Pex manifold or a simple "t" fitting?

Fastback

Well-known member
Joined
Oct 5, 2010
Messages
518
Location
Indy
So my floor heat just has two loops and I was thinking that instead of buying a manifold and capping off the unused connections that I could just use pex T fittings instead? My main concern is cavitation...
 
To avoid these ads, REGISTER NOW!

BTI

Well-known member
Joined
Feb 4, 2010
Messages
82
Location
SE Ohio
You could do it that way but it doesn't give you the ability to adjust the flow.
Manifolds also typically will have bleeders and such on them.
If you do decide not to use a manifold I would be sure to leave room to put one in later.

BTI
 
OP
F

Fastback

Well-known member
Joined
Oct 5, 2010
Messages
518
Location
Indy
It's just that with two loops on a system with about 7 gallons total of fluid, some of this seems a bit overkill.
 
To avoid these ads, REGISTER NOW!
OP
F

Fastback

Well-known member
Joined
Oct 5, 2010
Messages
518
Location
Indy
I think Ill just make a copper pipe with some "T' fittings with a pex connection, so it will be a tiny manifold I guess.

Thanks for the help so far!
 

hansen1

Well-known member
Joined
Jul 26, 2008
Messages
86
Location
Colorado
You can always put a ball valve on the return side so you can adjust the flow. I have done that on a few small systems and they seem to work fine.
 

cghsparky

Member
Joined
Sep 27, 2009
Messages
7
Location
Iowa
are your loops the same length? if not i would go with the pex manifold with flow meters to adjust the flow.
 