I am wiring up my lights in a workshop I had built and am running everything in conduit. I would like to have pilot lights at the switches, which are located at the main man door. I have (3) three way switches, that I would like a pilot lights installed. That way, I know when an exterior light is on and not have to happen to see that it is on when I am outside. My question is, what size of conductors do I need to run back to the pilot light from the switch leg of the light or the switch, depending on convenience. I have the lighting circuit on 20A circuit with #12 thhn wire. I'm not an NEC expert, but am quite familiar with the code book a40'nd it seems like that there is a variance of downsizing the wire size for pilot lights. Am I correct or do I just have wishful thinking? If I can downsize the conductors, what size am I am allowed to go to? The pilot lights will be of the led type. Cheers!:beer:

The reason for wanting to downsize from a #12 conductor, is that the conduits are fairly full and am just wanting an easier pull. The longest run is around 80' and the shortest is about 40'.
 
Last edited:
To avoid these ads, REGISTER NOW!

walta

Well-known member
Joined
Jan 13, 2017
Messages
2,311
Location
Dutzow Missouri
To my ear, downsizing the wires without a fuse/circuit breaker to limit the current sounds like a recipe for a fire.

Should the pilot light fail in a way that connects its 2 wires together the full rating of the breaker will flow thru the small wire it would likely get red hot and start a fire before the breaker trips.

Walta
 

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,580
Location
Fullerton, CA
It's Table 430.72(B) in the 2017 NEC and the control wires extend beyond the enclosure, so it says you can use up to.
#18 with 7 amps
#16= 10 amps
#14= 45 amps
#12= 60 amps

For the 18 you'd have to use fuses, the 16 fuses or a 10 amp breaker.
 
To avoid these ads, REGISTER NOW!

david5253

Active member
Joined
Nov 26, 2013
Messages
35
Location
Cripple Creek, Colorado
Insteon keypads are what you need. They will show which lights are on or off without the need to run any additional wires. Google "Insteon"
 

Attachments

  • insteon-garage-door-keypadlinc.jpg
    insteon-garage-door-keypadlinc.jpg
    12.9 KB · Views: 18

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
5,931
Location
NJ
It's Table 430.72(B) in the 2017 NEC and the control wires extend beyond the enclosure, so it says you can use up to.
#18 with 7 amps
#16= 10 amps
#14= 45 amps
#12= 60 amps

For the 18 you'd have to use fuses, the 16 fuses or a 10 amp breaker.

Article 430 is only for motor related topics, so it doesn't apply to a general purpose branch ckt.

Article 240.4(D)(1) & (2) lists the OCP requirements for "small conductors" similar 430.72B for #18 and #16 only.

Article 310.106(A) lists the min conductor sizes for General wiring as #14 for most types of insulation. Any exceptions I found listed don't apply to OP's situation.

OP will need #12 if OCP =20A or #14 if OCP = 15A.

If the OP picks up the lighting loads all at one switchbox, then those 3 S3's could be piloted style but this might fall short of OP's plan.
 
OP
R

raco232

Well-known member
Joined
Jan 2, 2018
Messages
87
Location
South Memphis, TN
I went ahead and ran #12 thhn and am done with it. It was tight, but did not exceed conduit fill in 3/4” emt. Thanks for all who replied! :beer:
 