Pioneer mini split install

softailtom

Well-known member
Joined
Feb 11, 2010
Messages
81
Location
Yukon Oklahoma
This is my experience with installation of a Pioneer 18k 17.7 seer unit. Shop is 21x27 with 5 windows 1 man door 1 overhead door. I purchased the unit from High Seer less than a week to arrive I did all the install myself was going530ebc9fc44a91e862f42ca3b45c55c8.jpgc38eae3a3c4173ebcefda360a34fc73d.jpgd08cee4ffb852c7ff13b8709ad057cd0.jpg hang the outside unit on my back wall but the brackets they sent me we're flimsy (they gave me money back) so I set it on 2 blocks. I was going to do the evacuation myself then have a hvac guy come in and pressure test but when I was ready to do it the 125.00 became 275.00 so I went looking for someone else lucked into someone who needed work done so while he pressured the system I put synchronizers in his Muncie. The unit works good but temps have been mild will update as temps get warmer. I'm waiting on another line set cover to finish the lines. Thanks to all that posted about mini splits helped me make my choice.
 

Attachments

  • 530ebc9fc44a91e862f42ca3b45c55c8.jpg
    530ebc9fc44a91e862f42ca3b45c55c8.jpg
    714.3 KB · Views: 4
  • d08cee4ffb852c7ff13b8709ad057cd0.jpg
    d08cee4ffb852c7ff13b8709ad057cd0.jpg
    910.1 KB · Views: 4
  • c38eae3a3c4173ebcefda360a34fc73d.jpg
    c38eae3a3c4173ebcefda360a34fc73d.jpg
    872.4 KB · Views: 4
To avoid these ads, REGISTER NOW!

justinjoyal

Well-known member
Joined
Apr 30, 2015
Messages
888
Location
Quebec
What kind of insulation do you have in that shop ?

Did you run the lineset or did the hvac guy do it ?
 

toyotadriver

Well-known member
Joined
Dec 30, 2010
Messages
1,586
Looks like you did a nice job. Paint the lineset the same color as your siding and it'll blend right in and be barely noticeable.
 

justinjoyal

Well-known member
Joined
Apr 30, 2015
Messages
888
Location
Quebec
8' ceilings ? Seems oversized to me but it's hard to really tell...

Is there a constant slope on the drain ? Judging by the siding, the lineset/drain seem to follow a level line ?
 
OP
S

softailtom

Well-known member
Joined
Feb 11, 2010
Messages
81
Location
Yukon Oklahoma
9 foot ceilings and moved the drain after that picture you see it next to the window. Line set cover is out of stock at high seer so I'm hold for finishing.0eba3f7efc1c47f5d84e85575c69b081.jpg5d164066372aa4c7bc6904af527aad15.jpg
 

Attachments

  • 0eba3f7efc1c47f5d84e85575c69b081.jpg
    0eba3f7efc1c47f5d84e85575c69b081.jpg
    777.5 KB · Views: 2
  • 5d164066372aa4c7bc6904af527aad15.jpg
    5d164066372aa4c7bc6904af527aad15.jpg
    973.2 KB · Views: 3
Last edited:

cagullett1

Well-known member
Joined
Sep 29, 2013
Messages
2,203
Location
North Texas
Justin, where are you located? I'm in a smaller garage and planned on going the same size unit (less insulation) and you said previously that would be oversized. During the summer, my garage doesn't get below 85-90, even at night or first thing in the morning. Texas heat can be brutal, and if the garage doors get opened much, I'm not sure it would be that oversized.
 

tab2

Well-known member
Joined
Apr 9, 2009
Messages
381
Location
Boston
Nice job. They aren't intimidating if you're NOT doing the evacuating and charge. I would do another one in a heart beat.
 

justinjoyal

Well-known member
Joined
Apr 30, 2015
Messages
888
Location
Quebec
Justin, where are you located? I'm in a smaller garage and planned on going the same size unit (less insulation) and you said previously that would be oversized. During the summer, my garage doesn't get below 85-90, even at night or first thing in the morning. Texas heat can be brutal, and if the garage doors get opened much, I'm not sure it would be that oversized.

Insulation plays a big part in sizing so if you have even less than R13 and the garage doors is often open then you could be fine with a bigger unit.
 

jcthorne

Well-known member
Joined
Apr 20, 2016
Messages
96
Location
Houston, TX
Anyone know if you have more than one of these in a large space, they each come with a remote, do the remotes interfere with each other or are they coded to be completely independent?
 

prostreetamx

Well-known member
Joined
Dec 19, 2016
Messages
222
Location
Las Vegas
Looking to do something similar in my new fully insulated 30'x38' x 14' ceiling garage in Las Vegas. I've already ran #10/3 wire to the locations I plan to install each part which in my case will be pretty close with the outside unit being installed about 10' away just outside the interior unit. Can't install till after my final inspection since It is not on prints. Permits for conditioned space cost more and the codes change some but I did set up the original build with this type of unit in mind so insulated for this. Insulation is not required in garages here. Can you give us some cost info? Will also be doing the install myself except for the pressure lines.
 
OP
S

softailtom

Well-known member
Joined
Feb 11, 2010
Messages
81
Location
Yukon Oklahoma
Looking to do something similar in my new fully insulated 30'x38' x 14' ceiling garage in Las Vegas. I've already ran #10/3 wire to the locations I plan to install each part which in my case will be pretty close with the outside unit being installed about 10' away just outside the interior unit. Can't install till after my final inspection since It is not on prints. Permits for conditioned space cost more and the codes change some but I did set up the original build with this type of unit in mind so insulated for this. Insulation is not required in garages here. Can you give us some cost info? Will also be doing the install myself except for the pressure lines.



It was 935.00 ship to my house that includes 18k unit with 25ft line set,wifi,line set cover,wall sleeve liner. HighSeer had a 10% off coupon on line that I used.
 

cagullett1

Well-known member
Joined
Sep 29, 2013
Messages
2,203
Location
North Texas
Insulation plays a big part in sizing so if you have even less than R13 and the garage doors is often open then you could be fine with a bigger unit.

I've got R13 in 2 walls and an insulated 2 bay door (not sure what rating). Ceiling isn't insulated, but once I find time to insulate it, it would be less than r30 due to only blowing in insulation between the sheetrock and attic floor. I have a feeling that my garage door will open up enough that the TX heat will help keep me from oversizing the unit.
 
OP
S

softailtom

Well-known member
Joined
Feb 11, 2010
Messages
81
Location
Yukon Oklahoma
I've got R13 in 2 walls and an insulated 2 bay door (not sure what rating). Ceiling isn't insulated, but once I find time to insulate it, it would be less than r30 due to only blowing in insulation between the sheetrock and attic floor. I have a feeling that my garage door will open up enough that the TX heat will help keep me from oversizing the unit.



The way I looked at it my shop gets full sun with 5 windows and a door going up and down applying regular calculations to my shop would have left me way unhappy.
 

cagullett1

Well-known member
Joined
Sep 29, 2013
Messages
2,203
Location
North Texas
The way I looked at it my shop gets full sun with 5 windows and a door going up and down applying regular calculations to my shop would have left me way unhappy.

I like the way you think. Plus, I doubt I'll ever have a smaller space than I'm in now.
 

soob

Well-known member
Joined
Jul 11, 2011
Messages
551
The sizing guides are intended for living space. Space that gets heated and cooled continuously. For a home shop you'll want something that can cool the space down quickly for when you want to use it, not something to keep it a steady temperature 24/7.
 
To avoid these ads, REGISTER NOW!
OP
S

softailtom

Well-known member
Joined
Feb 11, 2010
Messages
81
Location
Yukon Oklahoma
Update on pioneer sadly I've been unable to get this to cool effectively I worked with High Seer's technical department on this but they have gave up saying that the mini split is working as designed. I found a hvac company that does some mini split install to come take a look will update.


Sent from my iPhone using Tapatalk
 

soob

Well-known member
Joined
Jul 11, 2011
Messages
551
Why do you think an 18k btu mini split would outperform 8 + 8 + 12 window units?

18k btu would be marginal for that building even if the ceiling was insulated.
 

yeldogt

Well-known member
Joined
Jan 2, 2012
Messages
18,184
What are you asking it to do -- cool a hot room .. or maintain a space once cool.

There is no way you are going to cool a space with an uninsulated ceiling -- especially in a hot climate like TX.

You had a combined 30k with the window units -- if they did not work .. removing a ton of cooling is not going to work.
 
Last edited:
OP
S

softailtom

Well-known member
Joined
Feb 11, 2010
Messages
81
Location
Yukon Oklahoma
What are you asking it to do -- cool a hot room .. or maintain a space once cool.

There is no way you are going to cool a space with an uninsulated ceiling -- especially in a hot climate like TX.

You had a combined 30k with the window units -- if they did not work .. removing a ton of cooling is not going to work.



I've blown in more insulation in the ceiling the window units worked until you open the door then the recovery was hour or more. The pioneer will not hold 82 until the sun goes down. The power consumption by the pioneer is about the same as the 12000 window unit it's very efficient even when running 24/7.


Sent from my iPhone using Tapatalk
 

PoorOwner

Well-known member
Joined
Feb 10, 2007
Messages
5,032
Location
CA
Maybe late to consider but I had some issue with my last garage. I mounted the air handler close to the ceiling over 9 feet. When I get up on a ladder put my head near the ceiling there is a significant heat here because heat rises. The air handler always have to **** in the hottest air in the room and then cool it.

At least I think that's what happens when it is mounted close the ceiling. The manual would say something like 6" from ceiling minimum doesn't mean you have to... It just has to work extra hard. Let's say the air handler can give a delta of 20 degree cooler air. At my standing height it would be 80F and then the ceiling would be around 84F, the temp reading of the minisplit says. So you already lost 4 degree to mounting it close to ceiling. It is always hot up there and the cold air will not ever get up there to help. Unless you have alot of other airflow to stir the air then it would average out at best.

So for the next install I am going to mount it about 2-3 feet from the ceiling or just above header height. Mitsubishi recommends not to exceed 7.5 feet from floor.
 
OP
S

softailtom

Well-known member
Joined
Feb 11, 2010
Messages
81
Location
Yukon Oklahoma
Maybe late to consider but I had some issue with my last garage. I mounted the air handler close to the ceiling over 9 feet. When I get up on a ladder put my head near the ceiling there is a significant heat here because heat rises. The air handler always have to **** in the hottest air in the room and then cool it.

At least I think that's what happens when it is mounted close the ceiling. The manual would say something like 6" from ceiling minimum doesn't mean you have to... It just has to work extra hard. Let's say the air handler can give a delta of 20 degree cooler air. At my standing height it would be 80F and then the ceiling would be around 84F, the temp reading of the minisplit says. So you already lost 4 degree to mounting it close to ceiling. It is always hot up there and the cold air will not ever get up there to help. Unless you have alot of other airflow to stir the air then it would average out at best.

So for the next install I am going to mount it about 2-3 feet from the ceiling or just above header height. Mitsubishi recommends not to exceed 7.5 feet from floor.



That's funny I had a hvac guy out at lunch that was the first thing he said was the distance from the ceiling and also right above the window could be a issue. He's doing a evac and weighing the refrigerant to confirm correct charge.


Sent from my iPhone using Tapatalk
 

dnwong

Well-known member
Joined
Jul 27, 2006
Messages
104
Location
Aldie, VA
I just did a pioneer install this spring on my garage. 20x29x12 high. Did the install myself and vac the lines and torqued the flare fittings to spec and the system runs great. Barely notice it running at all. I have r19 wall, r38 ceiling and r18 door. My unit is around 10' high.
 

Attachments

  • IMG_1782 (Medium).jpg
    IMG_1782 (Medium).jpg
    71.4 KB · Views: 126
Last edited:

soob

Well-known member
Joined
Jul 11, 2011
Messages
551
If you have an air cushion of hot air with a tall ceiling that might be reasonable.

Just remember that, in general, you want to pull warmer air over the indoor coils as the evaporator is a heat exchanger; the warmer the air is, the more efficiently it works.
 

firebirdparts

Well-known member
Joined
Jun 8, 2016
Messages
10,584
Location
Kingsport, TN
If you have an air cushion of hot air with a tall ceiling that might be reasonable.

Just remember that, in general, you want to pull warmer air over the indoor coils as the evaporator is a heat exchanger; the warmer the air is, the more efficiently it works.

I think that is a misleading way to look at it. If you're standing on the floor, you want it cool down where you are. The amount of heat removed does not help you if that gets it cooler up next to the ceiling; You're not up there.
 

ticklechicken

Well-known member
Joined
Apr 25, 2016
Messages
110
Location
Florida
softailtom - Any updates?

I'm driving down to High Seer tomorrow to pick up my system. You've got me concerned...
 
OP
S

softailtom

Well-known member
Joined
Feb 11, 2010
Messages
81
Location
Yukon Oklahoma
Highseers tech department insisted the the unit was over charged so we pulled it out weight it and put 3.25 pounds back in(it had 3.38 pounds in it) Made no difference in performance. The hvac guy reset the board and it seems to be working better. He's installed some pioneer's and he likes the units. I'm going to lower the unit and move it from over the window.


Sent from my iPhone using Tapatalk
 
Last edited:

ticklechicken

Well-known member
Joined
Apr 25, 2016
Messages
110
Location
Florida
I'm right at 2x your square footage, and I picked up two 18k units. It'll be a few weeks until they're running. I'll be interested to see my results. I hope I'm getting enough cooling.

  • 24x45x10
  • no windows
  • 3 man doors
  • 1 insulated roll up door
  • closed cell foam - 2" on walls, 3" on ceiling
 
OP
S

softailtom

Well-known member
Joined
Feb 11, 2010
Messages
81
Location
Yukon Oklahoma
I'm right at 2x your square footage, and I picked up two 18k units. It'll be a few weeks until they're running. I'll be interested to see my results. I hope I'm getting enough cooling.



  • 24x45x10
  • no windows
  • 3 man doors
  • 1 insulated roll up door
  • closed cell foam - 2" on walls, 3" on ceiling


I hope you do too I'm very disappointed in the performance High Seers tech support hasn't been much help. I don't think it's moving much air even in turbo mode.


iPhone using Tapatalk
 

Razorsedge

Active member
Joined
Dec 6, 2015
Messages
26
I think it's just undersized. I went with a 36k in my 25x30x12 and it works well, but anything less would've been disappointing. The shop is has insulated walls, ceilings, and doors and the mini split will hold it at 72* on a 110* day. If I don't run it all day and just turn it on when I plan on going out there it will take it from 95* inside to 72* in about 1.5-2 hours
 

dw1

Well-known member
Joined
Jan 26, 2015
Messages
1,335
Location
Ky
I just inquired with High Seer about a Pioneer 18K mini split/heat pump for my pole barn, I am going to put a wall up and have a 16'x30'x12' area closed off with the mini split in it, they said the 18K btu was the correct size? what do you all think??, my walls are R13 and has a combination of barn wood and metal combination finish on them, I am thinking of the barn siding for my ceiling but have not installed it yet. Should I go 24K BTU?
I am getting ready to build a house and could (Will Be) living there for days at a time possibly
 

dw1

Well-known member
Joined
Jan 26, 2015
Messages
1,335
Location
Ky
Update on pioneer sadly I've been unable to get this to cool effectively I worked with High Seer's technical department on this but they have gave up saying that the mini split is working as designed. I found a hvac company that does some mini split install to come take a look will update.


Sent from my iPhone using Tapatalk

Tom, have you read through this? it is on their website, not sure if it can help you any?
http://www.highseer.com/pdf/Underperformance_Explained.pdf
 
OP
S

softailtom

Well-known member
Joined
Feb 11, 2010
Messages
81
Location
Yukon Oklahoma
I just inquired with High Seer about a Pioneer 18K mini split/heat pump for my pole barn, I am going to put a wall up and have a 16'x30'x12' area closed off with the mini split in it, they said the 18K btu was the correct size? what do you all think??, my walls are R13 and has a combination of barn wood and metal combination finish on them, I am thinking of the barn siding for my ceiling but have not installed it yet. Should I go 24K BTU?

I am getting ready to build a house and could (Will Be) living there for days at a time possibly



24k is what I was going to get but High Seer suggested that I stay at 18k. The hvac guy said he always recommends double what the calculations say for shops because of all the equipment and tools oversizeing not being a problem because of the inverter. If I had a do over I would have got the 24k and just maybe the 30k. My original in plain was to turn it on only when I was in the shop but been running it 24/7 when its 90 or hotter just to maintain 77/80.


iPhone using Tapatalk
 

txoid

New member
Joined
Jul 4, 2016
Messages
4
Location
TX
I just install a 24k pioneer in my garage last week. 30x20x9
3 car garage, builder grade door insulation, no windows, no installation except for the wall shared by the house, and no attic installation. Keep it set to 75 and had no problems all week long. It got up to 100 this weekend so I was pleased. I was going to get an 18k but I'm glad I didn't. Once I add insulation, it's not going to be a problem.
I got the + not the ++.
 