It's been a long time since you could legally install a new panel in a closet.
Is the service to the house too small or is the panel just out of spaces?
If you're just out of space and the old panel is still in decent shape you might be able to feed a sub panel in a differant part of house from current panel.
Post some pictures of what's in there now.;)
 
OP
9

930dreamer

Super Moderator
Staff member
Joined
Oct 7, 2009
Messages
22,928
Location
Amarillo,TX and Stinnett,TX
I know we have a small sub panel already for the swimming pool and recepticles. Baby sleeping right now. Can the panel be moved but the service coming into the house stay at the same location?
 
Last edited:

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,983
Location
Modesto, CA
I know we have a small sub panel already for the swimming pool and recepticles. Baby sleeping right now. Can the panel be moved but the service coming into the house stay at the same location?

How is the service setup?

Meter main, divorced meter pan or??

Sounds like u have just a pan on the outside so u would have to run new service entrance wire to the new panel location as well as extend the existing branch circuit wires.

What brand of oanel do u have?
 
OP
9

930dreamer

Super Moderator
Staff member
Joined
Oct 7, 2009
Messages
22,928
Location
Amarillo,TX and Stinnett,TX
Here's the panel (100 amp) and it still has a few empty spots, we're planing a remodel and hot tub so this is why I'm asking. Thank you!
 

Attachments

  • DSCN2635.jpg
    DSCN2635.jpg
    103.2 KB · Views: 42

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,580
Location
Fullerton, CA
What is on the other side of the wall?
It may be possible to just face the panel the other way around (and save having to extend the circuits)
 

txvwnut

Well-known member
Joined
Jan 1, 2015
Messages
7,588
Location
Bedford, Texas
When I upgraded my panel we made a harness to go from the new panel into the old one which we had gutted and used like a junction box.

My original panel was in the master closet and the meter base was mounted on the exterior wall about 8 feet from the panel.
 

farphle

Well-known member
Joined
Jan 18, 2012
Messages
64
Location
Bedford, TX
When I upgraded my panel we made a harness to go from the new panel into the old one which we had gutted and used like a junction box.

My original panel was in the master closet and the meter base was mounted on the exterior wall about 8 feet from the panel.

Tell me more about this harness. I'm looking to move my panel out of my master closet and into the garage. The closet shares a wall with the garage and the meter base is on the exterior wall directly behind my current panel. Panel will end up about 8 feet from where it is now.
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,752
Moving a panel is very likely going to trigger AFCI requirements, make the existing panel a subpanel off the new service is one way around that.
 
To avoid these ads, REGISTER NOW!

zmaxmotorsports

Well-known member
Joined
Jan 11, 2013
Messages
11,948
Location
South of omaha
I guess it depends on where you're at and how understanding your inspector is.
I wired a couple of additions out west of here this past summer where both properties had existing panels in closet,no city inspector so had to deal with state of nebraska inspector.
He let me come out of the existing ge panel in each with a 4 wire feed to a new sub panel in each addition.
Then I just had to use afci breakers for the bedrooms fed from new panel,and a gfci breaker to feed bath in each addition.
As long as I didn't do any major alteration in existing panel ge was fine with it.
 

txvwnut

Well-known member
Joined
Jan 1, 2015
Messages
7,588
Location
Bedford, Texas
Tell me more about this harness. I'm looking to move my panel out of my master closet and into the garage. The closet shares a wall with the garage and the meter base is on the exterior wall directly behind my current panel. Panel will end up about 8 feet from where it is now.

We gutted the original panel of all its breakers so it essentially became a large junction box. We then ran the harness which was made of enough romex to match the existing circuits in the original panel. My house is pier and beam so I ran conduit from the new panel to an LB that went through the exterior wall and under the house then up to the old panel.

The main reason for this was when I built my my shop I had to relocate the arial service lines to underground as they were in the way of my shop. So that meant I had to get the entire service setup up to code plus my house had two sub panels that I wanted to get rid of.
 

L5wolvesf

Well-known member
Joined
Dec 4, 2011
Messages
1,831
Location
Northern AZ
My current house panel is in a bedroom closet, I want to get a
240 volt hot tub. If I upgrade the panel goes it need to be relocated?

I was in the same position about 7 years ago. Was told the closet panel had to go. Luckily the other side of the wall is a storage room. Mounted the new and bigger panel and shifted the wiring over without much hassle.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,983
Location
Modesto, CA
We gutted the original panel of all its breakers so it essentially became a large junction box. We then ran the harness which was made of enough romex to match the existing circuits in the original panel. My house is pier and beam so I ran conduit from the new panel to an LB that went through the exterior wall and under the house then up to the old panel.

The main reason for this was when I built my my shop I had to relocate the arial service lines to underground as they were in the way of my shop. So that meant I had to get the entire service setup up to code plus my house had two sub panels that I wanted to get rid of.

by code NM-b aka Romex is not rated for outdoor use...
 
Last edited:

ddawg16

Well-known member
Joined
Jul 11, 2008
Messages
21,005
Location
S. California
Putting the panel upgrade issue to the side for a moment....

Before you go buy a hot tub, check out Craig's list for all the free ones.

You can find some really good tubs......for free. Someone buys a hot tub....uses it a lot the first year....a few times the second year....then after about the 4th year of no use....they give it away.

So......maybe you really don't need to do the panel upgrade?
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,983
Location
Modesto, CA
While the panel is exterior everything is concealed from the elements. Panel upgrade passed inspection with flying colors.

Thats inconsequential. Code says interior only.

Being in conduit doesnt change that. Conduit can and does get water in it so it doesnt shield it from the elements.

NM-b is not rated for wet, damp, or exterior locations PERIOD.

And just because it passed doesnt mean it was done right. It only means the inspector either didnt know how it was done or doesnt know the code. I have seen lots of insectors pass things that they shouldnt have.

What kind of inspector was he?

U do realize that the paper filler in NM-B soaks up water like a sponge? This leads to corrosion among other issues.....

This is why there is UF-b which has no paper filler.
 