black wire, one black wire with a red stripe, and one ground wire run from this panel to the plug.

I don’t know why they black wire with the red stripe was taken to the ground bar.

As I mentioned earlier, much of this house is ungrounded. But I have run across bare 12 gauge grounding wire run here and there to a couple of loads like ceiling fans. I think this was done by the previous owner.

I am comfortable, running a wire if I can reestablish the split phase circuit. I’ll have to go out and check tomorrow morning, but I believe the single ground rod is below the subpanel. [edit-ground rod at main where it should be] But it won’t be that big a project to run something through the attic and join up with this three wire run.

Though I’lll admit to being confused about the neutral ground connection location and how it works in this situation.

And yes, I can open the subpanel and photograph in the morning. [see below]

And many thanks to you all.

IMG_5313.jpeg
Forget the idea of a separate conductor. It has to be contained in the same cable.

Big red flag, is you discussing grd rods for this branch circuit.

Call a sparky.
 
OP
B

bluedog225

Well-known member
Joined
Jan 31, 2012
Messages
3,280
Location
Texas
The voltage spec reads as though it is straight 240v, no 120 needed. Not common.
Then mfr pre-wired with an L14-30P.

I'm not sure what you need.

Take pic of nameplate.


Here it is. I may have pulled European version of the manual.


IMG_5340.jpegIMG_5339.jpeg
 
OP
B

bluedog225

Well-known member
Joined
Jan 31, 2012
Messages
3,280
Location
Texas
Forget the idea of a separate conductor. It has to be contained in the same cable.

Big red flag, is you discussing grd rods for this branch circuit.

Call a sparky.
Mentioned the ground rod location. For some reason, I thought it was at the subpanel. Which I thought was inappropriate. But I was mistaken.
 
OP
B

bluedog225

Well-known member
Joined
Jan 31, 2012
Messages
3,280
Location
Texas
The guy who did that subpanel said he was the chief electrical inspector at one time. Though probably in the 70s.

I could pull a wire from the appliance location to the attic, get an electrician to re land the red striped wire, and make the final connection.

But if I need a 4 wire, pulling the wire from the panel is going to be way more trouble than this appliance is worth.

I’ll try to sell it.

Thank you all for the assist. I thought it was going to be an easier fix.
 

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
22,765
Location
VT
That's a 3-phase panel with the black feeding two bus bars,
Center lug probably not good for 2 wires.
Props for "creative recycling".
Thanks for explaining that.

I saw the jumper and had a WTF moment.


OP really needs to get these panels swapped out. The main panel, being outside, will be pretty quick, but require an electrician because the meter needs to be pulled.
 