Phase Taping - NEC rules

mobiledynamics

Well-known member
Joined
Mar 14, 2010
Messages
5,045
Location
Gotham City
Just doing some reading (pre-emptive for a new run for a electric car charger).

NEC rules allow you to use tape, etc to identify the phase ID of any wire except for ground as long as it's 4AWG or larger.

Anything smaller, you cannot phase tape.

Can anyone confirm if it's 4AWG or larger ?
I found some older blurbs that its 6AWG or larger.
 
To avoid these ads, REGISTER NOW!

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
The #4 and larger vs. #6 and smaller is the grounded conductor (neutral). I'm not aware of any size difference for the marking of ungrounded conductors. There is a size stipulation for marking ungrounded conductors in a DC system.

See NEC 200.6 grounded conductors, 210.5 and 215.12 for ungrounded conductors.
 
Last edited:

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,067
Location
Modesto, CA
Just doing some reading (pre-emptive for a new run for a electric car charger).

NEC rules allow you to use tape, etc to identify the phase ID of any wire except for ground as long as it's 4AWG or larger.

Anything smaller, you cannot phase tape.

Can anyone confirm if it's 4AWG or larger ?
I found some older blurbs that its 6AWG or larger.

Here's the run down(it depends on the conductor type AND size):

EGCs NEC 250.119
Insulated EGCs #6 and smaller must have continous outer finish that is green or green with one or more yellow stripes. On #4 and larger a conductor can be re-identified with green tape at every point that is accessible.

Grounded conductors/neutrals NEC 200.6(A) and (B)
Size #6 and smaller one of the following methods:
continuous white or gray finish
3 continuous white stripes along entire length on other than green insulation
(theres more but the above is the most common way)
Size #4 and larger
the above methods or by using white or gray marking such as tape at termination points

Ungrounded conductors do not have a size limitation for re-identifying conductors as far as I know. NEC 210.5 (C)(1),(2), and (3)...
 
OP
M

mobiledynamics

Well-known member
Joined
Mar 14, 2010
Messages
5,045
Location
Gotham City
Oh well. I guess there goes the idea of buying a 500 foot spool and using it for all 3. The neutral is the killer, unless I feel like taking 35 and making a spiral down the entire run
 

ddawg16

Well-known member
Joined
Jul 11, 2008
Messages
21,005
Location
S. California
Car charger?

I'm assuming 240Vac? Does it require a neutral? I would think 2 blacks and a ground are all you would need. 240Vac is single phase so you don't need to 'phase tape' them.

Basically, it's about the same as hooking up your electric water heater.
 

Mustang51js

Well-known member
Joined
Jan 24, 2014
Messages
1,734
Location
Haskell nj
Where are you putting the charger,can you just run romex to where it's going. Btw I never had issues with taping the neutral number 6 or larger just taping the ends
 
To avoid these ads, REGISTER NOW!

kiatech

Well-known member
Joined
Aug 23, 2012
Messages
2,570
Location
Toledo, Ohio
y8uza6yj.jpg

Like this
 
To avoid these ads, REGISTER NOW!
Top Bottom