Placing Breakers in New Sub-panel

nwav8tor

Well-known member
Joined
Feb 21, 2012
Messages
239
Location
Spokane, WA
Please remember the saying "The only stupid question is the one that's not asked."

I'm installing a new sub-panel in my attached garage. It's a Siemens 125A main lug with 16 spaces for a maximum of 24 circuits. Provisions for tandem breakers are in the bottom 4 positions on each side. I only plan to use 8 spaces initially ( 6 single pole and one double pole) so here's the question:

Is there a preferred/standard method for placing the circuit breakers in the panel? For example, all 8 in a single column on either the left or right side OR 4 C/Bs in each column at the top or bottom of the panel.

What would you do and why?


Thanks,
Paul
 
To avoid these ads, REGISTER NOW!

Stuart in MN

Well-known member
Joined
Sep 8, 2005
Messages
23,146
Location
Minneapolis
You want to have the loads equally distributed across both hots as well as you can, and arranged so the wiring can be routed neatly out of the panel, but otherwise it doesn't matter too much how you place them.
 
To avoid these ads, REGISTER NOW!

RECox286

Well-known member
Joined
Apr 11, 2012
Messages
1,399
Location
South Joisey (yeah, that is part of the USA)
Since the main bus bars are staggered like when you mesh fingers of

both hands, you would have to skip every other position in order to

load only one leg of input power. IOW: as long as you load the

panel with c/b's in a configuration that puts the breakers all touching

each other, the load is considered to be in balance. (Load the breakers

with a space in between each breaker, and you are out of balance.)

Savy ?

UncleBob as opposed to U n c l e B o b
 
OP
N

nwav8tor

Well-known member
Joined
Feb 21, 2012
Messages
239
Location
Spokane, WA
Since the main bus bars are staggered like when you mesh fingers of

both hands, you would have to skip every other position in order to

load only one leg of input power. IOW: as long as you load the

panel with c/b's in a configuration that puts the breakers all touching

each other, the load is considered to be in balance. (Load the breakers

with a space in between each breaker, and you are out of balance.)

Savy ?

UncleBob as opposed to U n c l e B o b


That much is clear to me - thanks.
 