Pics: Mr Heater Big Maxx install

Scott

Well-known member
Joined
Dec 21, 2005
Messages
139
Location
Bothell, WA
The heater is installed somewhat temporarly until the drywall goes up. Here are a couple of pictures of the install of a Mr Heater Big Maxx 45k natural gas heater. The install was pretty straight forward, I cut 4" out of my 1" gas line then threaded the ends installed a tee, union, drip leg and valve. I used a gas hookup kit for a furnace(yellow line) so that it is easy to unhook due to the flare fittings on the hose. I wired in an extra switched oultet for 110v power. The only thing left to do is hook up the flue pipe (Lowes did not have the right stuff :sad: ), need to go to HD to see if they have the right adapter tomorrow. I bought a simple digital thermostat for temp control.

I turned on the heater for a quick test, it's nice and quite and heats up in a hurry. Now onto the rest of the garage remodel! :thumbup:
 

Attachments

  • heater.JPG
    heater.JPG
    45.4 KB · Views: 2,399
  • outlet.JPG
    outlet.JPG
    40.8 KB · Views: 2,093
  • gas hookup.JPG
    gas hookup.JPG
    39.1 KB · Views: 2,111
To avoid these ads, REGISTER NOW!

fireman

Well-known member
Joined
Dec 7, 2005
Messages
129
Nice job Scott. It's unbelievable how quiet these units are. It must be because of the large diameter fan run at a slow speed. They included an extra sticker with mine so you could replace the original if you wanted to hang it upsidedown.
 
OP
S

Scott

Well-known member
Joined
Dec 21, 2005
Messages
139
Location
Bothell, WA
BearHit said:
Uh... Looks to be upside down there sir...

:lol: Yup, it is. It came with another sticker so I should fix that, otherwise I will hear about that till the end of time! The flue pipe and gas connection seemed to look better with it that way(it puts them towards the top of the unit).
 
OP
S

Scott

Well-known member
Joined
Dec 21, 2005
Messages
139
Location
Bothell, WA
There are quite few companies that make electric versions. Look up Dayton heaters on this forum.
 

spud

Member
Joined
Jan 22, 2005
Messages
19
Location
Alberta
Mine looks upside down too, because the stickes is upside down, nice install BUT... did you use regular 14/ 2 wire for your plug to your furnace ??? :wtf: or was it white extention cord cable .
 
OP
S

Scott

Well-known member
Joined
Dec 21, 2005
Messages
139
Location
Bothell, WA
I initially used romex because I had it around, I have since changed it over to appliance wire.
 

spit on it

New member
Joined
Dec 19, 2008
Messages
1
i picked up a hr heater 75,000 natural gas and it wont light up. there is gas going to the unit, it clicks like it wants to light, but no fire. any info would be great.... where did you put the ground?
 

Junkman

Well-known member
Joined
Dec 18, 2006
Messages
6,615
Location
Northeastern CT
Check to make sure there is gas getting to the unit. It is is getting gas, and there is spark, there should be some flame. If it isn't lighting then you might have another problem. Hard to diagnose with so little information. When I had a problem like that, it was that the sensors were not detecting a flame and it would go off on the safety. Once I got all the logs lit, there was no more problem. I had a problem that the flame didn't jump from one log to the next, so the top 3 or 4 were not igniting.
 

porschedude996TT

Well-known member
Joined
Oct 28, 2007
Messages
2,384
Location
Santa Maria, California
The heater is installed somewhat temporarly until the drywall goes up. Here are a couple of pictures of the install of a Mr Heater Big Maxx 45k natural gas heater. The install was pretty straight forward, I cut 4" out of my 1" gas line then threaded the ends installed a tee, union, drip leg and valve. I used a gas hookup kit for a furnace(yellow line) so that it is easy to unhook due to the flare fittings on the hose. I wired in an extra switched oultet for 110v power. The only thing left to do is hook up the flue pipe (Lowes did not have the right stuff :sad: ), need to go to HD to see if they have the right adapter tomorrow. I bought a simple digital thermostat for temp control.

I turned on the heater for a quick test, it's nice and quite and heats up in a hurry. Now onto the rest of the garage remodel! :thumbup:

I don't think it is to code if you use a union in a gas system. To join pipe you need to use Lt/Rt Treaded ****** and coupling.
 

Attachments

  • union.gif
    union.gif
    7.5 KB · Views: 2,629
  • Lt Rt Coupling.gif
    Lt Rt Coupling.gif
    3.1 KB · Views: 233
  • Lt Rt.gif
    Lt Rt.gif
    3.6 KB · Views: 262
Last edited:

ironroad 9c1

Banned
Joined
Sep 3, 2005
Messages
758
Location
Gum spring,VA
Also be aware that once you tighten that flexable tubing, you can't reuse it, I bought a kit today with the same thing and it says you can't reuse that tube.
 
To avoid these ads, REGISTER NOW!

69satelite

Active member
Joined
Jan 25, 2008
Messages
33
unions pass code here in minnesota on gas lines that might just be code in your area
 

Steve1968LS2

Well-known member
Joined
Mar 2, 2008
Messages
108
Location
Anaheim Hills, CA
How much was that unit.. in CA here but it's cold in the winter.. 450 sq-ft garage.

Looks like a good option since I have a gas line handy.

Thanks
 

RAMBIN

Well-known member
Joined
Jan 5, 2006
Messages
133
Location
canada
The heater is installed somewhat temporarly until the drywall goes up. Here are a couple of pictures of the install of a Mr Heater Big Maxx 45k natural gas heater. The install was pretty straight forward, I cut 4" out of my 1" gas line then threaded the ends installed a tee, union, drip leg and valve. I used a gas hookup kit for a furnace(yellow line) so that it is easy to unhook due to the flare fittings on the hose. I wired in an extra switched oultet for 110v power. The only thing left to do is hook up the flue pipe (Lowes did not have the right stuff :sad: ), need to go to HD to see if they have the right adapter tomorrow. I bought a simple digital thermostat for temp control.

I turned on the heater for a quick test, it's nice and quite and heats up in a hurry. Now onto the rest of the garage remodel! :thumbup:


ive just bought one of these myself and ur pics show the same scenario i'm looking at, the 2 hangers that come with it are now wide enough to span truss to truss (which thru out the world is 24" if i'm correct) i guess that would take brains eh? so now i gotta engineer something like you did with your hanging system which involves me going into the insualtion filled attic, oh the joys of stupidity!
 

CNCMAN

New member
Joined
Sep 7, 2010
Messages
2
Ordered my Mr. Heater on Friday. Should arrive by 9/10, 45,000 BTU. I'm using it to heat a 384 sq. ft. detached workshop. Did any installation hardware come with the unit?
 

regguy1

Well-known member
Joined
Dec 15, 2009
Messages
4,053
Location
On Mount Olympus with Zeus
I hung my Mr Heater 45K BTU like this, I made a cardboard template from the
shipping box. I put the template up to the ceiling at the angle I wanted the heater at (I have drywall) and punched holes through the drywall at the bolt locations, then went up above and screwd 2x4's betweem the trusses so I could put lag bolts into them. I pre drilled pilot holes and had a couple guys hold the heater up and I put the lags in with a ratchet. I was easy.

(Some photos before and after finishing)
 

Attachments

  • DSCN0598.jpg
    DSCN0598.jpg
    134.4 KB · Views: 649
  • DSCN0597.jpg
    DSCN0597.jpg
    136.9 KB · Views: 563
  • DSCN0601.jpg
    DSCN0601.jpg
    141.1 KB · Views: 559
  • DSCN0875.jpg
    DSCN0875.jpg
    136 KB · Views: 510

dipper

Well-known member
Joined
Jun 27, 2007
Messages
759
Location
Rochester, NY
CNCMAN,
They come with a metal bracket, but other than that they do not come with any bolts or threaded rod. Search my posts for my install, i documented my install pretty well and have some pics too.
 

regguy1

Well-known member
Joined
Dec 15, 2009
Messages
4,053
Location
On Mount Olympus with Zeus
CNCMAN,
They come with a metal bracket, but other than that they do not come with any bolts or threaded rod. Search my posts for my install, i documented my install pretty well and have some pics too.

I was under the impression that the PE gas line is only supposed to be used below grade you have it exposed inside the building, does that meet code in your area? The smallest fire would melt that stuff and you'd have a blow torch in your building.
 

rjmkn

Member
Joined
Jan 30, 2010
Messages
20
Location
Near Chicago, IL
I have one of those Mr. Heater 75000 BTU units. (Won it in a raffle) and the only question I have is running the flue through the exterior insulated/drywall wall. The "Thimble" that is required to go through the wall, how far does the insulation need to be from it and how do you seal the outer end from the elements. The cap to run horizontal is it different from a vertical flue cap? BTY you guy's did a nice job on the installs! Thanks in advance.
 

Sworks120

Member
Joined
Aug 5, 2010
Messages
16
The "Thimble" that is required to go through the wall, how far does the insulation need to be from it and how do you seal the outer end from the elements.

I am in the same position right now. Where the thimble would pass through the exterior wall is also home to the majority of my electrical wires that go to my sub-panel. The wires are all tacked down but is there a clearance issue with electrical wires? Obviously they would not touch the thimble but is there any problem with the thimble being between the same studs that the electrical runs up?
 

dipper

Well-known member
Joined
Jun 27, 2007
Messages
759
Location
Rochester, NY
I was under the impression that the PE gas line is only supposed to be used below grade you have it exposed inside the building, does that meet code in your area? The smallest fire would melt that stuff and you'd have a blow torch in your building.

It's covered by drywall in the wall and the ceiling tiles above.
 

Junkman

Well-known member
Joined
Dec 18, 2006
Messages
6,615
Location
Northeastern CT
I am in the same position right now. Where the thimble would pass through the exterior wall is also home to the majority of my electrical wires that go to my sub-panel. The wires are all tacked down but is there a clearance issue with electrical wires? Obviously they would not touch the thimble but is there any problem with the thimble being between the same studs that the electrical runs up?

I wouldn't use the area between studs that have electrical wires running through them, even it is legal in your jurisdiction. Too great of a chance of a wire being effected by the heat of the chimney...
 