Pilot light goes out!!

69boss9

Well-known member
Joined
Dec 13, 2009
Messages
57
Location
N/C Illinois
I have a Sterling overhead furnace in my garage and it does a very good job of heating. It is about 7 years old and is good and clean. However it has started shutting down the pilot light. It relights with no problem, I replaced the thermocouple, but that didn't correct the problem. It works fine for several days and then nothing, any ideas?
 
Last edited:
To avoid these ads, REGISTER NOW!

Orange_stang

Member
Joined
Dec 10, 2014
Messages
16
Location
Belfry, KY
Might sound crazy but have you tried cleaning the pilot? And the tube going to the pilot? About 30psi of air blown through the tube or if no compressor you can use a straw.
 

CNGsaves

Well-known member
Joined
Sep 26, 2012
Messages
13,233
Location
KS and OK
+1 to start with simple stuff like cleaning and blowing out with compressed air.

Check drip leg for excessive rust and/or water. Quality of the natural gas might be diminished.

Check flue for birds nest blocking flow of exhaust gases.
 

Kevin54

MEMBER EMERITUS
Joined
Jan 12, 2005
Messages
29,341
Location
Urbana, Ohio
My first guess would have been the thermocouple, second guess would be the flue. check for obstructions. If the flue goes straight out and wind can blow in, either put a down elbow on it, or put a flue cap on it
 
To avoid these ads, REGISTER NOW!
OP
6

69boss9

Well-known member
Joined
Dec 13, 2009
Messages
57
Location
N/C Illinois
Thanks for all your thoughts on my problem. I will try to address it possibly tomorrow, keep you posted with my results.
 

CJM8515

Well-known member
Joined
Mar 8, 2014
Messages
9,292
Location
NJ
This might sound crazy, and Im not HVAC guy at all-but years ago we had an issue with our furnace in the attic and it took 3x coming out before it was resolved. It wasnt the workers fault either as the fix was bizarre.

Apparently the pilot and associated piping was fine, however there was some sorta drain tube of some kind that removes condensation and it was icing up. All they did was change the tube and rerouted it somehow and no more issues.
 

CNGsaves

Well-known member
Joined
Sep 26, 2012
Messages
13,233
Location
KS and OK
x2 on the thermocouple

^ ^ Read 1st post . . . . OP says he already replaced the thermocouple. Think it would be unlikely that new out-of-box thermocouple would be bad.

Sounds to me like starved for fuel . . . or can't breathe (assuming that his replaced thermocouple is actually working).
 

LS6 Tommy

Well-known member
Joined
Dec 27, 2013
Messages
26,162
Location
Northern NJ
Check the heat exchanger. Sometimes when they leak, the pilot gets blown out. When the main flame shuts down, the fan continues to run until the fanstat opens. Air from the fan leaks through the exchanger out of the burner tubes and blows it out.

Tommy
 
Last edited: