Partially Detached Garage Subpanel

AndrewDouglasBird

Well-known member
Joined
Oct 15, 2013
Messages
217
Location
Vancouver, WA
The wiring in my garage is from the 50's, has no ground wires and needs to be re-wired. It's a detached garage, spaced about 6 feet from the house, but is connected to the house by a small roof section over the doors going in the house and garage. The attic in the house is connected to roof connecting the two, so running wire into the garage will be easy.

But this has me wondering, do I treat this like a detached garage, or an attached garage in regards to grounding?
 
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,994
Location
Modesto, CA
You need a ground wire either way via 4-wire feeder.

The only question is whether you need electrodes.

Adding them wont hurt other than a little to your wallet
 
OP
A

AndrewDouglasBird

Well-known member
Joined
Oct 15, 2013
Messages
217
Location
Vancouver, WA
That makes sense. I was wondering if the ground and neutral needed to be bonded, but ALL sub panels have to have them un-bonded, correct?

As far as ground rods go, do I need 1 or two? I seem to be finding information that says both.

Thanks!
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,752
If it has a breezeway then I would call it attached.
 
To avoid these ads, REGISTER NOW!

aandpdan

Well-known member
Joined
Nov 12, 2009
Messages
847
Location
In between MA and PA
Check with your local AHJ as to whether or not it is considered attached or detached.

If you do need ground rods you'll need 2 - unless you can find someone to test the one for 25 ohms or less resistance to ground NEC 250.56. It's easier just to drive the other one.

3 wire subpanels, older code versions, are bonded. 4 wire, new code, are not bonded. You'll be using 4 wires.
 

b-boy

Well-known member
Joined
Oct 2, 2013
Messages
2,155
Location
Buffalo NY
Check with your local AHJ as to whether or not it is considered attached or detached.

If you do need ground rods you'll need 2 - unless you can find someone to test the one for 25 ohms or less resistance to ground NEC 250.56. It's easier just to drive the other one.

3 wire subpanels, older code versions, are bonded. 4 wire, new code, are not bonded. You'll be using 4 wires.

Follow up question - I understand the grounding rods need to be 6 ft apart, but how far from the structure should they be?
 